Last week I was doing a rough-in w/air handler installed duct test. I taped all the supply boots and installed the fan to the return grill just as always. When I set up the manometer, I noticed a pressure reading of 135Pa, this without the fan being turned on. If I disconnected the hose from the manometer, pressure fell to zero. Assuming I had done something to cause this I checked and rechecked everything, even installed fresh batteries. Finally, I moved the hose to another supply boot, this resulted in a proper reading so I went ahead with the test.
Does anyone have any idea what was going on to give such a reading? Let me know if you need more information. Thanks for help solving this perplexing question.
Tags:
Permalink Reply by David Meiland on April 23, 2012 at 9:56pm Hard to see how there could be +135 in one supply duct without at least some positive reading everywhere else. Maybe someone accidentally (?) tied a bath fan into that duct.......
Permalink Reply by Bill Bennett on April 24, 2012 at 6:55am No power to the house at time of testing.
Permalink Reply by Glen Gallo on April 24, 2012 at 6:39am someone stepping on the hose?
Permalink Reply by Bill Bennett on April 24, 2012 at 6:55am No.
Permalink Reply by Bud Poll on April 24, 2012 at 6:52am I would tend to agree with Glen, as a blocked tube will clock up rather fast. If there is still a pin hole I suspect the pressure would stabilize at some point, although I'm not going to test it. It could have been a kink somewhere that unfolded when you moved the hoses. If it was a positive pressure the block was on the input. If negative it would have been on the reference, DG700 at least.
Bud
Permalink Reply by Bill Bennett on April 24, 2012 at 7:09am I just submitted this to the Energy Conservatory. If I get something useful back from them, I'll post it here.
Permalink Reply by Bill Bennett on April 26, 2012 at 7:04am As promised, I asked the folks at The Energy Conservatory about my funky duct test results. Paul Morin, a Technical Sales Specialist suggested that such a situation could occur if the hose is stopped up or perhaps was up against insulation in the supply boot. He went on to say; "You can simulate a pressure this high by putting your finger over an open tap on the DG-700 gauge. It is harder to reproduce a pressure that high with a long length of hose attached, but you would see pressures that high if some debris is plugging the hose. You also will see pressures that high if the hose is pinched, stepped on or if there is water in the hose."
I believe that the end of the metal probe must have been up against the boot insulation, probably when I taped the hose to secure it. The resulting restriction of air caused the errant reading.
Thanks to everyone who offered a suggestion.
Something else to look out for. If you use the metal probe to punch through the plastic tape you can actually punch a hole in the plastic tape which will cover the end of the probe. I've had this happen to me and it caused some temporary confusion.
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Tom Delconte commented on Tom Delconte's blog post Lykans $29, Vampires $0 !
Judi Lyall joined allen p tanner's group
Judi Lyall replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase
Tom Maides commented on Jim Gunshinan's blog post The Universe Is Made of Stories
Laurie DiDonato posted an event
Tom Delconte posted a blog post
Jim Gunshinan commented on Jim Gunshinan's blog post The Universe Is Made of Stories
Edward Foskey commented on Jim Gunshinan's blog post The Universe Is Made of Stories© 2013 Created by Lawrence Berkeley National Laboratory.