I'm wondering if anyone out there has come across specific language for the attachment of fiberglass insulation over an unconditioned crawl space.  I realize there are various ways to accomplish proper installation where the insulation material makes contact with the floor diaphragm.  Personally I prefer to see the use of nylon twine as a means of attachment and I'm wondering if anyone happens to know of any recommended spacing guidelines for the attachment points of a zig zag pattern of twine when used for support of floor insulation.

Views: 1946

Replies are closed for this discussion.

Replies to This Discussion

Seems like a good question for one or more of the insulation manufacturers. When we "twine" insulation, we run it straight instead of zig-zag and generally on 16" centers.

Generally wire supports are used for this purpose:

But there is a danger in leaving the bottom of batts and floor joists exposed in an unconditioned crawl space in cold climates, since the underside of the floor assembly will be radiantly-coupled to the ground beneath and remain very close in temperature. If the crawl space is damp (and which one's aren't?), there is a high probability of mold growth on the joists and condensation on the batts.

bsi009_figure_03.jpg

So a far better approach is to place rigid foam board under the insulated joists to thermally isolate the entire floor assembly from the cold crawlspace floor and to create an air/moisture barrier as well. This is explained in Building Science Inc BSI-009 New Light in Crawlspaces http://www.buildingscience.com/documents/insights/bsi-009-new-light...

bsi009_figure_07.jpg

Those "lightning rods" rarely make for a good installation in my opinion. They depend on over-compressing the insulation in order to be securely installed, and if the insulation isn't over-compressed, they soon fall out.

In some cases I like rigid board under the floor, but in many houses there isn't an access door big enough to put full 4' sheets into the crawl, so you end up cutting the stuff in half or thirds.

I've never liked the "lightning rods" either. I prefer wood strapping.

But you can always jack the house up several feet onto cribbing, install the foam board, and drop it back onto its foundation.

Robert, you can save time by simply jacking one edge of the house. Lift it enough to slip all of the foam board into the crawl space, then lower it.

I like the idea of jacking several feet, though. When I retrofit a foundation to my old house, I lifted it just above head level so I could walk around under it, excavate, set forms, pour piers, do all of the mechanical work, etc. It was extremely convenient. It's back down to about 30" now, a crawl space once again, but most of the work is already done.

I like some headroom, too.

raise3

I appreciate the feedback on the floor installation procedures.  Just want to remind you that what I'm looking for are guidelines such as one might find through Resnet or Energy Star.  Personal opinions?  Not so much.  Thanks again though.

I don't think you'll find any such recommendations from either of those sources. There are best industry practices, building science evaluations, insulation manufacturer's recommendations, and the extensive personal experience (what you deride as "opinions") of professionals in the field.

I have considered this issue several times as well. I am thinking of using House wrap or the reflective bubble wrap as support/vapor barrier attached to the underside of the joist. Both are able to fit into the crawlspace areas. My concern is trapping moisture in the floor system. I would be happy with an "experienced opionion" or two.

House wrap is exactly the wrong thing to use if there is any dampness in the crawlspace, as it allows water vapor through but traps liquid water. Bubble foil would have the advantage of being a vapor barrier and radian barrier to decouple the joists from the ground temperature, but it would also trap moisture above.

I've used filter fabric if there was not a significant moisture source below (such as on cantilevered porches that got enclosed and insulated), which is not a vapor barrier but will breath if moisture does enter the cavity.

I guess my thinking was to isolate the floor cavity from the crawlspace with the barrier. The drawing above witht the rigid foam board makes sense but the issue is getting it in and installing it as stated above. I suppose the bubble foil might not prevent condensation from forming which could allow water to form above. How much moisture is likely to make its way throught the floor assembly from the inside? 

That depends on the permeability and leakiness of the floor above - will mop water or spills seep through? - and on the RH below. If the crawl space has a dirt floor with no VB or has any leakage from the outside, then you can bet the RH will be close to 100%.

To effectively decouple the floor assembly from the ground temperature requires both enough insulation and a radiant barrier, such as foil-faced foam board. Bubble Foil is a relatively useless product and simple Kraft-backed builder's foil works just as well in most applications.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Everblue posted events
3 minutes ago
Mst. Fatema Aktar is now a member of Home Energy Pros
8 hours ago
Robert Leone added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Blower Door Package for Sale

Hi,I am selling my blower door with extras as a package or individually. These items are used but…See More
15 hours ago
Profile IconRobert Leone and Richard Vito joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
15 hours ago
Richard Vito joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
23 hours ago
Richard Vito joined James Sayers's group
Thumbnail

Marketing Energy Efficiency

Sharing ideas, tools and examples of promoting energy efficiency to consumersSee More
23 hours ago
Richard Vito joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
23 hours ago
Richard Vito joined Kyle Brown's group
Thumbnail

Wrightsoft - Manual J / Manual D

If you use Wrightsoft to calculate loads or design ducts, you likely have questions.  Get answers…See More
23 hours ago
Jim Gunshinan commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"I had a revelation while attending Bruce Manclark's session of duct leak testing at the Energy…"
yesterday
George J. Nesbitt commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"Blower Door; the 2007 test was a depressurization test, and the 2014 a pressurization test, which…"
yesterday
George J. Nesbitt replied to Kaushal Bharath Raju's discussion Affordability & Deep Energy Upgrade/Passive House Retrofit in Berkeley, California.
"Plan, plan, plan, plan. The 1st step to is to understand the house, how it's built, the…"
yesterday
George J. Nesbitt posted an event

High Performance Windows - A Panel of Experts at Pyramid Alehouse`

April 26, 2014 from 3pm to 5pm
Join a lively panel discussion on high performance windows. We'll cover some basics, as well as…See More
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service