I'm wondering if anyone out there has come across specific language for the attachment of fiberglass insulation over an unconditioned crawl space.  I realize there are various ways to accomplish proper installation where the insulation material makes contact with the floor diaphragm.  Personally I prefer to see the use of nylon twine as a means of attachment and I'm wondering if anyone happens to know of any recommended spacing guidelines for the attachment points of a zig zag pattern of twine when used for support of floor insulation.

Views: 4432

Replies are closed for this discussion.

Replies to This Discussion

Seems like a good question for one or more of the insulation manufacturers. When we "twine" insulation, we run it straight instead of zig-zag and generally on 16" centers.

Generally wire supports are used for this purpose:

But there is a danger in leaving the bottom of batts and floor joists exposed in an unconditioned crawl space in cold climates, since the underside of the floor assembly will be radiantly-coupled to the ground beneath and remain very close in temperature. If the crawl space is damp (and which one's aren't?), there is a high probability of mold growth on the joists and condensation on the batts.

bsi009_figure_03.jpg

So a far better approach is to place rigid foam board under the insulated joists to thermally isolate the entire floor assembly from the cold crawlspace floor and to create an air/moisture barrier as well. This is explained in Building Science Inc BSI-009 New Light in Crawlspaces http://www.buildingscience.com/documents/insights/bsi-009-new-light...

bsi009_figure_07.jpg

Those "lightning rods" rarely make for a good installation in my opinion. They depend on over-compressing the insulation in order to be securely installed, and if the insulation isn't over-compressed, they soon fall out.

In some cases I like rigid board under the floor, but in many houses there isn't an access door big enough to put full 4' sheets into the crawl, so you end up cutting the stuff in half or thirds.

I've never liked the "lightning rods" either. I prefer wood strapping.

But you can always jack the house up several feet onto cribbing, install the foam board, and drop it back onto its foundation.

Robert, you can save time by simply jacking one edge of the house. Lift it enough to slip all of the foam board into the crawl space, then lower it.

I like the idea of jacking several feet, though. When I retrofit a foundation to my old house, I lifted it just above head level so I could walk around under it, excavate, set forms, pour piers, do all of the mechanical work, etc. It was extremely convenient. It's back down to about 30" now, a crawl space once again, but most of the work is already done.

I like some headroom, too.

raise3

I appreciate the feedback on the floor installation procedures.  Just want to remind you that what I'm looking for are guidelines such as one might find through Resnet or Energy Star.  Personal opinions?  Not so much.  Thanks again though.

I don't think you'll find any such recommendations from either of those sources. There are best industry practices, building science evaluations, insulation manufacturer's recommendations, and the extensive personal experience (what you deride as "opinions") of professionals in the field.

I have considered this issue several times as well. I am thinking of using House wrap or the reflective bubble wrap as support/vapor barrier attached to the underside of the joist. Both are able to fit into the crawlspace areas. My concern is trapping moisture in the floor system. I would be happy with an "experienced opionion" or two.

House wrap is exactly the wrong thing to use if there is any dampness in the crawlspace, as it allows water vapor through but traps liquid water. Bubble foil would have the advantage of being a vapor barrier and radian barrier to decouple the joists from the ground temperature, but it would also trap moisture above.

I've used filter fabric if there was not a significant moisture source below (such as on cantilevered porches that got enclosed and insulated), which is not a vapor barrier but will breath if moisture does enter the cavity.

I guess my thinking was to isolate the floor cavity from the crawlspace with the barrier. The drawing above witht the rigid foam board makes sense but the issue is getting it in and installing it as stated above. I suppose the bubble foil might not prevent condensation from forming which could allow water to form above. How much moisture is likely to make its way throught the floor assembly from the inside? 

That depends on the permeability and leakiness of the floor above - will mop water or spills seep through? - and on the RH below. If the crawl space has a dirt floor with no VB or has any leakage from the outside, then you can bet the RH will be close to 100%.

To effectively decouple the floor assembly from the ground temperature requires both enough insulation and a radiant barrier, such as foil-faced foam board. Bubble Foil is a relatively useless product and simple Kraft-backed builder's foil works just as well in most applications.

RSS

Featured Forum Discussions

What causes a temperature plane in a home

Started by Energy Wise Solutions in HVAC. Last reply by Peter Krych on Friday. 4 Replies

Velocity Pressure Testing

Started by Horace Douglas Hunt, Jr. in General Forum. Last reply by Horace Douglas Hunt, Jr. Apr 15. 2 Replies

Videos

  • Add Videos
  • View All

Latest Activity

Alana Barnett added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Energy audit equipment -all very new

I have a FLIR infrared camera, E40bx. Only used a few times -box, camera, charger, it is all there,…See More
12 hours ago
Alana Barnett joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
12 hours ago
Crosbey Archery posted a blog post
17 hours ago
Profile IconRon Sarrick and Alana Barnett joined Home Energy Pros
yesterday
Jim Fowler posted a discussion

TREAT modeling of mid-rise apartments low heating load

Does anyone have experience using TREAT to model mid-rise (3-story) apartment buildings with…See More
Friday
Peter Krych replied to Energy Wise Solutions's discussion What causes a temperature plane in a home
"I also should have asked where the furnace was located,basement,1st or 2nd floor. In any case the…"
Friday
Profile IconJim Fowler, Jennifer Flanagan, Debra Smit and 2 more joined Home Energy Pros
Friday
Eric Sperline added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Wanted: Energy Auditing Equipment for sale

I am looking to buy a door frame panel that will accept a duct blaster fan.  I don't need the…See More
Friday

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service