I've been doing HP assessments for 12 years, but find myself a little limited in my knowledge of this issue.

Here's the scenario: I do an initial assessment where I find a 7-year old NG water heater with 1500 ppm undiluted CO. The homeowner brings in his plumber to "fix" it. The plumber, who doesn't own a CO monitor, cleans the burner and air intake grill, and proclaims it good. After work is done on the home, I re-test and find the CO to be even higher this time, and the draft weak.

What typically can be done to a fairly new water heater to fix the CO problem? The gas/air ratio must be out of wack, I'm thinking. Is it usually corrected by replacing the gas control valve?

The homeowner is left hanging, the plumber is without a clue and me telling him it needs to be corrected. I would recommend a different plumber, but I want to find out what a knowledgeable individual would typically do to correct this, short of replacing it. One thing I know is I need to align with a knowledgeable person to address this in the future.

John Shillito

Tags: CO, heater, plumber, water

Views: 640

Reply to This

Replies to This Discussion

I have to agree with Kurt. 2000 ppm is exceedingly high. I have tested hundreds of hot water heater (NG, Oil) and mostly they come in around 16 ppm. There is clearly something wrong and we all know that a gas hot water draft can easily be compromised. 

hey thanks for the links. Very informative on FVIR units

Hello John (and everyone else in the forum),

I'm a new visitor at this forum and it this is my first post. I look forward to more sharing and learning in the future.

The first condition that I would investigate the "weak draft". Is the flame lazy too? Is the equipment in place the same as what the flue was originally designed for?

I find the best place to contact when at a loss is the manufacturer's technical support.

Steve

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Empower Efficiency added a discussion to the group Job Board
Thumbnail

Position Opening: Local Community Outreach Specialist, Energy Efficiency (San Carlos, CA)

Local Community Outreach Specialist, Energy Efficiency (San Carlos, CA) Job Title: Local Community…See More
3 hours ago
Amber Vignieri posted a blog post

Elevate Energy Mythbusters: Windows & Attics Edition

This blog post is guest written by former staff member Eric Keeley.Great enthusiasm for home energy…See More
5 hours ago
Glen Gallo replied to Diane Chojnowski's discussion Poll: What is you favorite or most important home performance diagnostic or measurement tool?
"I agree with Ted. If I could bring just one piece of equipment it would be the blower door. It has…"
7 hours ago
Glen Gallo replied to Shaun 's discussion Commercial duct testing
"If above the ceiling tiles the wall is a finished assembly and there is insulation on or under the…"
7 hours ago
Tom White's video was featured

Combustion Appliance Zone Testing (CAZ) Made Easy (March 24, 2016)

Combustion Appliance Zone Testing (CAZ) Made Easy (March 24, 2016) -Gauge Fundamentals -Adapting to the new BPI standard -RESNET testing requirements -NFPA testing requirements -Best practices for best results
8 hours ago
Profile IconLaura Capps and Bret Abrams joined Home Energy Pros
yesterday
Olivia Taylor posted a blog post

5 Key Reasons Why Rooftop Solar Is Popular In The US

The rapid switch from traditional electricity to clean, economical and renewable solar energy is…See More
yesterday
Adam Swain posted a blog post

Top 5 Tips For Hiring A Crawl Space Contractor

A homes crawl space is one of the few places most homeowners try to avoid at all cost, and for good…See More
Wednesday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service