I've been doing HP assessments for 12 years, but find myself a little limited in my knowledge of this issue.

Here's the scenario: I do an initial assessment where I find a 7-year old NG water heater with 1500 ppm undiluted CO. The homeowner brings in his plumber to "fix" it. The plumber, who doesn't own a CO monitor, cleans the burner and air intake grill, and proclaims it good. After work is done on the home, I re-test and find the CO to be even higher this time, and the draft weak.

What typically can be done to a fairly new water heater to fix the CO problem? The gas/air ratio must be out of wack, I'm thinking. Is it usually corrected by replacing the gas control valve?

The homeowner is left hanging, the plumber is without a clue and me telling him it needs to be corrected. I would recommend a different plumber, but I want to find out what a knowledgeable individual would typically do to correct this, short of replacing it. One thing I know is I need to align with a knowledgeable person to address this in the future.

John Shillito

Tags: CO, heater, plumber, water

Views: 541

Reply to This

Replies to This Discussion

I have to agree with Kurt. 2000 ppm is exceedingly high. I have tested hundreds of hot water heater (NG, Oil) and mostly they come in around 16 ppm. There is clearly something wrong and we all know that a gas hot water draft can easily be compromised. 

hey thanks for the links. Very informative on FVIR units

Hello John (and everyone else in the forum),

I'm a new visitor at this forum and it this is my first post. I look forward to more sharing and learning in the future.

The first condition that I would investigate the "weak draft". Is the flame lazy too? Is the equipment in place the same as what the flue was originally designed for?

I find the best place to contact when at a loss is the manufacturer's technical support.

Steve

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Colin Genge posted events
5 hours ago
John Nicholas replied to Sean Lintow Sr's discussion Duct Testing - is a change in order? in the group Best Practices (Residential)
"Yes,  I was connected to the AH cabinet.  I find it easier in this area, given the common…"
7 hours ago
Colin Genge replied to Kim Tanner's discussion Blower Door Applications Guide in the group Multifamily Buildings
"This is a great guide that anyone testing with multiple fans should get hold  of. "
8 hours ago
Colin Genge added a discussion to the group Multifamily Buildings
Thumbnail

Just posted a lot of Multi-Family oriented blower door videos.

Just posted a lot of Multi-Family oriented blower door videos. Everything to do with Multi-Fan…See More
8 hours ago
Colin Genge joined Norm Bourassa's group
Thumbnail

Multifamily Buildings

For too long there has been relatively little EE focus on multifamily, but some new programs have…See More
8 hours ago
Colin Genge replied to Sean Lintow Sr's discussion Duct Testing - is a change in order? in the group Best Practices (Residential)
"I would assume you tested that high air leakage from the equipment cabinet and not on a flex…"
8 hours ago
Colin Genge replied to Sean Lintow Sr's discussion Blower Doors & Methods Used in the group Best Practices (Residential)
"For those of you who need  a Tectite report, FanTestic's report Generator is powerful…"
8 hours ago
Colin Genge joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
8 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service