I've been doing HP assessments for 12 years, but find myself a little limited in my knowledge of this issue.

Here's the scenario: I do an initial assessment where I find a 7-year old NG water heater with 1500 ppm undiluted CO. The homeowner brings in his plumber to "fix" it. The plumber, who doesn't own a CO monitor, cleans the burner and air intake grill, and proclaims it good. After work is done on the home, I re-test and find the CO to be even higher this time, and the draft weak.

What typically can be done to a fairly new water heater to fix the CO problem? The gas/air ratio must be out of wack, I'm thinking. Is it usually corrected by replacing the gas control valve?

The homeowner is left hanging, the plumber is without a clue and me telling him it needs to be corrected. I would recommend a different plumber, but I want to find out what a knowledgeable individual would typically do to correct this, short of replacing it. One thing I know is I need to align with a knowledgeable person to address this in the future.

John Shillito

Tags: CO, heater, plumber, water

Views: 629

Reply to This

Replies to This Discussion

I have to agree with Kurt. 2000 ppm is exceedingly high. I have tested hundreds of hot water heater (NG, Oil) and mostly they come in around 16 ppm. There is clearly something wrong and we all know that a gas hot water draft can easily be compromised. 

hey thanks for the links. Very informative on FVIR units

Hello John (and everyone else in the forum),

I'm a new visitor at this forum and it this is my first post. I look forward to more sharing and learning in the future.

The first condition that I would investigate the "weak draft". Is the flame lazy too? Is the equipment in place the same as what the flue was originally designed for?

I find the best place to contact when at a loss is the manufacturer's technical support.

Steve

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Joseph Frederick added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Blower door Equipment for sale

Minneapolis Blower Door model 700, DG with cruise control. Hoses and manuals, door frame. Used once…See More
13 minutes ago
Dan Antonioli replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"For my particular application the heat pump heater would be integral to the tank and thus be…"
2 hours ago
Dennis Heidner replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"What climate zone are you in?  Where would the hot water heater be set?  Northern…"
4 hours ago
Larry Weingarten replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"Hello:  Looking for solid numbers,you might want to search "Martin Holladay solar thermal…"
4 hours ago
Profile IconGabriel Lieb, Beth Neri and Aaron Beck joined Home Energy Pros
5 hours ago
Kim Tanner posted a discussion

Game of Homes

Have you seen the new online game by EnergyLogic, Game of Homes? If not you should check it out!…See More
6 hours ago
Beth Neri liked John Gillis's discussion Tamarack Technologies Introduces First Intelligent Whole House Fan
6 hours ago
Steven Lefler replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"Dan, I build "Net Zero" modular homes. I was given this company as a possible solution…"
6 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service