I've been doing HP assessments for 12 years, but find myself a little limited in my knowledge of this issue.

Here's the scenario: I do an initial assessment where I find a 7-year old NG water heater with 1500 ppm undiluted CO. The homeowner brings in his plumber to "fix" it. The plumber, who doesn't own a CO monitor, cleans the burner and air intake grill, and proclaims it good. After work is done on the home, I re-test and find the CO to be even higher this time, and the draft weak.

What typically can be done to a fairly new water heater to fix the CO problem? The gas/air ratio must be out of wack, I'm thinking. Is it usually corrected by replacing the gas control valve?

The homeowner is left hanging, the plumber is without a clue and me telling him it needs to be corrected. I would recommend a different plumber, but I want to find out what a knowledgeable individual would typically do to correct this, short of replacing it. One thing I know is I need to align with a knowledgeable person to address this in the future.

John Shillito

Tags: CO, heater, plumber, water

Views: 435

Reply to This

Replies to This Discussion

I have to agree with Kurt. 2000 ppm is exceedingly high. I have tested hundreds of hot water heater (NG, Oil) and mostly they come in around 16 ppm. There is clearly something wrong and we all know that a gas hot water draft can easily be compromised. 

hey thanks for the links. Very informative on FVIR units

Hello John (and everyone else in the forum),

I'm a new visitor at this forum and it this is my first post. I look forward to more sharing and learning in the future.

The first condition that I would investigate the "weak draft". Is the flame lazy too? Is the equipment in place the same as what the flue was originally designed for?

I find the best place to contact when at a loss is the manufacturer's technical support.

Steve

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner replied to Kevin Jordan's discussion Does anyone have pointers on approaching real estate induatry.
"Kevin, Several years ago I worked closely with a general contractor and a real estate…"
4 minutes ago
Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"That same RCC, used as paint on the ceiling of living space, will do the same as if it was applied…"
25 minutes ago
John Nicholas commented on Michael Stuart's group INFRARED THERMOGRAPHY USERS
"Don,  You are incorrect!  This is *NOT* the only course available that meets the ASNT…"
37 minutes ago
Craig Bird commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Correct, that is exactly what I said"
1 hour ago
Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"At 1.7% enterng the structure, that Radiant barrier is now going to allow the R-rated insulation/s…"
1 hour ago
Craig Bird commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"And how much of that 1.7% of the suns energy that got through the RB or RCC gets into the house,…"
1 hour ago
Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"OK.  This might be rudamentary here.  I want to make sure everyone understands how SOLAR…"
2 hours ago
Craig Bird commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Hal - I would disagree that radiant heat "goes through" fibrous insulation. Radiant heat…"
2 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service