I've been doing HP assessments for 12 years, but find myself a little limited in my knowledge of this issue.

Here's the scenario: I do an initial assessment where I find a 7-year old NG water heater with 1500 ppm undiluted CO. The homeowner brings in his plumber to "fix" it. The plumber, who doesn't own a CO monitor, cleans the burner and air intake grill, and proclaims it good. After work is done on the home, I re-test and find the CO to be even higher this time, and the draft weak.

What typically can be done to a fairly new water heater to fix the CO problem? The gas/air ratio must be out of wack, I'm thinking. Is it usually corrected by replacing the gas control valve?

The homeowner is left hanging, the plumber is without a clue and me telling him it needs to be corrected. I would recommend a different plumber, but I want to find out what a knowledgeable individual would typically do to correct this, short of replacing it. One thing I know is I need to align with a knowledgeable person to address this in the future.

John Shillito

Tags: CO, heater, plumber, water

Views: 541

Reply to This

Replies to This Discussion

I have to agree with Kurt. 2000 ppm is exceedingly high. I have tested hundreds of hot water heater (NG, Oil) and mostly they come in around 16 ppm. There is clearly something wrong and we all know that a gas hot water draft can easily be compromised. 

hey thanks for the links. Very informative on FVIR units

Hello John (and everyone else in the forum),

I'm a new visitor at this forum and it this is my first post. I look forward to more sharing and learning in the future.

The first condition that I would investigate the "weak draft". Is the flame lazy too? Is the equipment in place the same as what the flue was originally designed for?

I find the best place to contact when at a loss is the manufacturer's technical support.

Steve

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

David I. Shepherd-Gaw replied to Ryan Miller's discussion Wouldn't it make more sense to post jobs on a single board nationally? in the group Job Board
"I have managed and overseen several efforts with www.energyexpert.org and other similar sites. It…"
9 minutes ago
David Baerg replied to Bachi Brunato's discussion Modeling a Gas Fireplace in Wrightsoft
"I would not include it.  Given that it is likely much less efficient than the gas furnace, you…"
1 hour ago
Ryan Miller posted a discussion

First NC and now GA - Building Performance Associations taking shape

Hi All - Just a quick "this is what we're up to" for the community.The NC Building Performance…See More
2 hours ago
Bachi Brunato posted a discussion

Modeling a Gas Fireplace in Wrightsoft

Any advice on how to factor a gas fireplace into a Wrightsoft Manual J model? Seems like it would…See More
2 hours ago
Ryan Miller added a discussion to the group Job Board
Thumbnail

Wouldn't it make more sense to post jobs on a single board nationally?

Home Performance Coalition has one. Other organizations have one.  We have one for North Carolina. …See More
2 hours ago
Profile IconRyan Miller and David M Cohen joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
2 hours ago
robert jones posted a status
"Does anybody have audit tools for sale in the Albany NY area? Give me a call at 518-209-5912"
2 hours ago
Bachi Brunato joined Kyle Brown's group
Thumbnail

Wrightsoft - Manual J / Manual D

If you use Wrightsoft to calculate loads or design ducts, you likely have questions.  Get answers…See More
9 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service