I've been doing HP assessments for 12 years, but find myself a little limited in my knowledge of this issue.

Here's the scenario: I do an initial assessment where I find a 7-year old NG water heater with 1500 ppm undiluted CO. The homeowner brings in his plumber to "fix" it. The plumber, who doesn't own a CO monitor, cleans the burner and air intake grill, and proclaims it good. After work is done on the home, I re-test and find the CO to be even higher this time, and the draft weak.

What typically can be done to a fairly new water heater to fix the CO problem? The gas/air ratio must be out of wack, I'm thinking. Is it usually corrected by replacing the gas control valve?

The homeowner is left hanging, the plumber is without a clue and me telling him it needs to be corrected. I would recommend a different plumber, but I want to find out what a knowledgeable individual would typically do to correct this, short of replacing it. One thing I know is I need to align with a knowledgeable person to address this in the future.

John Shillito

Tags: CO, heater, plumber, water

Views: 472

Reply to This

Replies to This Discussion

I have to agree with Kurt. 2000 ppm is exceedingly high. I have tested hundreds of hot water heater (NG, Oil) and mostly they come in around 16 ppm. There is clearly something wrong and we all know that a gas hot water draft can easily be compromised. 

hey thanks for the links. Very informative on FVIR units

Hello John (and everyone else in the forum),

I'm a new visitor at this forum and it this is my first post. I look forward to more sharing and learning in the future.

The first condition that I would investigate the "weak draft". Is the flame lazy too? Is the equipment in place the same as what the flue was originally designed for?

I find the best place to contact when at a loss is the manufacturer's technical support.

Steve

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Trip Smith posted a discussion

Where to spend my marketing dollars?

Hey everyone, I'm a new home performance company owner. (Originally a general contractor who is…See More
28 minutes ago
Profile IconManuel Gutierrez, Chris Baker, Sharon Cannizzo and 1 more joined Home Energy Pros
2 hours ago
Kevin Jordan replied to Kevin Jordan's discussion air infiltration total
"thanks.  but it was just an illustration of a hole 2x2 with money going out of that…"
4 hours ago
Tom White posted a video

Adaptive Thermostats Demonstration Results Installed at UC Davis 6/26/2014

In buildings where variations in occupancy would fool a standard programmable thermostat, new adaptive thermostats have potential for significant energy savi...
7 hours ago
Hal Skinner's discussion was featured

Has Lead Based Paint ever stopped you on an energy upgrade?

In the process of determining all the different things that a home energy rater suggests to a…See More
8 hours ago
George Kopf's 2 discussions were featured
8 hours ago
George Kopf posted discussions
11 hours ago
Craig Bird replied to Hal Skinner's discussion What this RCC will do on an exterior wall compared to standard paint. in the group The RCC Classroom (Radiant Control Coatings)
"I agree and studies done will agree with you in those cases too - it makes sense when there is…"
23 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service