I've been doing HP assessments for 12 years, but find myself a little limited in my knowledge of this issue.

Here's the scenario: I do an initial assessment where I find a 7-year old NG water heater with 1500 ppm undiluted CO. The homeowner brings in his plumber to "fix" it. The plumber, who doesn't own a CO monitor, cleans the burner and air intake grill, and proclaims it good. After work is done on the home, I re-test and find the CO to be even higher this time, and the draft weak.

What typically can be done to a fairly new water heater to fix the CO problem? The gas/air ratio must be out of wack, I'm thinking. Is it usually corrected by replacing the gas control valve?

The homeowner is left hanging, the plumber is without a clue and me telling him it needs to be corrected. I would recommend a different plumber, but I want to find out what a knowledgeable individual would typically do to correct this, short of replacing it. One thing I know is I need to align with a knowledgeable person to address this in the future.

John Shillito

Tags: CO, heater, plumber, water

Views: 530

Reply to This

Replies to This Discussion

I have to agree with Kurt. 2000 ppm is exceedingly high. I have tested hundreds of hot water heater (NG, Oil) and mostly they come in around 16 ppm. There is clearly something wrong and we all know that a gas hot water draft can easily be compromised. 

hey thanks for the links. Very informative on FVIR units

Hello John (and everyone else in the forum),

I'm a new visitor at this forum and it this is my first post. I look forward to more sharing and learning in the future.

The first condition that I would investigate the "weak draft". Is the flame lazy too? Is the equipment in place the same as what the flue was originally designed for?

I find the best place to contact when at a loss is the manufacturer's technical support.

Steve

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Rick Karg replied to Carly@AirCycler's discussion The (Small) Cost of Ventilation Without Recovery
"As a member of the ASHRAE 62.2 committee (and president of Residential Energy Dynamics, the author…"
22 hours ago
Bradford E. White replied to Elizabeth Guinn's discussion ERV in need of backflow preventer.
"I would use an in-line backdraft damper such as Artis Industries or the ones made by Fantech and…"
yesterday
Kim Tanner posted a video

Wireless Air Leakage Testing

This webinar will discuss the use of WiFi technology to conduct and document blower door and duct leakage tests for compliance with local energy codes. The s...
yesterday
Profile IconPerry Grossman, Daniel Pate and Ottawa Furnace Filters joined Home Energy Pros
yesterday
Kirsten Richnavsky added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Breaking the link between unhealthy homes and unhealthy kids

Listen in on IAQ Radio to a discussion on reducing the household triggers that cause asthmaattacks…See More
yesterday
Kirsten Richnavsky posted a discussion

Breaking the link between unhealthy homes and unhealthy kids

Listen in on IAQ Radio to a discussion on reducing the household triggers that cause asthmaattacks…See More
yesterday
Kim Tanner posted events
yesterday
Ottawa Furnace Filters posted a blog post

Some Useful Information about Furnace Air Filters

There is not much we can do about the air pollution outside of a house in Ottawa, Canada, but we…See More
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service