I've been doing HP assessments for 12 years, but find myself a little limited in my knowledge of this issue.

Here's the scenario: I do an initial assessment where I find a 7-year old NG water heater with 1500 ppm undiluted CO. The homeowner brings in his plumber to "fix" it. The plumber, who doesn't own a CO monitor, cleans the burner and air intake grill, and proclaims it good. After work is done on the home, I re-test and find the CO to be even higher this time, and the draft weak.

What typically can be done to a fairly new water heater to fix the CO problem? The gas/air ratio must be out of wack, I'm thinking. Is it usually corrected by replacing the gas control valve?

The homeowner is left hanging, the plumber is without a clue and me telling him it needs to be corrected. I would recommend a different plumber, but I want to find out what a knowledgeable individual would typically do to correct this, short of replacing it. One thing I know is I need to align with a knowledgeable person to address this in the future.

John Shillito

Tags: CO, heater, plumber, water

Views: 693

Reply to This

Replies to This Discussion

I have to agree with Kurt. 2000 ppm is exceedingly high. I have tested hundreds of hot water heater (NG, Oil) and mostly they come in around 16 ppm. There is clearly something wrong and we all know that a gas hot water draft can easily be compromised. 

hey thanks for the links. Very informative on FVIR units

Hello John (and everyone else in the forum),

I'm a new visitor at this forum and it this is my first post. I look forward to more sharing and learning in the future.

The first condition that I would investigate the "weak draft". Is the flame lazy too? Is the equipment in place the same as what the flue was originally designed for?

I find the best place to contact when at a loss is the manufacturer's technical support.

Steve

RSS

Videos

  • Add Videos
  • View All

Latest Activity

Jan Green liked Chris Laumer-Giddens's blog post Rock Wool Insulation for Floor of High Performance Tiny House
2 hours ago
Carly Maltais posted a discussion

Comparing the AirCycler g2 and HRV [Infographic]

AirCycler is excited to share that we have recently launched a new version of our…See More
7 hours ago
SolyMoly, Inc posted discussions
8 hours ago
Home Energy Magazine's blog post was featured
13 hours ago
Brad Cook replied to Jim Tenhundfeld's discussion LED's and motion sensors
"I don't know what it stands for. See RAB.com"
Saturday
Jim Tenhundfeld replied to Jim Tenhundfeld's discussion LED's and motion sensors
"That makes sense since the same thing happened with dimmable CFL's.  I have never heard…"
Saturday
Brad Cook replied to Jim Tenhundfeld's discussion LED's and motion sensors
"My first thought is whether the motion sensor and/or the LED lamp is a cheap one. I had so many…"
Saturday
John Wagner joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
Friday

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service