I've been doing HP assessments for 12 years, but find myself a little limited in my knowledge of this issue.

Here's the scenario: I do an initial assessment where I find a 7-year old NG water heater with 1500 ppm undiluted CO. The homeowner brings in his plumber to "fix" it. The plumber, who doesn't own a CO monitor, cleans the burner and air intake grill, and proclaims it good. After work is done on the home, I re-test and find the CO to be even higher this time, and the draft weak.

What typically can be done to a fairly new water heater to fix the CO problem? The gas/air ratio must be out of wack, I'm thinking. Is it usually corrected by replacing the gas control valve?

The homeowner is left hanging, the plumber is without a clue and me telling him it needs to be corrected. I would recommend a different plumber, but I want to find out what a knowledgeable individual would typically do to correct this, short of replacing it. One thing I know is I need to align with a knowledgeable person to address this in the future.

John Shillito

Tags: CO, heater, plumber, water

Views: 473

Reply to This

Replies to This Discussion

I have to agree with Kurt. 2000 ppm is exceedingly high. I have tested hundreds of hot water heater (NG, Oil) and mostly they come in around 16 ppm. There is clearly something wrong and we all know that a gas hot water draft can easily be compromised. 

hey thanks for the links. Very informative on FVIR units

Hello John (and everyone else in the forum),

I'm a new visitor at this forum and it this is my first post. I look forward to more sharing and learning in the future.

The first condition that I would investigate the "weak draft". Is the flame lazy too? Is the equipment in place the same as what the flue was originally designed for?

I find the best place to contact when at a loss is the manufacturer's technical support.

Steve

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner replied to Hal Skinner's discussion An example of what an RCC can do with no R- insulation in the walls.
"Mornin Brett. 90 to 85, yes a slight variance there.  Same ASTM test, different scientists,…"
17 hours ago
Bret Curry replied to Hal Skinner's discussion An example of what an RCC can do with no R- insulation in the walls.
"Great information Hal. It appears the thermal emissivity in your test was .85 rather than .90. Are…"
18 hours ago
Juan Roca commented on Dale Stephens's blog post LED Lighting - Garage Door opener interference
"Hi,There is a real problem with remote controls and LED lights. However, there is a solution in the…"
yesterday
Profile IconJuan Roca and Elizabeth Coe joined Home Energy Pros
yesterday
Casey Gesell posted videos
yesterday
Gerald Shechter posted videos
yesterday
Hal Skinner replied to Hal Skinner's discussion An example of what an RCC can do with no R- insulation in the walls.
"Bret,  here are the 2 reports I referred…"
yesterday
Craig Foley shared George Kopf's discussion on Twitter
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service