What sort of leakage reduction could I expect if I try to plug all these tiny gaps?

This is a typical cathedral ceiling around these parts, 2x6 tongue and groove over 4x beams. In this image we're looking at a big valley rafter running diagonally in front, with a beam in the background at right. There are a couple of can lights and a couple of skylights in there too. This is after about 30 minutes with the door running and a 20 degree delta T. All of the beams have strips of trim, about 3/8" x 1", nailed on with brads. Lots of air comes out from behind that trim, where boards end. Relatively little comes out in the field, apparently because there's poly sheeting behind the 2x6.

It would be possible to pull each piece of trim with a flat bar, pull the nails, caulk behind it, drill a hole into each joint, inject more caulk in hopes of sealing the tongue/groove, and renail the trim. Some of this stuff is 16 feet in the air above the grand piano, really hard to get at. 

Ever done a test-in, test-out on leakage like this? Did you get big results? This house is well around 2 CFM50 per square foot, so it needs a major reduction.

Views: 191

Attachments:

Reply to This

Replies to This Discussion

I have sealed this before. IMO, it would be easier to run two beads of caulk on each side of trim rather than removing the trim piece. Unfortunately I didn't individually test the measure when I did the job, so I am not sure how much that contributed.

Hi David,

I've worked above expensive furnishings and either everything has to be moved or protected.  Drop that flat bar and no one is going to be happy.  Thus, I might consider the back door approach.  Do everything else and what is left is some base amount plus that ceiling.  If you can isolate that room in any way, some zone pressure readings might help identify how much is coming from where.  Again, even if you can't read that space, maybe you can read others.  Divide and conquer.

Bud

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

David Holtzclaw replied to Steve Mann's discussion Alnor 6200 LoFlo Capture Hood in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hi Steve I'm interested 402-213-3788 dholtzclaw@transductiontechnologies.com thanks david "
6 hours ago
Eric Kjelshus replied to Steve Mann's discussion Alnor 6200 LoFlo Capture Hood in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"call me Monday 816-537-5100 "
7 hours ago
Steve Mann added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Alnor 6200 LoFlo Capture Hood

I've got an Alnor 6200 Balometer (Flowhood) I'd like to get rid of. No longer needed--I have a big…See More
7 hours ago
Paul Raymer posted an event
Thumbnail

MA Crew Chief/BPI Building Analyst Training at Bristol Community College at Commonwealth Landing

September 12, 2016 at 9am to September 16, 2016 at 4:30pm
Bristol Community College has created a hands-on training cabin in their laboratory.  This class…See More
11 hours ago
Daniel Morrison replied to John Nicholas's discussion Slab Edge Insulation - A Side Thread to Melissa's Question
"John, I just collaborated with Steve Baczek on a few videos for ProTradeCraft about slab insulation…"
19 hours ago
Profile IconMichael Sumpter and Bill Gartner joined Home Energy Pros
yesterday
Malcolm Jackson joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
yesterday
Amber Vignieri liked tedkidd's discussion What if more efficient homes were actually worth more?
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service