I installed an ERV on my last job with the intake and exhaust utilizing 6" round hard duct.  I have no problem locating an exhaust vent cover for the exterior of the house with a backflow preventer.  However, I cannot locate an exterior cover with a backflow preventer for the INTAKE side of the system.  Does anything like this exist?

Views: 483

Reply to This

Replies to This Discussion

Hi Elizabeth, Zero experience with installing H/ERVs, but what you are looking for is probably a powered damper or powered latch.  Between the changing seasons where stack effect changes direction and the wind a passive solution would be challenging. 

What is the duty cycle on your ERV?  Is the home owner complaining or are you just anticipating this to be a problem?

Bud

Bud pretty much nailed it - only a powered damper would really help do what you are envisioning - I take it this unit only runs for part of the time? If it runs 24x7 then it is completely unnecessary & one could even argue probably unnecessary even for the short periods of time the unit is off unless connected to an HVAC unit which in that case per codes requires a mechanical damper

I could see flipping a damper and placing it in the duct work inside but the only catch with that is how much would it affect the amount of air being pulled in & are you creating any moisture / icing problems  

I would use an in-line backdraft damper such as Artis Industries or the ones made by Fantech and other ERV/HRV manufacturers.  The Fantech ones are mildly spring loaded but have a low pressure drop that I have measured at less than 0.04 inches water column. The Artis brand are gravity operated and even when installed level, the center post hinge axis is tipped back so gravity does the job.  If the duct runs uphill a bit, all the better. Remember these are positioned in direction of flow. You want to install them as close to the exterior as possible and insulate the ductwork from the building exit including past the damper. Being outside air ductwork, you want to insulate it all anyway, but on the exhaust, at least from the damper to the exterior.

http://www.artiscaps.com/products/backdraft-dampers/

http://www.amazon.com/Fantech-9800004-RSK-6-Backdraft-Damper/dp/B00...

Bud and Sean both asked a good question though, what is the duty cycle and on vs. off hours?  Typically we know that an ERV/HRV to be cost-effective, requires higher hours of operation. If manual cycle duty (e.g. a bath fan), I would use a direct exhaust fan for what might be a half hour a day.

I prefer simple and install these regardless and have not had reported problems, but then again, the systems operate for more hours than not. Not a lot of off-hours to show up back-drafting.

But yes too, you can install motorized dampers. Adds some complexity, interlocking and the question of if the damper is powered open/spring closed, which is what I think you would want. In a power failure the damper would fail closed.

http://www.heyokasolutions.com/Intake_or_Exhaust_Vent_Hood_for_6_Du...

Talk to Paul Raymer , he is contributor to this website.

http://www.southwarkmetal.com/product/butterfly-dampers/

I have made my own but some work better than others.    You can take sail skrap and fold in a way to make a one way damper.   Jump up to 7" - 8" so the presser drop is not to great.   Eric Kjelshus Energy HVAC.

First,  What is the 24/7 CFM requirement for your house?  

Second,  What is the CFM rating for the unit?

The most efficient ERVs run closest to 60 minutes out of each hour.  Buying a unit that moves 70 CFM is less capital outlay then one the moves 150 or 220 CFM.  45 - 60 CFM is a good range for many new homes.  If you are getting above that as a requirement, then does the house have 2 HVAC systems?  You should then consider going to two ERVs, if you plan to use the HVAC ductwork to distribute the air.

A better design strategy in larger homes would be to separate the systems. If you have a high performing building enclosure (below 5 ACH @ 50 blower door and above code insulation)  the shoulder seasons benefit greatly from an effective ERV distribution and collection.  Keeping the house comfortable when the inside temperature swings from 67 - 74 degrees for a week and the HVAC does not run is very energy efficient.  I see that when we have outside temperature swings from 50 - 80 degrees during the 24 hour period.

Over-kill unless you are in an arctic environment. 

Back flow preventer is a device used to protect potable water from the "back-flow" of non-potable fluids that may contaminate a water supply. 

Damper is the term you are searching for. 

RSS

Featured Forum Discussions

Too many BTU's. Too much horsepower?

Started by Steve in General Forum. Last reply by Eric Kjelshus 9 hours ago. 4 Replies

Stack/wind pressure and flow networks.

Started by Daniel James Grundy in Training. Last reply by Daniel James Grundy yesterday. 5 Replies

BDT with vermiculite in hollow CMU walls?

Started by Brad Cook in General Forum. Last reply by John Nicholas yesterday. 2 Replies

Strange IR Image

Started by Larry Nissman in General Forum. Last reply by Brad Cook Mar 9. 7 Replies

Videos

  • Add Videos
  • View All

Latest Activity

Eric Kjelshus replied to Steve's discussion Too many BTU's. Too much horsepower?
"Its more about run time with high RH removing, than to large over sized AC unit, in houses.  …"
9 hours ago
Sarah OConnell posted a blog post

Crowdsourcing for Innovation

Share Your Ideas!Novel Building Envelope Design for Increased Thermal PerformanceIn 2014, more than…See More
23 hours ago
Colin de Paor is now a member of Home Energy Pros
yesterday
Walter Ahlgrim replied to Steve's discussion Too many BTU's. Too much horsepower?
"The 5 ton system you have is not 500 hp racecar engines they are 500 hp truck engines. The duct…"
yesterday
Daniel James Grundy replied to Daniel James Grundy's discussion Stack/wind pressure and flow networks.
"So I wanted to start with a basic who can help then go into more detail later. But yes find…"
yesterday
Daniel James Grundy replied to Daniel James Grundy's discussion Stack/wind pressure and flow networks.
"My tutor got back to me and while areas don't quite feel right a little to much assumptions…"
yesterday
Brennan Less replied to Daniel James Grundy's discussion Stack/wind pressure and flow networks.
"Daniel, I'm assuming you're trying to predict the airflows through the different openings…"
yesterday
Martin Newmark joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
yesterday

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service