I am working on a 1950's colonial with attic insulation consisting of 2"x6" joists filled with loose fill fiberglass. The fiberglass is covered by 1" x 6" decking with 1/4" between the boards. I am recommending adding cellulose to improve the air barrier and insulate. My question is whether I can get away with not removing the old boards, or maybe removing every third one? How much area is needed to ensure moisture can dry to the outside? It should not get damp because of proper ventilation.
The upfront cost of retrofits is a big barrier to comprehensive weatherization. Anything I can do to reduce the cost of installation will help.
Thanks.

Views: 223

Reply to This

Replies to This Discussion

Thanks for asking this question - I've actually been wondering the same thing for personal use. I hadn't thought of the every-third-board idea (seems a good thought), but was instead pondering how far sideways I could shoot sprayfoam (the decking doesn't extend to where the sloped roof gets very low). There's currently ~1" of ancient cellulose in my attic and I'm a total hypocrite for not doing anything about it in the year we've been in the house!

Also need to decide whether or not to shop-vac up the cellulose before sprayfoaming. Thoughts?

Best case is that you remove the boards and the existing insulation completely before doing air sealing--the loose FG has only marginal value, an inch of cellulose almost none. Ideally you are going to install 16-18" of insulation, so the boards will be buried and doing you no good anyway, in the long term.

 

Second best is to carefully move insulation aside so that you can still do a thorough job.

 

If there's a moisture issue, it's probably going to come from air leakage into the attic, not the presence of the boards, so the air sealing is critical. 

Just adding cellulose insulation will not improve your air barrier.  I would recommend removing the floor boards, spot air-sealing with foam (and rigid if necessary) at bypasses, etc. and installing new cellulose or FG.  I would not recommend replacing the boards unless you plan on raising the platform to accommodate adequate insulation.  I discourage attic storage --what's the R-value of a box of christmas ornaments or a suitcase crushing insulation near the platform?

 

Depending on the strength of the ceiling below and no can-lights, etc, you may be able to remove the existing insulation and dense-pack insulation below the boards from the ends or via drilled holes into or removal of certain boards.  You may not achieve enough thickness and I would still be concerned with air and moisture migration since it's not a truly enclosed cavity.

 

If the air barrier is good at the ceiling below (obviously with no can-lights), you could just add more insulation on top of everything.  Seal and bury the ducts as well.  Avoid or replace your knob-n-tube wiring!

This seems to come up often, especially when customers want to keep the floor boards in place for storage.  Best solution would be to remove floor boards, allowing for proper air sealing and achieve a minimum of R-38.  Another option is to remove some boards to air seal, then inject dense pack cellulose.  But, you will only get R-24.  Not so great, and the utilities may not grant you an exception.  Third option, inject foam into cavity (use injection foam and not spray foam). This will take care of air sealing, but again you only get R-30.  Option 3 can also present some IAQ issues.  If it comes into contact with any formaldehyde baring material, the formaldehyde will off-gas.  Injection foam on a flat surface can also warp the material on which it sits.  

 

So, remove the floor boards, do the job right and get rid of the old junk you are trying to store!  IMHO.

In order to do make a substantial difference in the air sealing of your home (this is possible!) you have got to be able to access the ceiling and do some caulking, foaming and rigid batting of air leaks.  While I feel for you and all the work it is going to take in order to remove boards and existing insulation, you will be far ahead by doing so.  My recommendation would be to visit the local temporary labor business in town and get a couple of people to help you for a day.  I imagine you could get some serious work done removing these hindrances in a solid day of work.  No one is going to go back to do air sealing once you have blown additional insulation in your attic.  What you decide now will be there for the next multiple decades.  Bite the bullet!

Your last two statements, "The upfront cost of retrofits is a big barrier to comprehensive weatherization. Anything I can do to reduce the cost of installation will help," are compelling. You need a solution that makes sense, given the conditions.

 

I'd pull up every third or fourth board, as well as the perimeter boards, install baffles, and blow it to r-38 or r-49, infilling where there are voids in the existing fiberglass.

 

Even then, pulling the boards from anywhere but the perimeter may be superfluous. You could blow 16" on top and make sure the ends at the baffles are well-filled. And if the customer insists on retaining some floor space, build a dam around a section and call it good.

 

This may only be an 80% solution, but it may make the difference between an upgrade sold and efficiency gain lost.

 

We need to consider the extent to which some of our austere approaches to home performance scares off our customers, and sends the public a message that our field is unapolegetically fixed and inflexible. We don't have enough credibility among the masses to take that kind of approach. Yet.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Eric Kjelshus replied to Johnny Ritzo's discussion Selecting a Water Heater
"I have been using  Rheem or State or Brad/white PVC flued tank type hot water heater…"
2 hours ago
Bachi Brunato replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"As it turns out, we have 10 Halo 99RT housings with Halo 998P Eyeball trim in the kitchen. The trim…"
4 hours ago
Bachi Brunato's discussion was featured

Boxing and Insulating Around Non-ICAT Cans

I have a client with 16) 4" halogen recessed light fixtures in the attic.I'd like to cover the cans…See More
6 hours ago
Johnny Ritzo's discussion was featured

Selecting a Water Heater

I am looking at updating the heating and water heating systems in a rental home I recently…See More
6 hours ago
George Kopf's discussion was featured

Misting Aeroseal in Pressurized Home = Amazing Air Sealing Innovation

As a training program manager for a non-profit, I am often too busy managing my program to catch…See More
6 hours ago
Tom Delconte's blog post was featured
6 hours ago
Christopher Morin's blog post was featured

Selling with Rebates: The Simple Payback

  The easiest way to show a homeowner how their investment in high-efficient equipment will help…See More
6 hours ago
Edward Foskey's blog post was featured
6 hours ago
Mike Rogers's blog post was featured

HOMES Act introduced with Bi-Partisan Sponsorship

We don't see a lot of bi-partisan bills in Congress these days. Here's one focusing on home…See More
6 hours ago
Mike Rogers posted a blog post

HOMES Act introduced with Bi-Partisan Sponsorship

We don't see a lot of bi-partisan bills in Congress these days. Here's one focusing on home…See More
10 hours ago
David Eggleton replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"That varies, as policies are different from state to state."
10 hours ago
Orvil D Boyer replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I have a Fluke TIR 32.  Used aproximately 10 times 1.5 yrs old.  This is the first…"
10 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service