I am working on a 1950's colonial with attic insulation consisting of 2"x6" joists filled with loose fill fiberglass. The fiberglass is covered by 1" x 6" decking with 1/4" between the boards. I am recommending adding cellulose to improve the air barrier and insulate. My question is whether I can get away with not removing the old boards, or maybe removing every third one? How much area is needed to ensure moisture can dry to the outside? It should not get damp because of proper ventilation.
The upfront cost of retrofits is a big barrier to comprehensive weatherization. Anything I can do to reduce the cost of installation will help.
Thanks.

Views: 649

Reply to This

Replies to This Discussion

Thanks for asking this question - I've actually been wondering the same thing for personal use. I hadn't thought of the every-third-board idea (seems a good thought), but was instead pondering how far sideways I could shoot sprayfoam (the decking doesn't extend to where the sloped roof gets very low). There's currently ~1" of ancient cellulose in my attic and I'm a total hypocrite for not doing anything about it in the year we've been in the house!

Also need to decide whether or not to shop-vac up the cellulose before sprayfoaming. Thoughts?

Best case is that you remove the boards and the existing insulation completely before doing air sealing--the loose FG has only marginal value, an inch of cellulose almost none. Ideally you are going to install 16-18" of insulation, so the boards will be buried and doing you no good anyway, in the long term.

 

Second best is to carefully move insulation aside so that you can still do a thorough job.

 

If there's a moisture issue, it's probably going to come from air leakage into the attic, not the presence of the boards, so the air sealing is critical. 

Just adding cellulose insulation will not improve your air barrier.  I would recommend removing the floor boards, spot air-sealing with foam (and rigid if necessary) at bypasses, etc. and installing new cellulose or FG.  I would not recommend replacing the boards unless you plan on raising the platform to accommodate adequate insulation.  I discourage attic storage --what's the R-value of a box of christmas ornaments or a suitcase crushing insulation near the platform?

 

Depending on the strength of the ceiling below and no can-lights, etc, you may be able to remove the existing insulation and dense-pack insulation below the boards from the ends or via drilled holes into or removal of certain boards.  You may not achieve enough thickness and I would still be concerned with air and moisture migration since it's not a truly enclosed cavity.

 

If the air barrier is good at the ceiling below (obviously with no can-lights), you could just add more insulation on top of everything.  Seal and bury the ducts as well.  Avoid or replace your knob-n-tube wiring!

This seems to come up often, especially when customers want to keep the floor boards in place for storage.  Best solution would be to remove floor boards, allowing for proper air sealing and achieve a minimum of R-38.  Another option is to remove some boards to air seal, then inject dense pack cellulose.  But, you will only get R-24.  Not so great, and the utilities may not grant you an exception.  Third option, inject foam into cavity (use injection foam and not spray foam). This will take care of air sealing, but again you only get R-30.  Option 3 can also present some IAQ issues.  If it comes into contact with any formaldehyde baring material, the formaldehyde will off-gas.  Injection foam on a flat surface can also warp the material on which it sits.  

 

So, remove the floor boards, do the job right and get rid of the old junk you are trying to store!  IMHO.

In order to do make a substantial difference in the air sealing of your home (this is possible!) you have got to be able to access the ceiling and do some caulking, foaming and rigid batting of air leaks.  While I feel for you and all the work it is going to take in order to remove boards and existing insulation, you will be far ahead by doing so.  My recommendation would be to visit the local temporary labor business in town and get a couple of people to help you for a day.  I imagine you could get some serious work done removing these hindrances in a solid day of work.  No one is going to go back to do air sealing once you have blown additional insulation in your attic.  What you decide now will be there for the next multiple decades.  Bite the bullet!

Your last two statements, "The upfront cost of retrofits is a big barrier to comprehensive weatherization. Anything I can do to reduce the cost of installation will help," are compelling. You need a solution that makes sense, given the conditions.

 

I'd pull up every third or fourth board, as well as the perimeter boards, install baffles, and blow it to r-38 or r-49, infilling where there are voids in the existing fiberglass.

 

Even then, pulling the boards from anywhere but the perimeter may be superfluous. You could blow 16" on top and make sure the ends at the baffles are well-filled. And if the customer insists on retaining some floor space, build a dam around a section and call it good.

 

This may only be an 80% solution, but it may make the difference between an upgrade sold and efficiency gain lost.

 

We need to consider the extent to which some of our austere approaches to home performance scares off our customers, and sends the public a message that our field is unapolegetically fixed and inflexible. We don't have enough credibility among the masses to take that kind of approach. Yet.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

R Higgins replied to Energy Wise Solutions's discussion No Utility Homes, Are we ready to start building Homes that are not connected to traditional utilities ?
"First off, check the laws in your area.  Drought prone areas often prohibit on site collection…"
1 hour ago
R Higgins commented on Tom White's video
Thumbnail

Building Science Insights -- To Vent or Not to Vent

"Great lecture, kept thinking, but what about existing buildings.  Too little room at eaves for…"
1 hour ago
Luis Imery added a discussion to the group Job Board
Thumbnail

Hiring: Construction Manager with High Performance Custom Home Experience

POSITION DESCRIPTIONJob Title: Construction ManagerDepartment: Construction –…See More
21 hours ago
Profile IconLuis Imery and Quinn Korzeniecki joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
21 hours ago
Colin Genge posted an event

Retrotec is attending the NEBB Testing and Balancing (Tab) Certified Professional Review Seminar in Chicago, IL at Hilton Chicago O’Hare Airport

June 6, 2016 at 8am to June 8, 2016 at 5pm
Building owners and tenants are concerned that the environmental performance of buildings must be…See More
yesterday
Colin Genge updated an event
Thumbnail

Retrotec is exhibiting at the NFPA Conference & Expo-Booth 1355 at Mandalay Bay Convention Center

June 13, 2016 at 8am to June 16, 2016 at 5pm
NFPA's Conference & Expo is widely regarded as the most comprehensive industry event for…See More
yesterday
Tom White posted a video

Hayward Healthy Home Principles and Products

Bill Hayward discusses the principles that were used to build the first Hayward Healthy Home and how the products were evaluated for toxicity before they wer...
yesterday
Tom White's video was featured

Building Science Insights -- To Vent or Not to Vent

Building Science Presentation with Dr. Joseph Lstiburek.
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service