If one had a large-scale home retrofit program with the goal of saving energy, what would be the pros and cons of a policy to replace all standing pilot light furnaces?  Health and safety improvements count, as do energy savings.

Views: 5668

Reply to This

Replies to This Discussion

1) Turn down the gas pressure, that is a crazy big pilot

2) Replacing this cast iron beauty is a lot more complicated than it sounds. Unless the distribution system is also updated, return water temps will be >120F resulting in your new 90%+ mod con boiler running at 80% efficiency. A boiler like this if running properly will be 75% efficient.

3) The coal soot left in every possible place throughout the distribution system will plug up the low flow heat exchanger of any 90%+ boiler I have seen except the Burnham Revolution. I learned this the hard way!

4) Most people do not have the funds for boiler replacement and serious weatherization upgrades. When forced to choose, I will recommend the weatherization every time.

5) In 50 years when this boiler is still running without issues, how many times will the tech have to come out and service the mod con that is now past it's useful life? If you follow the manufacturer's advice, 16 cleanings at $100 each adds $1600 to the cost of operation.

Most HVAC contractors make their money with changing these old dogs out, but they still have their place. By reducing the load, through air sealing and insulating we reduce the fuel used and if after that the homeowner still wants to buy a Prius or solar panels or a new mod con boiler, then great, but not until the enclosure is tight.

Health and safety improvements count, as do Secure Home Services  If one had a large-scale home retrofit program with the goal of saving energy, what would be the pros and cons of a policy to replace all standing pilot light furnaces?  

Biggest pro is to keep the clay or brick or high mass chimney warm  with the 4-8" flame.   We can waste 50-70,000 BTU hr just to keep the flue working.

If firing rate = 100,000 Btu/hr and SSE = 75%, then 75,000 Btu/hr go to the distribution system and 25,000 Btu/hr go through the vent.If the burner on-cycle is 12 minutes (.2 hrs), then during one cycle the vent receives: .2 hr x 25,000 Btu/hr = 5,000 Btu/cycle MASONRY CHIMNEY:A masonry chimney (block or brick + tile liner) requires about 4570 Btu/.ft. to go from 0 deg to 120 deg. So, on a very cold day, about one foot of chimney will be warmed in one burner cycle: 5,000 Btu/cycle @4,570Btu/ft = 1 ft/cycle TYPE B-VENT CHIMNEY:A 6" B-vent chimney requires about 90 Btu/.ft. to go from 0o to 120o. So,5,000 Btu/cycle @ 90Btu/ft = 55 ft/cycle

1) is correct.

2) is not. We install dozens of condensing boilers a year, and I clock them regularly. A sealed combustion/condensing boiler with a vertical/counterflow heat exchanger (think Triangle Tube "Prestige" or Weil McLain "Ultra") runs with an exhaust temp 10 to 20 degrees lower than the supply temp. I routinely test boilers delivering 160 degree supply that have 140 degree exhaust gas and 89% to 93% SSE.

3) "Coal soot" in the distribution fluid is physically impossible. Maybe you are referring to corrosion products and particulates -- a REALLY common problem in old systems originally built for steam, with steel or iron plumbing and radiation. Flush, flush, flush, get the water chemistry right, install a good strainer, and MAINTAIN the system.

4) I sure wish these decisions were always that simple...

5) Wrong again. That 50 year old boiler SHOULD have been serviced every year or two, same as the new one. The only difference is that it will run (poorly to sort-of OK) for years regardless of the neglect. You could have said the same thing about my 1973 AMC Matador, too. But that doesn't mean I want the darn thing back -- no way! The fact that the old cast iron system doesn't shut down due to neglect is a problem, not an advantage.

Makes sense. Egt could be very close to as low as return water temp, not supply water.

My indirect seems to satisfy when return temp hits 115f.

Standing pilot units should be replaced but not for energy savings due to the capital cost.  Suggest to replace with sealed combustion units when old unit fails.  In the mean time shut off pilots in spring and re-light in the fall 

RSS

Featured Forum Discussions

Too many BTU's. Too much horsepower?

Started by Steve in General Forum. Last reply by Eric Kjelshus yesterday. 4 Replies

Stack/wind pressure and flow networks.

Started by Daniel James Grundy in Training. Last reply by Daniel James Grundy on Thursday. 5 Replies

BDT with vermiculite in hollow CMU walls?

Started by Brad Cook in General Forum. Last reply by John Nicholas on Thursday. 2 Replies

Strange IR Image

Started by Larry Nissman in General Forum. Last reply by Brad Cook Mar 9. 7 Replies

Videos

  • Add Videos
  • View All

Latest Activity

Derrick Brodanex joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
19 hours ago
Eric Kjelshus replied to Steve's discussion Too many BTU's. Too much horsepower?
"Its more about run time with high RH removing, than to large over sized AC unit, in houses.  …"
yesterday
Sarah OConnell posted a blog post

Crowdsourcing for Innovation

Share Your Ideas!Novel Building Envelope Design for Increased Thermal PerformanceIn 2014, more than…See More
Friday
Colin de Paor is now a member of Home Energy Pros
Friday
Walter Ahlgrim replied to Steve's discussion Too many BTU's. Too much horsepower?
"The 5 ton system you have is not 500 hp racecar engines they are 500 hp truck engines. The duct…"
Friday
Daniel James Grundy replied to Daniel James Grundy's discussion Stack/wind pressure and flow networks.
"So I wanted to start with a basic who can help then go into more detail later. But yes find…"
Thursday
Daniel James Grundy replied to Daniel James Grundy's discussion Stack/wind pressure and flow networks.
"My tutor got back to me and while areas don't quite feel right a little to much assumptions…"
Thursday
Brennan Less replied to Daniel James Grundy's discussion Stack/wind pressure and flow networks.
"Daniel, I'm assuming you're trying to predict the airflows through the different openings…"
Thursday

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service