I've noticed my new furnace uses about the same electrical power to operate as my old furnace, even though the new furnace (44k) is 1/2 the BTU of he old one (88k). Both furnaces use 1/3HP 5amp blower motors, old furnace was on high speed, new furnace was on low. New furnace uses a 1.8amp shaded pole inducer motor and is considerably larger than my previous furnace inducer. I didn't get the amp rating on the old furnace inducer, but it was a standard 'c frame' motor, most are about 1amp. Condensing furnaces do tend to use much larger inducer motors overall.

I write this post because I've noticed the increased electrical consumption with lower temperatures. Electrical efficiency isn't mentioned in furnace specs, but it appears to contribute considerably to operation costs.

Views: 91

Attachments:

Reply to This

Replies to This Discussion

Have you looked into any of the ECM motors? I hear they consume less electricity. It would probably take a couple years to pay for itself in savings, but with a new furnace, it may be worth looking into.

http://www.youtube.com/watch?v=YjoY6hRSudk

This motor looks like a good bet.

ECM could be the way to go. At $250 it does have a long payback though. The use of a 1.8A Shaded Pole inducer motor seems wasteful, a PSC would use 1/2 the power to do the same job.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Profile IconAmanda Hallock, Kalvis, Tyler Grubbs and 6 more joined Home Energy Pros
2 hours ago
Corbett Lunsford posted videos
2 hours ago
Sean Lintow Sr replied to randy tolowski's discussion Another unvented roof question
3 hours ago
randy tolowski posted discussions
5 hours ago
Todd Collins replied to Tom Strumolo's discussion Ancient (70's) wall foam insulation, now a powder.
"What did you find about the dust?  "
9 hours ago
Susan E. Buchan commented on Shawna Henderson's blog post Drainwater Heat Recovery Units & Water Efficiency
"Makes sense, Shawna. Thanks"
9 hours ago
Shawna Henderson commented on Shawna Henderson's blog post Drainwater Heat Recovery Units & Water Efficiency
"Susan, I'm not sure that insulation on the unit would be of great benefit, as the drainwater…"
9 hours ago
Susan E. Buchan posted events
9 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service