I've noticed my new furnace uses about the same electrical power to operate as my old furnace, even though the new furnace (44k) is 1/2 the BTU of he old one (88k). Both furnaces use 1/3HP 5amp blower motors, old furnace was on high speed, new furnace was on low. New furnace uses a 1.8amp shaded pole inducer motor and is considerably larger than my previous furnace inducer. I didn't get the amp rating on the old furnace inducer, but it was a standard 'c frame' motor, most are about 1amp. Condensing furnaces do tend to use much larger inducer motors overall.

I write this post because I've noticed the increased electrical consumption with lower temperatures. Electrical efficiency isn't mentioned in furnace specs, but it appears to contribute considerably to operation costs.

Views: 78

Attachments:

Reply to This

Replies to This Discussion

Have you looked into any of the ECM motors? I hear they consume less electricity. It would probably take a couple years to pay for itself in savings, but with a new furnace, it may be worth looking into.

http://www.youtube.com/watch?v=YjoY6hRSudk

This motor looks like a good bet.

ECM could be the way to go. At $250 it does have a long payback though. The use of a 1.8A Shaded Pole inducer motor seems wasteful, a PSC would use 1/2 the power to do the same job.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Hi KLurt. I would isagree with the comment that the attic floor is heated by the…"
5 minutes ago
Craig Bird commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Now back to your question - the best data for radiant barriers is the DOE studies from the ORNL.…"
16 minutes ago
Kevin Jordan posted a discussion

Does anyone have pointers on approaching real estate induatry.

Hello All!!I am figuring on approaching the real estate and low income housing industries here in…See More
20 minutes ago
Craig Bird commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Kurt - Radiant heat transfer does not heat the air. It is the passing heat directly from hot object…"
28 minutes ago
Steven Turetsky replied to John Shillito's discussion Fixing a water heater?
"Hello John (and everyone else in the forum), I'm a new visitor at this forum and it this is my…"
30 minutes ago
Kevin Jordan posted a status
"I have questions about approaching the real estate industry? I need help."
31 minutes ago
Kurt Shafer commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"And, Mr. Bird, in my experience the attic floor is not heated by radiation from the roof so much as…"
52 minutes ago
Kurt Shafer commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Mr. Byrd,  I did not accept my IR camera data off hand, I could FEEL the heat. What I am…"
54 minutes ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service