Location Seattle

Winter design temp 28

Heating Degree days 4797

Design Temp 80/64

South facing with lots of windows u28

My question is I have new construction  3000sqft 2 story house. The living room is 2 story the rest will have a 9 ft ceiling.  I haven't used the ductless and am wondering with the 2 story living room which would be most efficient and comfortable to heat the main living area. My concern is with the 2 story living room the ductless will be less comfortable because all the heat will go upstairs causing the lower level to be either colder or the upstairs to be hot.  The other concern is with the ductless will there be a noticeable breeze.  The Radiant would be under floor type with hardwoods. 

thanks

Views: 5940

Reply to This

Replies to This Discussion

Do you have any need for cooling or dehumidification? If you don't, I don't see that this would be an application for a ductless heatpump.  

You're correct that radiant will not create a temperature gradient between floor and ceiling, and will be most comfortable. 

One challenge may be the slow response of radiant due to the mass of the floor - even a wood floor. For instance I do not setback my radiant at night because it simply takes too long. If you have long shoulder seasons where you'd be heating at night and be off during the day, you may want to consider a second zone with panel radiators on the wall, which respond very quickly and are also very comfortable. If you oversize them you can run them at the same temperature as the radiant and won't need a mixing valve.

Now if I was to build a new home for myself right now, I'd use a water to water geothermal heatpump to supply my radiant and go 100% electric.

thanks

Why 100% electric.

  •  100% electric makes it easier to go net zero.
  • A heatpump allows both heating and cooling in one unit, where with a gas/oil boiler/furnace I'd need a separate A/C unit.
  • High efficiency combustion equipment requires regular maintenance/cleaning to run well and have a long service life. Electric equipment generally requires less maintenance.
  • 100% also allows to go off-grid or run when there is a power-outage (provided I have backup).
  • Looking at one energy bill (electric) and you know your performance.

Joachim, if you are in a mild climate all the performance risks and capital expense of geo become hard to justify. Air to water should be considered for radiant, and is likely to mean less risk, first cost, and more actual efficiency (not theoretical efficiency).

Depending on house size and enclosure efficiency, straight electric radiant might even make sense. If annual btu load is small, efficiency of delivery may not justify complexity or capital cost of any type of heat pump.

James, be careful of radiant sales people selling false justification for radiant. if you don't go cheap on your ductless split or enclosure thermal quality, it is unlikely you will even be able to tell ductless is running. The ductless I've sold, you have to go over to it and put your hand in front of the grille to know if it is running.

James wrote 4800 HDD, which I would not consider a mild climate.

Super insulated homes can achieve heat loads so low instead of a geothermal vertical well a slinky can be installed under the foundation at very little cost bringing the price for geothermal down tremendously.

Modern air to air and air to water heat pumps can certainly achieve some very impressive efficiencies, however I am not a fan of them because the outdoor unit harasses the neighbor in dense neighborhoods.

We are a mild climate, tight enclosure. The ductless seems to be very efficient.  My objective is to keep the monthly bill lower but comfort is the most important factor.  With install costs being similar my concern is with the 2 story living room (18x20).  If I use a air heat pump or gas furnace I have multiple vents for each room.  With the ductless I have 1 or 2 heads for the main level (about 1100sqft open concept).  Will that evenly heat the entire main level?

James,

People mistake the effect of stack leakage as stratification.  The distinction is important.  Heat wants to equalize.  Stratification takes energy.  If you do not have large temperature deltas, you will not see the stratification you worry about.  If you heat with a wood stove, you WILL see stratification and have the need to mix.  

Stack leakage is buoyant heated air rising up and pushing out of your home through high holes, and cold air being sucked in to replace it through low holes (btw, the reverse happens in summer). Often people mistake temperature variance as stratification when it's actually this cold leaking in low, and warm leaking out high.  If you have a good enclosure, this leakage is so minimal this variance goes away.    

Here are homes in Mass that heat with mini-splits.  http://bit.ly/netzeroMass  

You get how much colder it is in Mass than where you are?  I'm in similar climate in NY and we've had temps in single digits just about every week since November.   

We should mention that Transformations' homes in MA have 12" Double Studded R-45 Low Density Foam Walls and typically not a lot of glazing. An 1,800 sqft home may have two mini-splits on the first floor and one on the second floor.

If there is no hot air in the room, there's nothing to rise to the ceiling. In other words if you don't have great heat loss in that living room that would require the mini splits to produce air that is significantly hotter than ambient, you won't have to worry about hot air rising. Pick a quality model with ECM blower and variable refrigerant flow that modulates instead of cycling on and off. 

An open floor plan is essential for even distribution on the main level. With a tight enclosure you should have an HRV/ERV with strategically placed exhaust and supply, which will also promote distribution.

4800 seems pretty mild to me. Which do you think impacts efficiency, hdd, or average winter temperature? If you have long mild winters, air source is likely to be more efficient than ground source.

I don't know many people willing to throw thousands of dollars away so their neighbors don't have to listen to condensers. I think that argument sinks at launch except for 'Portlandia' types - you know, folks that put solar panels facing north because they want them facing the street so people can see them...

That said, better units are significantly quieter and people ARE sometimes inclined to invest in the better units for their lower db.

Quality of life is very important to me, and I am trying to convince my customers that 'you get what you pay for'.

But each their own and I don't think we're adding value to James' question above. Cheers!

RSS

Forum Discussions

What causes a temperature plane in a home

Started by Energy Wise Solutions in HVAC. Last reply by Eric Kjelshus yesterday. 9 Replies

Solar panel leasing

Started by Luis Hernandez in General Forum. Last reply by John Nicholas yesterday. 15 Replies

Factory built Net Zero

Started by Steven Lefler in General Forum. Last reply by Steven Lefler May 18. 3 Replies

Latest Activity

Chad Nicholson is now a member of Home Energy Pros
yesterday
Eric Kjelshus replied to Energy Wise Solutions's discussion What causes a temperature plane in a home
"Hot air goes up and cool air goes down.   I put in returns high and low.  In summer use…"
yesterday
John Nicholas replied to Luis Hernandez's discussion Solar panel leasing
"The variables in buying a solar panel installation: Equipment -  Length of all Guarantees,…"
yesterday
Richard Drohan liked Brian Sipp's discussion Minneapolis Duct Blaster System with DG-700 For Sale
Thursday

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service