Location Seattle

Winter design temp 28

Heating Degree days 4797

Design Temp 80/64

South facing with lots of windows u28

My question is I have new construction  3000sqft 2 story house. The living room is 2 story the rest will have a 9 ft ceiling.  I haven't used the ductless and am wondering with the 2 story living room which would be most efficient and comfortable to heat the main living area. My concern is with the 2 story living room the ductless will be less comfortable because all the heat will go upstairs causing the lower level to be either colder or the upstairs to be hot.  The other concern is with the ductless will there be a noticeable breeze.  The Radiant would be under floor type with hardwoods. 

thanks

Views: 512

Reply to This

Replies to This Discussion

Do you have any need for cooling or dehumidification? If you don't, I don't see that this would be an application for a ductless heatpump.  

You're correct that radiant will not create a temperature gradient between floor and ceiling, and will be most comfortable. 

One challenge may be the slow response of radiant due to the mass of the floor - even a wood floor. For instance I do not setback my radiant at night because it simply takes too long. If you have long shoulder seasons where you'd be heating at night and be off during the day, you may want to consider a second zone with panel radiators on the wall, which respond very quickly and are also very comfortable. If you oversize them you can run them at the same temperature as the radiant and won't need a mixing valve.

Now if I was to build a new home for myself right now, I'd use a water to water geothermal heatpump to supply my radiant and go 100% electric.

thanks

Why 100% electric.

  •  100% electric makes it easier to go net zero.
  • A heatpump allows both heating and cooling in one unit, where with a gas/oil boiler/furnace I'd need a separate A/C unit.
  • High efficiency combustion equipment requires regular maintenance/cleaning to run well and have a long service life. Electric equipment generally requires less maintenance.
  • 100% also allows to go off-grid or run when there is a power-outage (provided I have backup).
  • Looking at one energy bill (electric) and you know your performance.

Joachim, if you are in a mild climate all the performance risks and capital expense of geo become hard to justify. Air to water should be considered for radiant, and is likely to mean less risk, first cost, and more actual efficiency (not theoretical efficiency).

Depending on house size and enclosure efficiency, straight electric radiant might even make sense. If annual btu load is small, efficiency of delivery may not justify complexity or capital cost of any type of heat pump.

James, be careful of radiant sales people selling false justification for radiant. if you don't go cheap on your ductless split or enclosure thermal quality, it is unlikely you will even be able to tell ductless is running. The ductless I've sold, you have to go over to it and put your hand in front of the grille to know if it is running.

James wrote 4800 HDD, which I would not consider a mild climate.

Super insulated homes can achieve heat loads so low instead of a geothermal vertical well a slinky can be installed under the foundation at very little cost bringing the price for geothermal down tremendously.

Modern air to air and air to water heat pumps can certainly achieve some very impressive efficiencies, however I am not a fan of them because the outdoor unit harasses the neighbor in dense neighborhoods.

We are a mild climate, tight enclosure. The ductless seems to be very efficient.  My objective is to keep the monthly bill lower but comfort is the most important factor.  With install costs being similar my concern is with the 2 story living room (18x20).  If I use a air heat pump or gas furnace I have multiple vents for each room.  With the ductless I have 1 or 2 heads for the main level (about 1100sqft open concept).  Will that evenly heat the entire main level?

James,

People mistake the effect of stack leakage as stratification.  The distinction is important.  Heat wants to equalize.  Stratification takes energy.  If you do not have large temperature deltas, you will not see the stratification you worry about.  If you heat with a wood stove, you WILL see stratification and have the need to mix.  

Stack leakage is buoyant heated air rising up and pushing out of your home through high holes, and cold air being sucked in to replace it through low holes (btw, the reverse happens in summer). Often people mistake temperature variance as stratification when it's actually this cold leaking in low, and warm leaking out high.  If you have a good enclosure, this leakage is so minimal this variance goes away.    

Here are homes in Mass that heat with mini-splits.  http://bit.ly/netzeroMass  

You get how much colder it is in Mass than where you are?  I'm in similar climate in NY and we've had temps in single digits just about every week since November.   

We should mention that Transformations' homes in MA have 12" Double Studded R-45 Low Density Foam Walls and typically not a lot of glazing. An 1,800 sqft home may have two mini-splits on the first floor and one on the second floor.

If there is no hot air in the room, there's nothing to rise to the ceiling. In other words if you don't have great heat loss in that living room that would require the mini splits to produce air that is significantly hotter than ambient, you won't have to worry about hot air rising. Pick a quality model with ECM blower and variable refrigerant flow that modulates instead of cycling on and off. 

An open floor plan is essential for even distribution on the main level. With a tight enclosure you should have an HRV/ERV with strategically placed exhaust and supply, which will also promote distribution.

4800 seems pretty mild to me. Which do you think impacts efficiency, hdd, or average winter temperature? If you have long mild winters, air source is likely to be more efficient than ground source.

I don't know many people willing to throw thousands of dollars away so their neighbors don't have to listen to condensers. I think that argument sinks at launch except for 'Portlandia' types - you know, folks that put solar panels facing north because they want them facing the street so people can see them...

That said, better units are significantly quieter and people ARE sometimes inclined to invest in the better units for their lower db.

Quality of life is very important to me, and I am trying to convince my customers that 'you get what you pay for'.

But each their own and I don't think we're adding value to James' question above. Cheers!

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner replied to Richard Beyer's discussion Spontaneous Combustion and Flash Fire regarding Spray Foam Insulation
"Richard, here is something else that might be pertinent. In my hundreds of conversations with our…"
5 hours ago
Trip posted a discussion

Starting a Home Weatherization Business. Considering it...

I am considering starting a home weatherization business. (I live in Southeast Alabama)  Currently…See More
6 hours ago
Jim Gunshinan commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"To all, one thing I don't lack is advice from the experts! Thanks for the input, challenges,…"
7 hours ago
tedkidd commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"Jim, I'm glad you are open, that's great!  We all learn best when we are open! The…"
7 hours ago
David Eakin commented on Jim Gunshinan's blog post My Energy Upgrade California—The Numbers Are In
"Jim, Well, as the editor of Home Energy you should already know that the order of remediation is…"
7 hours ago
Greg Labbe posted a blog post

Technical Tape Desecration

Lets face it – building science is pushing the performance of adhesive tapes to a new levels and…See More
9 hours ago
Stacy Hunt posted an event

High Performance Enclosure Strategies: Part II, New Construction at Online

August 13, 2014 from 1pm to 2:30pm
Please join the Building America Program for our free webinar: High Performance Enclosure…See More
11 hours ago
Richard Beyer replied to Howard Katzman's discussion UV lights on filters
"Howard, There are numerous manufacturer's who swear these systems work and then you have the…"
19 hours ago
Christopher Morin posted a blog post

How do You Test a TXV?

  Thermostatic Expansion Valves (TEV or TXV), one of the most popular metering devices for…See More
23 hours ago
Howard Katzman posted a discussion

UV lights on filters

I recently saw UV bulb installations in 2 HVAC systems in a home. Each system had the Lennox…See More
yesterday
Don Fitchett joined Michael Stuart's group
Thumbnail

INFRARED THERMOGRAPHY USERS

This group is dedicated to knowledge sharing and discussion of infrared thermography for building…See More
yesterday
Don Fitchett commented on Diane Chojnowski's group Pinterest
"While most of our (BIN95.com) energy post and boards are industrial related, there are crossovers…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service