When using the Duct Blaster I have found it necessary to seal the combustion air grilles on the furnace door and flue on an 80% afue gas furnace in order to obtain accurate leakage results. Any comments?

Views: 136

Reply to This

Replies to This Discussion

Far from my expertise, but there should be no connection between the combustion side and the conditioned air side.  The only thing I can think of would be duct side leakage inside the cabinet then accessing the combustion side through the air intake.  Of course there is a possibility of a cracked air exchanger, but not something you would run into on every unit, I would hope.  I'll be watching to see what the pros have to say.

Bud

Damien, if you do that, your results are inaccurate and of course the HVAC guy has an issue to find & fix

The duct test doesn't test just the ducts, but the whole air handling apparatus. The only exception is the version where the air handler hasn't been installed & then they are only allowed 4% leakage per the 2009 codes. With that said many municipalities don't accept that test & we simply won't perform it

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Bud Poll replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"This is a topic I have discussed many times, but unfortunately cost is all too often the deciding…"
2 hours ago
Sean Lintow Sr replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"If you can't talk them into replacing with IC rated... Look into Tenmat - those are designed…"
2 hours ago
Bachi Brunato posted a discussion

Boxing and Insulating Around Non-ICAT Cans

I have a client with 16) 4" halogen recessed light fixtures in the attic.I'd like to cover the cans…See More
8 hours ago
Dennis Heidner replied to Patrick Michaelyan's discussion Hot Upper Stories
"Could you have them make a simple two line graph of the outside temperature, noting sun/clouds,…"
17 hours ago
Bob Blanchette replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"You make some valid points, especially with the base rate charges. Increasing the base rate instead…"
yesterday
Bob Blanchette replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"Amen, make energy show it's true cost instead of subsidizing it. We have some of the lowest…"
yesterday
Dennis Heidner replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"The press report really doesn't give enough information to clearly answer why  they are…"
yesterday
Edward Foskey commented on Edward Foskey's blog post Preparing to Update the Heat Pump
"Gustavo, Thanks for the input. I agree with you in that I will be waiting till my system's…"
yesterday
Gustavo Melo commented on Edward Foskey's blog post Preparing to Update the Heat Pump
"Any system that is out of warranty is really a coin toss as to whether it is financially better to…"
yesterday
Dennis Heidner replied to J.C. Martel's discussion Disasters & sustainable energy
"Such as Greensburg…"
yesterday
Tom Delconte commented on Edward Foskey's blog post Preparing to Update the Heat Pump
"Thanks, Ed, I get it now. I would just put in what my hvac guy tells me to put in: a $17,000…"
yesterday
Jim Gunshinan commented on Jim Gunshinan's blog post The Universe Is Made of Stories
"Hi Tom, I'm sorry you didn't think my blog post was helpful or appropriate. I'll…"
yesterday

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service