David Richardson posted an interesting piece on changing from % based testing based on conditioned floor area versus the duct area

http://ncidavid.blogspot.com/2013/10/should-duct-surface-area-be-us... 

Personally I see quite a few problems with this based on the way things are done now, but I am curious what you all think.

As for some of my concerns - most installers have no clue what the duct area is because we cant even get them to do a Manual J much less a D (sorry I also have no desire to run a tape against them either)

Leaving the air handler out means more sloppy installs of them & manufacturers wouldn't have to concentrate on making them by default tighter

With that he does make some very valid points & I would love to hear your thoughts

Views: 635

Replies to This Discussion

Interesting thought but the issue with that is contractors bumping up manual J's for bigger units - the 99 occupants, leaky house, etc... tricks we have all seen used to get to there favorite 400 or 500 SF per ton. Granted commercial never sees this issue but that is because they require a mechanical engineer in many cases & also have higher loads than residential due to ventilation requirements

I think John has it nailed - 6% total (at final) & 10% for inside conditioned space (especially for "balanced" systems where they have actual returns in each room) with maybe a max based on nominal airflow. Shoot to make it fair for smaller houses  to promote them maybe even go 8% for homes under 1200 SF. As for reporting, I think it should be both the % but also as Ted points out - actual leakage numbers 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

w d posted a discussion

AERC testing and Solar Grates update

AERC of WCMA has been created to test the effectiveness of window attachments and to design an…See More
9 hours ago
Profile IconRob Pender, Sheldon White and jerrycarter joined Home Energy Pros
10 hours ago
Morgan M Audetat commented on Tom White's blog post Embodied Energy: Minimizing Waste with Off-Site Construction
"What is new…"
10 hours ago
Mark posted events
12 hours ago
Jim Gunshinan's video was featured

GoGreen Portland 2014: The Myth of Apathy - Renee Lertzman, Ph.D

http://portland.gogreenconference.net Renee Lertzman, PhD is the Director of Insight for Brand Cool, a marketing agency supporting a sustainable world. An internationally recognized researcher, speaker, author, instructor and thought leader in…
13 hours ago
Jim Gunshinan posted a video

GoGreen Portland 2014: The Myth of Apathy - Renee Lertzman, Ph.D

http://portland.gogreenconference.net Renee Lertzman, PhD is the Director of Insight for Brand Cool, a marketing agency supporting a sustainable world. An internationally recognized researcher, speaker, author, instructor and thought leader in…
13 hours ago
Stacy Hunt posted blog posts
13 hours ago
Colin Genge posted an event

Air Leakage Testing for Home Inspectors at Online

July 7, 2015 from 1pm to 2pm
• What sort of effect will IECC adoption have on the building industry? Home owners? Inspectors? •…See More
16 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service