Concerning duct testing in crawlspaces (this is for new houses for Energy Star, but will be the same for existing houses):

I have a house on a conditioned crawl with ducts in that crawl.  There is an exterior hatchway into the crawl, and no intentional connection between the house and the crawl.  When performing a total duct leakage test, no problem, just open the hatch before the test.  When performing a duct leakage to outside test, the crawlspace ducts never experience the effect of the blower door, so the test is inaccurate, with leakage to outside numbers that are too high.

We know the numbers are too high in a case like this, and we have been able to simulate the problem in a house with a basement by taping the basement door while doing the leakage to outside test.  Just today, we tested 2 identical houses that we had sealed while under construction.  The 2 identical houses - 1400 ft2 on a basement making them 2800 ft2 of conditioned space - had building leakage of 620 CFM50 and 650 CFM 50.  Duct systems are entirely within the shell.  Both had a leakage to outside numbers of 20 and 26 CFM25 range.  We then taped the doors to the basements and got numbers of 82 and 92 CFM25 as leakage to the outside.  In these cases, off by a large factor from the real 20-25 number.

Without cutting a hole in the floor or installing a second blower door in the crawlspace, do you have any ideas?

Ed Minch

Tags: conditioned, crawl, duct, testing

Views: 717

Reply to This

Replies to This Discussion

It does, but even though:

"According to the RESNET Formal Interpretation mentioned above: The measured outside leakage shall be deemed to be 0  CFM25 for each system the meets the following criteria: 100% of ducts and air handler located in conditioned space boundary, 100% visible, and not located in an enclosed space such as a chaseway, interior or exterior wall or roof cavity or in an enclosed floor cavity."

EStar says you have to test BOTH total leakage and leakage-to-outside on every house, with a few exceptions some of which you mentioned.  I think V 3 has overreached on a lot of topics, this total leakage number being one of them.  

Here is another topic:  Next time you do a duct-leakage-to-outside test, when the test is done, leave the equipment running with the leakage number showing on your manometer.  Then pull the tape off the registers one at a time.  Check the leakage number on the gauge.  If the house is reasonably tight  (let's say 4 ACH50), the number won't change even with all registers open - you didn't have to tape!

Ed Minch

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Craig Foley posted an event
Thumbnail

NESEA BuildingEnergy '15 at Seaport World Trade Center, Boston

March 4, 2015 from 10:30am to 12:30pm
High-Performance, Green Homes in Residential Real EstateInstructor Craig Foley will present three…See More
yesterday
Casey Gesell posted a video

ThermalDry® Insulated Floor Decking!

Larry Janesky, owner and founder of Dr. Energy Saver is once again On the Job insulating and finishing a basement in the northeast – and introducing a brand new insulation product: ThermalDry Insulated Floor Decking. ThermalDry Floor Decking was…
yesterday
Profile IconBergen Heat, Travis Thom and Amita Singh joined Home Energy Pros
yesterday
Tom White's video was featured

U.S. Department of Education Webinar for HVACR Educators

Rebroadcast from On April 30, 2013 Sharon Miller and Robin Utz of the U.S. Department of Education conducted a one hour webinar for HVACR educators to provide them firsthand information from Washington. Highlights include: * A blueprint to revise…
yesterday
Tom White posted a video

U.S. Department of Education Addresses HVACR Educators 4-30-2013

Rebroadcast from On April 30, 2013 Sharon Miller and Robin Utz of the U.S. Department of Education conducted a one hour webinar for HVACR educators to provid...
yesterday
Nate Adams's discussion was featured
Friday
Bud Poll replied to Bud Poll's discussion CO poisoning in Yarmouth Maine
"Hi Chad, I sure would like to hear the follow-up on what caused the CO issue down there.  As…"
Friday
Chad Mcaulife replied to Bud Poll's discussion CO poisoning in Yarmouth Maine
"I got a call yesterday from a homeowner who had a direct vent furnace installed a year ago and she…"
Friday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service