Concerning duct testing in crawlspaces (this is for new houses for Energy Star, but will be the same for existing houses):

I have a house on a conditioned crawl with ducts in that crawl.  There is an exterior hatchway into the crawl, and no intentional connection between the house and the crawl.  When performing a total duct leakage test, no problem, just open the hatch before the test.  When performing a duct leakage to outside test, the crawlspace ducts never experience the effect of the blower door, so the test is inaccurate, with leakage to outside numbers that are too high.

We know the numbers are too high in a case like this, and we have been able to simulate the problem in a house with a basement by taping the basement door while doing the leakage to outside test.  Just today, we tested 2 identical houses that we had sealed while under construction.  The 2 identical houses - 1400 ft2 on a basement making them 2800 ft2 of conditioned space - had building leakage of 620 CFM50 and 650 CFM 50.  Duct systems are entirely within the shell.  Both had a leakage to outside numbers of 20 and 26 CFM25 range.  We then taped the doors to the basements and got numbers of 82 and 92 CFM25 as leakage to the outside.  In these cases, off by a large factor from the real 20-25 number.

Without cutting a hole in the floor or installing a second blower door in the crawlspace, do you have any ideas?

Ed Minch

Tags: conditioned, crawl, duct, testing

Views: 731

Reply to This

Replies to This Discussion

It does, but even though:

"According to the RESNET Formal Interpretation mentioned above: The measured outside leakage shall be deemed to be 0  CFM25 for each system the meets the following criteria: 100% of ducts and air handler located in conditioned space boundary, 100% visible, and not located in an enclosed space such as a chaseway, interior or exterior wall or roof cavity or in an enclosed floor cavity."

EStar says you have to test BOTH total leakage and leakage-to-outside on every house, with a few exceptions some of which you mentioned.  I think V 3 has overreached on a lot of topics, this total leakage number being one of them.  

Here is another topic:  Next time you do a duct-leakage-to-outside test, when the test is done, leave the equipment running with the leakage number showing on your manometer.  Then pull the tape off the registers one at a time.  Check the leakage number on the gauge.  If the house is reasonably tight  (let's say 4 ACH50), the number won't change even with all registers open - you didn't have to tape!

Ed Minch

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Brian Clavette added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

FLIR i-7 thermal imaging camera

Hi,I have a very lightly used FLIR 1-7 for sale.   i-7, serial # 60101-4267.  Full hard case and…See More
14 hours ago
Don Fitchett commented on Home Energy Magazine's blog post At Home with the Internet of Annoying Things
"True, for the smart consumer, the power savings should offset the additional power usage. For the…"
16 hours ago
Michael Dunseith posted an event

BPI Exams - All at Green Jobs Training Center

March 2, 2015 at 10am to March 31, 2015 at 2pm
Green Jobs Training Center is currently providing written and field exams for all of BPI…See More
17 hours ago
Michael Dunseith posted photos
17 hours ago
Dennis Heidner commented on Home Energy Magazine's blog post At Home with the Internet of Annoying Things
"Nice article. I am an electrical engineer, creating sensors for data collection and "possibly…"
18 hours ago
Chris Hunt commented on Home Energy Magazine's blog post At Home with the Internet of Annoying Things
"Hi Alan, You correctly identified a lot of the potential issues coming with the IOT or the…"
18 hours ago
Nicole Miller joined James Sayers's group
Thumbnail

Marketing Energy Efficiency

Sharing ideas, tools and examples of promoting energy efficiency to consumersSee More
20 hours ago
Avi Yashchin posted a video

CleanEdison: BPI Training

Avi Yashchin's former company, CleanEdison, provided education and training for those seeking clean jobs, These services included Exam Prep for Leadership in...
21 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service