Concerning duct testing in crawlspaces (this is for new houses for Energy Star, but will be the same for existing houses):

I have a house on a conditioned crawl with ducts in that crawl.  There is an exterior hatchway into the crawl, and no intentional connection between the house and the crawl.  When performing a total duct leakage test, no problem, just open the hatch before the test.  When performing a duct leakage to outside test, the crawlspace ducts never experience the effect of the blower door, so the test is inaccurate, with leakage to outside numbers that are too high.

We know the numbers are too high in a case like this, and we have been able to simulate the problem in a house with a basement by taping the basement door while doing the leakage to outside test.  Just today, we tested 2 identical houses that we had sealed while under construction.  The 2 identical houses - 1400 ft2 on a basement making them 2800 ft2 of conditioned space - had building leakage of 620 CFM50 and 650 CFM 50.  Duct systems are entirely within the shell.  Both had a leakage to outside numbers of 20 and 26 CFM25 range.  We then taped the doors to the basements and got numbers of 82 and 92 CFM25 as leakage to the outside.  In these cases, off by a large factor from the real 20-25 number.

Without cutting a hole in the floor or installing a second blower door in the crawlspace, do you have any ideas?

Ed Minch

Tags: conditioned, crawl, duct, testing

Views: 656

Reply to This

Replies to This Discussion

It does, but even though:

"According to the RESNET Formal Interpretation mentioned above: The measured outside leakage shall be deemed to be 0  CFM25 for each system the meets the following criteria: 100% of ducts and air handler located in conditioned space boundary, 100% visible, and not located in an enclosed space such as a chaseway, interior or exterior wall or roof cavity or in an enclosed floor cavity."

EStar says you have to test BOTH total leakage and leakage-to-outside on every house, with a few exceptions some of which you mentioned.  I think V 3 has overreached on a lot of topics, this total leakage number being one of them.  

Here is another topic:  Next time you do a duct-leakage-to-outside test, when the test is done, leave the equipment running with the leakage number showing on your manometer.  Then pull the tape off the registers one at a time.  Check the leakage number on the gauge.  If the house is reasonably tight  (let's say 4 ACH50), the number won't change even with all registers open - you didn't have to tape!

Ed Minch

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"Hi Kurt.  I am in Modesto.  If you have the grey comp shingled on your roof (Roofing…"
20 minutes ago
Kurt Shafer commented on Hal Skinner's group The RCC Classroom (Radiant Control Coatings)
"All, I have been trying out a radiant barrier from atticfoil.com (not my co.)  I see that you…"
32 minutes ago
Hal Skinner replied to Aaren Stewart's discussion HVAC - Cooling and Heating Load Reduction
"Hi Aaren. Check out the group below.  Some RCCs are very versatile and can be used on…"
35 minutes ago
Kurt Shafer joined Hal Skinner's group
Thumbnail

The RCC Classroom (Radiant Control Coatings)

A group where energy professionals can learn about all the different energy saving aspects of…See More
42 minutes ago
Hannah Finch posted a blog post

Not too Late to Join the RaterFest! Party THIS Weekend!

RaterFest! kicks off this Friday, September 5, at Covenant Heights in Estes Park, CO. We still have…See More
58 minutes ago
Hal Skinner replied to Kurt Shafer's discussion Where can I find the best radiant barrier to install under my roof?
"Hi Kurt, You can find some information on Radiant Control Coatings in the group listed…"
1 hour ago
Profile IconPing Wang, Whitney Cooper and Mike Burton joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
1 hour ago
Ping Wang commented on Michael Stuart's group INFRARED THERMOGRAPHY USERS
"Hello Everyone, we produce and export Infrared heating lamp used for various food oven,industrial…"
1 hour ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service