Concerning duct testing in crawlspaces (this is for new houses for Energy Star, but will be the same for existing houses):

I have a house on a conditioned crawl with ducts in that crawl.  There is an exterior hatchway into the crawl, and no intentional connection between the house and the crawl.  When performing a total duct leakage test, no problem, just open the hatch before the test.  When performing a duct leakage to outside test, the crawlspace ducts never experience the effect of the blower door, so the test is inaccurate, with leakage to outside numbers that are too high.

We know the numbers are too high in a case like this, and we have been able to simulate the problem in a house with a basement by taping the basement door while doing the leakage to outside test.  Just today, we tested 2 identical houses that we had sealed while under construction.  The 2 identical houses - 1400 ft2 on a basement making them 2800 ft2 of conditioned space - had building leakage of 620 CFM50 and 650 CFM 50.  Duct systems are entirely within the shell.  Both had a leakage to outside numbers of 20 and 26 CFM25 range.  We then taped the doors to the basements and got numbers of 82 and 92 CFM25 as leakage to the outside.  In these cases, off by a large factor from the real 20-25 number.

Without cutting a hole in the floor or installing a second blower door in the crawlspace, do you have any ideas?

Ed Minch

Tags: conditioned, crawl, duct, testing

Views: 656

Reply to This

Replies to This Discussion

It does, but even though:

"According to the RESNET Formal Interpretation mentioned above: The measured outside leakage shall be deemed to be 0  CFM25 for each system the meets the following criteria: 100% of ducts and air handler located in conditioned space boundary, 100% visible, and not located in an enclosed space such as a chaseway, interior or exterior wall or roof cavity or in an enclosed floor cavity."

EStar says you have to test BOTH total leakage and leakage-to-outside on every house, with a few exceptions some of which you mentioned.  I think V 3 has overreached on a lot of topics, this total leakage number being one of them.  

Here is another topic:  Next time you do a duct-leakage-to-outside test, when the test is done, leave the equipment running with the leakage number showing on your manometer.  Then pull the tape off the registers one at a time.  Check the leakage number on the gauge.  If the house is reasonably tight  (let's say 4 ACH50), the number won't change even with all registers open - you didn't have to tape!

Ed Minch

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Profile IconKevin Jordan, Hannah Strong, Rich Snyder and 1 more joined Home Energy Pros
15 hours ago
EnergyLogic Academy posted events
15 hours ago
EnergyLogic Academy updated an event
Thumbnail

RESCAZ- RESNET Combustion Safety Testing: North Carolina at Wilmington, NC

November 7, 2014 from 6pm to 7pm
The health and safety of the home energy auditor’s clients should be the top priority when…See More
15 hours ago
EnergyLogic Academy updated an event
Thumbnail

RESNET Phase 2 Rater Training - Field Training at EnergyLogic Academy - Berthoud CO

September 22, 2014 to September 24, 2014
The EnergyLogic Academy will be hosting the second phase of HERS Rater Training August 4th - 7th,…See More
15 hours ago
Hal Skinner replied to Scott Katznelson's discussion Database of zip code or county by climate zone
"Hi Scott. I dont know of a database that you are referring to.  I was always under the…"
16 hours ago
Rich Snyder joined Rich Brunco's group
Thumbnail

Cape Cod Energy Pros

Recent BPI classmates, a place to share referals and informationSee More
17 hours ago
Scott Katznelson posted a discussion

Database of zip code or county by climate zone

HI.  I'm looking for a database that could help me assess the average energy use of a home (per…See More
23 hours ago
Hal Skinner replied to Hal Skinner's discussion The 'Touchy - Feely' sales pitch. in the group Radiant Control Coatings
"The 2nd bestsales tool I ever came up with.  aI will be happy to send anyone a test strip like…"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service