Concerning duct testing in crawlspaces (this is for new houses for Energy Star, but will be the same for existing houses):

I have a house on a conditioned crawl with ducts in that crawl.  There is an exterior hatchway into the crawl, and no intentional connection between the house and the crawl.  When performing a total duct leakage test, no problem, just open the hatch before the test.  When performing a duct leakage to outside test, the crawlspace ducts never experience the effect of the blower door, so the test is inaccurate, with leakage to outside numbers that are too high.

We know the numbers are too high in a case like this, and we have been able to simulate the problem in a house with a basement by taping the basement door while doing the leakage to outside test.  Just today, we tested 2 identical houses that we had sealed while under construction.  The 2 identical houses - 1400 ft2 on a basement making them 2800 ft2 of conditioned space - had building leakage of 620 CFM50 and 650 CFM 50.  Duct systems are entirely within the shell.  Both had a leakage to outside numbers of 20 and 26 CFM25 range.  We then taped the doors to the basements and got numbers of 82 and 92 CFM25 as leakage to the outside.  In these cases, off by a large factor from the real 20-25 number.

Without cutting a hole in the floor or installing a second blower door in the crawlspace, do you have any ideas?

Ed Minch

Tags: conditioned, crawl, duct, testing

Views: 715

Reply to This

Replies to This Discussion

It does, but even though:

"According to the RESNET Formal Interpretation mentioned above: The measured outside leakage shall be deemed to be 0  CFM25 for each system the meets the following criteria: 100% of ducts and air handler located in conditioned space boundary, 100% visible, and not located in an enclosed space such as a chaseway, interior or exterior wall or roof cavity or in an enclosed floor cavity."

EStar says you have to test BOTH total leakage and leakage-to-outside on every house, with a few exceptions some of which you mentioned.  I think V 3 has overreached on a lot of topics, this total leakage number being one of them.  

Here is another topic:  Next time you do a duct-leakage-to-outside test, when the test is done, leave the equipment running with the leakage number showing on your manometer.  Then pull the tape off the registers one at a time.  Check the leakage number on the gauge.  If the house is reasonably tight  (let's say 4 ACH50), the number won't change even with all registers open - you didn't have to tape!

Ed Minch

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Craig Lane posted photos
3 hours ago
David Snell replied to Patrick Michaelyan's discussion Mold on exterior walls
"I have dealt with mold on multiple occasions.. ​As a Mold Inspector Charlotte NC, i recommend…"
3 hours ago
Chad Mcaulife replied to Bart Nicholson's discussion Minneapolis Blower Door and Duct Blaster for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I would be interested in the blaster!!!"
15 hours ago
Chad Mcaulife replied to Matthew P's discussion Needed: Gas Detector and CO Detector. What do you recommend?
"The new BPI standards require a Gas Sniffer which has a read out of the LEL.  The cheapest I…"
15 hours ago
Profile IconDavid I. Shepherd-Gaw, Craig Lane, Barry Martin and 1 more joined Home Energy Pros
16 hours ago
Craig Lane joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
18 hours ago
Tom White posted videos
19 hours ago
Tom White's 2 videos were featured
19 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service