Dose anyone have experience testing high velocity duct systems?

I've been asked to duct test a Zhender HRV with comfoducts (2" homerun ducts).

I designed & installed a hydronic high velocity system a few years ago. It had 25' of 12" return flex duct, and 15-20' of 6+8" sheet metal ducting, 2 + 2-1/2" branch ducting. I sealed everything with mastic.

I installed the duct tester at the return, and the duct pressure at the nearest supply to the air hander, as I would on a low velocity system. I measured a high duct leakage, I was disappointed. I'm wondering if I should have taken my duct pressure at the supply trunk (6-8") rather than the 2 - 2-1/2" ducts, due to pressure drop.

Any thoughts?

Thanks

 

Views: 172

Reply to This

Replies to This Discussion

This duct system should be tight enough that it should not matter where you test it from.  I recommend you test under negative pressure to ensure you get good seals at the registers.  How high was your reading and what flow range were you on?

When measuring super low flow, do a field check of your duct tester (thank you for not calling it a Blaster) by cutting a 1 inch x 3 inch hole in thick card board and tape it to the flange on your duct tester. This hole should come in at around 16 cfm at 25 Pa with the pressure measured across the cardboard.  If it measures more than that, your duct testing system could be leaking or out of whack some how. 

if the duct leakage is relatively low, 200 cfm or less, the pressure in the duct system will be quite uniform and either location will give consistent results.  If the duct leakage is high, over 500 cfm, we recommend that you do two tests.  One with the probe in the supply register closest to the Duct Blaster setup and one with it in the farthest supply register and average the readings.  

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

David Eakin commented on Elisa Wood's blog post Momentum builds for energy efficiency...but is the wolf at the door?
"Here's a very recent article on Green Building Advisor that reinforces the issues to…"
8 hours ago
Home Energy Magazine posted blog posts
10 hours ago
Egr renovation posted a status
"of course he is in paris but works around europe http://ning.it/16KrbS7"
13 hours ago
Egr renovation posted a status
"i just find a good photogrpahe for your master piece http://www.armanimage.com"
13 hours ago

Tom Mallard just added their location.
(via Member Map)

yesterday
Profile IconDon Hughes, Julian Sark, James Hatheway and 4 more joined Home Energy Pros
yesterday
Meagan Foster posted events
yesterday
Meagan Foster updated an event

EnergyLogic's RaterFest! at Black Hawk, CO

September 13, 2013 at 10am to September 15, 2013 at 12pm
Join us for one of the best home energy conferences available!  This retreat will provide…See More
yesterday
Meagan Foster updated an event

Homes 401: Green Rater Training at Berthoud, CO

June 25, 2013 to June 26, 2013
This highly interactive workshop builds upon the material presented in the online course, further…See More
yesterday
Meagan Foster updated an event

HERS Rater Training - Online at Online

July 1, 2013 to July 26, 2013
NEW - our great RESNET HERS Rater online training is now completely self-paced, so you can start at…See More
yesterday
Meagan Foster updated an event

BPI Building Analyst Training - Online at Online

June 3, 2013 to June 28, 2013
Join the EnergyLogic Academy for our BPI BA online training - we just went to a completely open…See More
yesterday

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service