Dose anyone have experience testing high velocity duct systems?

I've been asked to duct test a Zhender HRV with comfoducts (2" homerun ducts).

I designed & installed a hydronic high velocity system a few years ago. It had 25' of 12" return flex duct, and 15-20' of 6+8" sheet metal ducting, 2 + 2-1/2" branch ducting. I sealed everything with mastic.

I installed the duct tester at the return, and the duct pressure at the nearest supply to the air hander, as I would on a low velocity system. I measured a high duct leakage, I was disappointed. I'm wondering if I should have taken my duct pressure at the supply trunk (6-8") rather than the 2 - 2-1/2" ducts, due to pressure drop.

Any thoughts?

Thanks

 

Views: 259

Reply to This

Replies to This Discussion

This duct system should be tight enough that it should not matter where you test it from.  I recommend you test under negative pressure to ensure you get good seals at the registers.  How high was your reading and what flow range were you on?

When measuring super low flow, do a field check of your duct tester (thank you for not calling it a Blaster) by cutting a 1 inch x 3 inch hole in thick card board and tape it to the flange on your duct tester. This hole should come in at around 16 cfm at 25 Pa with the pressure measured across the cardboard.  If it measures more than that, your duct testing system could be leaking or out of whack some how. 

if the duct leakage is relatively low, 200 cfm or less, the pressure in the duct system will be quite uniform and either location will give consistent results.  If the duct leakage is high, over 500 cfm, we recommend that you do two tests.  One with the probe in the supply register closest to the Duct Blaster setup and one with it in the farthest supply register and average the readings.  

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Christopher Morin posted a blog post
2 hours ago
Bud Poll replied to Bud Poll's discussion Another benefit from air sealing
"That is also one of my concerns about adding new insulation over old.  On a consultation I…"
6 hours ago
Barbara Smith replied to Bud Poll's discussion Another benefit from air sealing
"The only time I was present during dense packing of an attic with cellulose, people who were…"
7 hours ago
Barbara Smith replied to Christopher Talarico's discussion Heating with Tankless Water Heater & Hydronic Air Handler vs. Gas Furnace
"See "Why Pay for Two Condensing Systems When One Will Do?" by Schoenbauer et al…"
7 hours ago
Bud Poll posted a discussion

Another benefit from air sealing

From our perspective air sealing should often be the first step, but when explaining its importance…See More
7 hours ago
Brett Little posted events
9 hours ago
Brett Little's 2 events were featured
10 hours ago
Profile IconSATISH KUMAR GUPTA, Kimberly Loewen, Bob Whelan and 2 more joined Home Energy Pros
10 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service