Dose anyone have experience testing high velocity duct systems?

I've been asked to duct test a Zhender HRV with comfoducts (2" homerun ducts).

I designed & installed a hydronic high velocity system a few years ago. It had 25' of 12" return flex duct, and 15-20' of 6+8" sheet metal ducting, 2 + 2-1/2" branch ducting. I sealed everything with mastic.

I installed the duct tester at the return, and the duct pressure at the nearest supply to the air hander, as I would on a low velocity system. I measured a high duct leakage, I was disappointed. I'm wondering if I should have taken my duct pressure at the supply trunk (6-8") rather than the 2 - 2-1/2" ducts, due to pressure drop.

Any thoughts?

Thanks

 

Views: 285

Reply to This

Replies to This Discussion

This duct system should be tight enough that it should not matter where you test it from.  I recommend you test under negative pressure to ensure you get good seals at the registers.  How high was your reading and what flow range were you on?

When measuring super low flow, do a field check of your duct tester (thank you for not calling it a Blaster) by cutting a 1 inch x 3 inch hole in thick card board and tape it to the flange on your duct tester. This hole should come in at around 16 cfm at 25 Pa with the pressure measured across the cardboard.  If it measures more than that, your duct testing system could be leaking or out of whack some how. 

if the duct leakage is relatively low, 200 cfm or less, the pressure in the duct system will be quite uniform and either location will give consistent results.  If the duct leakage is high, over 500 cfm, we recommend that you do two tests.  One with the probe in the supply register closest to the Duct Blaster setup and one with it in the farthest supply register and average the readings.  

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Joe Konopacki posted an event

Duct & Envelope Tightness (DET) Verifier at Temperature Equipment Corporation

May 8, 2015 from 8:30am to 4:30pm
The Duct & Envelope Tightness Certification (DET) was designed by the Illinois Association of…See More
4 hours ago
Paul Raymer posted a blog post

Shades of Gray in Residential Construction Morality

I was called in to perform a last minute duct test for a modular home builder.  He was all in a…See More
6 hours ago
Alfie Davis posted a blog post

Tiles Flooring – A Better Choice than Concrete Flooring

This article can change one’s perception about flooring and can act as an excellent guide in…See More
8 hours ago
Charlie Hewitt posted a blog post

Residential Electric Load Disaggregation

“What gets measured gets managed” is a quote often attributed to the venerable management expert…See More
19 hours ago
Kurt Albershardt replied to Larry Schaffert's discussion How to correctly insulate exterior wall in a 1900 house?
"Balloon framed houses make for easy upgrades IME.  We cover the open bays from the sill plate…"
20 hours ago
Kurt Albershardt replied to William Fisher's discussion Can tankless water heaters provide hot water even when the groundwater is fairly cold?
"There are a number of approaches that can work depending on the specifics of your situation. What…"
20 hours ago
Bob Mariani joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
yesterday
Bob Mariani replied to William Parlapiano's discussion Equipment for Sale Updated April 9, 2015 in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I would be interested in a package deal for the items marked as "Available"  Email…"
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service