Dose anyone have experience testing high velocity duct systems?

I've been asked to duct test a Zhender HRV with comfoducts (2" homerun ducts).

I designed & installed a hydronic high velocity system a few years ago. It had 25' of 12" return flex duct, and 15-20' of 6+8" sheet metal ducting, 2 + 2-1/2" branch ducting. I sealed everything with mastic.

I installed the duct tester at the return, and the duct pressure at the nearest supply to the air hander, as I would on a low velocity system. I measured a high duct leakage, I was disappointed. I'm wondering if I should have taken my duct pressure at the supply trunk (6-8") rather than the 2 - 2-1/2" ducts, due to pressure drop.

Any thoughts?

Thanks

 

Views: 362

Reply to This

Replies to This Discussion

This duct system should be tight enough that it should not matter where you test it from.  I recommend you test under negative pressure to ensure you get good seals at the registers.  How high was your reading and what flow range were you on?

When measuring super low flow, do a field check of your duct tester (thank you for not calling it a Blaster) by cutting a 1 inch x 3 inch hole in thick card board and tape it to the flange on your duct tester. This hole should come in at around 16 cfm at 25 Pa with the pressure measured across the cardboard.  If it measures more than that, your duct testing system could be leaking or out of whack some how. 

if the duct leakage is relatively low, 200 cfm or less, the pressure in the duct system will be quite uniform and either location will give consistent results.  If the duct leakage is high, over 500 cfm, we recommend that you do two tests.  One with the probe in the supply register closest to the Duct Blaster setup and one with it in the farthest supply register and average the readings.  

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Profile IconMichael Sumpter and Bill Gartner joined Home Energy Pros
10 hours ago
Malcolm Jackson joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
13 hours ago
Amber Vignieri liked tedkidd's discussion What if more efficient homes were actually worth more?
16 hours ago
Amber Vignieri posted a blog post
17 hours ago
Eric Kjelshus replied to Rob Madden, Solar Home Broker's discussion Indoor Air Quality Monitors and Meters
"I have been using air advice for 5 yr or so - I end up with a report in 35 min I can e-mail or show…"
19 hours ago
Profile IconShane Matteson, Jay Cooper and Mike Harris joined Home Energy Pros
yesterday
Kim Burnett commented on Diane Chojnowski's group Home Energy Pros on Twitter
"Good morning, would you please add me. Thank you. Kim Burnett A+ Abundant Energy Experts"
yesterday
Kim Burnett joined Diane Chojnowski's group
Thumbnail

Home Energy Pros on Twitter

We've created a twitter list of members of Home Energy Pros who tweet about home performance and…See More
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service