Dose anyone have experience testing high velocity duct systems?

I've been asked to duct test a Zhender HRV with comfoducts (2" homerun ducts).

I designed & installed a hydronic high velocity system a few years ago. It had 25' of 12" return flex duct, and 15-20' of 6+8" sheet metal ducting, 2 + 2-1/2" branch ducting. I sealed everything with mastic.

I installed the duct tester at the return, and the duct pressure at the nearest supply to the air hander, as I would on a low velocity system. I measured a high duct leakage, I was disappointed. I'm wondering if I should have taken my duct pressure at the supply trunk (6-8") rather than the 2 - 2-1/2" ducts, due to pressure drop.

Any thoughts?

Thanks

 

Views: 293

Reply to This

Replies to This Discussion

This duct system should be tight enough that it should not matter where you test it from.  I recommend you test under negative pressure to ensure you get good seals at the registers.  How high was your reading and what flow range were you on?

When measuring super low flow, do a field check of your duct tester (thank you for not calling it a Blaster) by cutting a 1 inch x 3 inch hole in thick card board and tape it to the flange on your duct tester. This hole should come in at around 16 cfm at 25 Pa with the pressure measured across the cardboard.  If it measures more than that, your duct testing system could be leaking or out of whack some how. 

if the duct leakage is relatively low, 200 cfm or less, the pressure in the duct system will be quite uniform and either location will give consistent results.  If the duct leakage is high, over 500 cfm, we recommend that you do two tests.  One with the probe in the supply register closest to the Duct Blaster setup and one with it in the farthest supply register and average the readings.  

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Mariusz Chorazy posted a blog post

Here are a few tips to keep your air conditioning bill low

TAKE GOOD CARE OF YOUR AIR CONDITIONER – Like any major appliance, your AC requires regular…See More
yesterday
Dale Pickard replied to Rod Fox's discussion Does altitude affect AFUE? or just the input/output BTUs?
"Morgan, I got this below from the Knight installation manual. I note a few things, -These…"
yesterday
Dale Pickard replied to Rod Fox's discussion Does altitude affect AFUE? or just the input/output BTUs?
"Hans, The car manufacturer's are doing it with mass flow sensors and oxygen sensors…"
yesterday
Dale Pickard replied to Rod Fox's discussion Does altitude affect AFUE? or just the input/output BTUs?
"I was trying to avoid naming manufacturers, but I was going by the published information for the…"
yesterday
Eric Kjelshus replied to Rod Fox's discussion Does altitude affect AFUE? or just the input/output BTUs?
"I look at this not about AFUE,  but flue gas dewpoint.  If your burn rate is rotting the…"
yesterday
Bob Blanchette replied to Kirsten Richnavsky's discussion Crawl spaces and attics: OSHA to implement new rule on confined spaces
"Keeping HVAC equipment out of attics should be part of the new code. "
yesterday
Linda Wigington replied to Linda Wigington's discussion Weigh in - Honorable Mention? 2nd Base? Half-Way There? 50% Better? On the Path? in the group 1000 Home Challenge
"Nickie -  Good points. I think it is easy enough to flag or designate projects that achieve…"
yesterday
Morgan M Audetat replied to Rod Fox's discussion Does altitude affect AFUE? or just the input/output BTUs?
"Though Viessmann is relatively unique in the application of Lambda technology to condensing…"
Friday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service