Dose anyone have experience testing high velocity duct systems?

I've been asked to duct test a Zhender HRV with comfoducts (2" homerun ducts).

I designed & installed a hydronic high velocity system a few years ago. It had 25' of 12" return flex duct, and 15-20' of 6+8" sheet metal ducting, 2 + 2-1/2" branch ducting. I sealed everything with mastic.

I installed the duct tester at the return, and the duct pressure at the nearest supply to the air hander, as I would on a low velocity system. I measured a high duct leakage, I was disappointed. I'm wondering if I should have taken my duct pressure at the supply trunk (6-8") rather than the 2 - 2-1/2" ducts, due to pressure drop.

Any thoughts?

Thanks

 

Views: 346

Reply to This

Replies to This Discussion

This duct system should be tight enough that it should not matter where you test it from.  I recommend you test under negative pressure to ensure you get good seals at the registers.  How high was your reading and what flow range were you on?

When measuring super low flow, do a field check of your duct tester (thank you for not calling it a Blaster) by cutting a 1 inch x 3 inch hole in thick card board and tape it to the flange on your duct tester. This hole should come in at around 16 cfm at 25 Pa with the pressure measured across the cardboard.  If it measures more than that, your duct testing system could be leaking or out of whack some how. 

if the duct leakage is relatively low, 200 cfm or less, the pressure in the duct system will be quite uniform and either location will give consistent results.  If the duct leakage is high, over 500 cfm, we recommend that you do two tests.  One with the probe in the supply register closest to the Duct Blaster setup and one with it in the farthest supply register and average the readings.  

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Crosbey Archery liked Don Hynek's discussion Testing "Magic Pak" units??
9 minutes ago
Crosbey Archery joined Norm Bourassa's group
Thumbnail

Multifamily Buildings

For too long there has been relatively little EE focus on multifamily, but some new programs have…See More
22 minutes ago
Crosbey Archery liked Crosbey Archery's blog post Energy Tips - Fresh Look at Heating and Cooling the Home
26 minutes ago
tedkidd liked Luis Hernandez's discussion Airsealing an old basement ceiling
7 hours ago
Ryan T De La Rosa posted a blog post

The Clean Power Plan and What You Can Do

Last month, Jessica Hardcastle at Environment Leader described an especially non-polarizing…See More
8 hours ago
Ed Minch replied to Luis Hernandez's discussion Airsealing an old basement ceiling
"Luis Think of it as a part of the house that is not being used, but part of the house none the…"
12 hours ago
Luis Hernandez replied to Luis Hernandez's discussion Searching for a multifamily study book in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Hey Craig!  Well, let's get serious and keep asking all our friends in the Home…"
14 hours ago
Luis Hernandez replied to Luis Hernandez's discussion Airsealing an old basement ceiling
"Hey there Ed,      I appreciate you comments... this is an interesting case because…"
14 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service