Dose anyone have experience testing high velocity duct systems?

I've been asked to duct test a Zhender HRV with comfoducts (2" homerun ducts).

I designed & installed a hydronic high velocity system a few years ago. It had 25' of 12" return flex duct, and 15-20' of 6+8" sheet metal ducting, 2 + 2-1/2" branch ducting. I sealed everything with mastic.

I installed the duct tester at the return, and the duct pressure at the nearest supply to the air hander, as I would on a low velocity system. I measured a high duct leakage, I was disappointed. I'm wondering if I should have taken my duct pressure at the supply trunk (6-8") rather than the 2 - 2-1/2" ducts, due to pressure drop.

Any thoughts?

Thanks

 

Views: 297

Reply to This

Replies to This Discussion

This duct system should be tight enough that it should not matter where you test it from.  I recommend you test under negative pressure to ensure you get good seals at the registers.  How high was your reading and what flow range were you on?

When measuring super low flow, do a field check of your duct tester (thank you for not calling it a Blaster) by cutting a 1 inch x 3 inch hole in thick card board and tape it to the flange on your duct tester. This hole should come in at around 16 cfm at 25 Pa with the pressure measured across the cardboard.  If it measures more than that, your duct testing system could be leaking or out of whack some how. 

if the duct leakage is relatively low, 200 cfm or less, the pressure in the duct system will be quite uniform and either location will give consistent results.  If the duct leakage is high, over 500 cfm, we recommend that you do two tests.  One with the probe in the supply register closest to the Duct Blaster setup and one with it in the farthest supply register and average the readings.  

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Kim Tanner posted a discussion

Acronym Challenge!

We challenge you to make suggestions to help troubleshoot the below problem using as many acronyms…See More
1 hour ago
Kim Tanner joined Brandon Walton's group
Thumbnail

Efficiency First Arizona Chapter

Efficiency First of Arizona is the Official State Chapter of that unites the Home Performance…See More
1 hour ago
Paul Morin commented on Sean Maxwell's blog post The Better Blower Door Test for Multifamily Energy Code
"Thanks Sean for a very will stated article.  I agree with your assessment of the importance of…"
1 hour ago
Profile IconBenjamin Mailian and Michael Laurie joined Home Energy Pros
2 hours ago
SmithWatson posted a blog post

It is time to replace your boiler, isn’t it?

Have you suddenly started noticing a spike in your energy bills? If yes, one of the main things you…See More
3 hours ago
Theresa L Gilbride's blog post was featured
19 hours ago
Quinn Korzeniecki added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Obama Announced New Actions to Bring Energy Efficiency to Households across the Country

Big news out of The White House last week for the ‪‎clean energy‬ housing sector: HUD and DOE have…See More
22 hours ago
Theresa L Gilbride posted a blog post
23 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service