Dose anyone have experience testing high velocity duct systems?

I've been asked to duct test a Zhender HRV with comfoducts (2" homerun ducts).

I designed & installed a hydronic high velocity system a few years ago. It had 25' of 12" return flex duct, and 15-20' of 6+8" sheet metal ducting, 2 + 2-1/2" branch ducting. I sealed everything with mastic.

I installed the duct tester at the return, and the duct pressure at the nearest supply to the air hander, as I would on a low velocity system. I measured a high duct leakage, I was disappointed. I'm wondering if I should have taken my duct pressure at the supply trunk (6-8") rather than the 2 - 2-1/2" ducts, due to pressure drop.

Any thoughts?

Thanks

 

Views: 378

Reply to This

Replies to This Discussion

This duct system should be tight enough that it should not matter where you test it from.  I recommend you test under negative pressure to ensure you get good seals at the registers.  How high was your reading and what flow range were you on?

When measuring super low flow, do a field check of your duct tester (thank you for not calling it a Blaster) by cutting a 1 inch x 3 inch hole in thick card board and tape it to the flange on your duct tester. This hole should come in at around 16 cfm at 25 Pa with the pressure measured across the cardboard.  If it measures more than that, your duct testing system could be leaking or out of whack some how. 

if the duct leakage is relatively low, 200 cfm or less, the pressure in the duct system will be quite uniform and either location will give consistent results.  If the duct leakage is high, over 500 cfm, we recommend that you do two tests.  One with the probe in the supply register closest to the Duct Blaster setup and one with it in the farthest supply register and average the readings.  

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Ed Voytovich replied to Beverly Lerch's discussion Fireplace drafts
"Our solution was to install a Lopi Answer wood burning insert that vents directly through a metal…"
35 minutes ago
kevin mack is now a member of Home Energy Pros
3 hours ago
Jim Gunshinan's blog post was featured

A Healthy Home and a Healthy Bottom Line

There has been a lot of interest of late in the weatherization and broader home performance…See More
22 hours ago
Jonathan Beers commented on Home Energy Magazine's blog post Natural Gas is Becoming Less Attractive
"The carbon intensity of electricity use (lbs. of CO2/MWh) varies a lot from region to region. For…"
23 hours ago
Diane Chojnowski posted events
yesterday
Home Energy Magazine posted a blog post

Natural Gas is Becoming Less Attractive

The United States and Canada have been fortunate to have access to natural gas for space heating,…See More
yesterday
Jim Gunshinan posted a blog post

A Healthy Home and a Healthy Bottom Line

There has been a lot of interest of late in the weatherization and broader home performance…See More
yesterday
Luke Langhals commented on Tom White's video
Thumbnail

Passivhaus Goes Personal

"Great video. This shows that Passive House isn't all about Energy. Selling it to customers…"
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service