When using the Duct Blaster I have found it necessary to seal the combustion air grilles on the furnace door and flue on an 80% afue gas furnace in order to obtain accurate leakage results. Any comments?

Views: 175

Reply to This

Replies to This Discussion

Far from my expertise, but there should be no connection between the combustion side and the conditioned air side.  The only thing I can think of would be duct side leakage inside the cabinet then accessing the combustion side through the air intake.  Of course there is a possibility of a cracked air exchanger, but not something you would run into on every unit, I would hope.  I'll be watching to see what the pros have to say.

Bud

Damien, if you do that, your results are inaccurate and of course the HVAC guy has an issue to find & fix

The duct test doesn't test just the ducts, but the whole air handling apparatus. The only exception is the version where the air handler hasn't been installed & then they are only allowed 4% leakage per the 2009 codes. With that said many municipalities don't accept that test & we simply won't perform it

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Mike Burton joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
1 hour ago
Hal Skinner replied to Trip Smith's discussion Starting a Home Weatherization Business. Considering it...
"Hi Tri,p Your 'Yard sign' comment caught my eye.  I work with a Radiant Barrier…"
1 hour ago
Profile IconEric Kjelshus and Trip Smith joined James Sayers's group
Thumbnail

Marketing Energy Efficiency

Sharing ideas, tools and examples of promoting energy efficiency to consumersSee More
4 hours ago
Bob Blanchette replied to Christopher Talarico's discussion Heating with Tankless Water Heater & Hydronic Air Handler vs. Gas Furnace
"When it costs the same price as 2 separate systems there is no juice regardless of how hard you…"
4 hours ago
j. west shared Christopher Morin's blog post on Facebook
10 hours ago
j. west commented on Christopher Morin's blog post UPDATED: Big Changes for Duct Testing in MA
"You're right Christopher- the trick to saving the profit margin is being in several places at…"
10 hours ago
tedkidd replied to Christopher Talarico's discussion Heating with Tankless Water Heater & Hydronic Air Handler vs. Gas Furnace
"Nice posts Steven and Eric.   Scale on my combi is a recurring problem.  Attaching…"
11 hours ago
Eric Kjelshus replied to Christopher Talarico's discussion Heating with Tankless Water Heater & Hydronic Air Handler vs. Gas Furnace
"I find the tank less hot water lime up.   I have a condensate pump that I pump white vinegar…"
12 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service