When using the Duct Blaster I have found it necessary to seal the combustion air grilles on the furnace door and flue on an 80% afue gas furnace in order to obtain accurate leakage results. Any comments?

Views: 196

Reply to This

Replies to This Discussion

Far from my expertise, but there should be no connection between the combustion side and the conditioned air side.  The only thing I can think of would be duct side leakage inside the cabinet then accessing the combustion side through the air intake.  Of course there is a possibility of a cracked air exchanger, but not something you would run into on every unit, I would hope.  I'll be watching to see what the pros have to say.


Damien, if you do that, your results are inaccurate and of course the HVAC guy has an issue to find & fix

The duct test doesn't test just the ducts, but the whole air handling apparatus. The only exception is the version where the air handler hasn't been installed & then they are only allowed 4% leakage per the 2009 codes. With that said many municipalities don't accept that test & we simply won't perform it



  • Add Videos
  • View All


Latest Activity

Seth Romme is now a member of Home Energy Pros
4 hours ago
John Nicholas replied to Rob Madden's discussion Blower Door Testing on Energy Star v3 home
"So you have a slab on grade home, duct work in the attic?"
17 hours ago
Diane Jackson posted a photo

"Drive Home"

Addison Homes spent a fun day with a film crew from the National Association of Home Builders. We…
23 hours ago
Paul Raymer posted a blog post

Healthy Home Evaluator Training

Fall River, MA     October 13, 2016…See More
Diane Chojnowski updated an event

Better homes video series at Seventhwave

October 24, 2016 to January 26, 2017
Profile Iconseoeleczo and Parfait Pouliotte joined Home Energy Pros
Amber Vignieri's blog post was featured
Sarah Holloway's blog post was featured

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service