Drilling through a flue pipe of a power-vented combustion appliance

Here is a dilemma for a BPI-certified building auditor - should I or shouldn't I drill through a flue pipe of a power-vented combustion appliance? At first it seems obvious - don't. The BPI standards state that clearly. However, in the industry I see a number of people do that anyway. And even one of the best demo videos of combustion safety test performed by a BPI certified guy you can find online shows him drill through it in TWO places, without even a sign of doubt or concern on his face. Also, some government financing programs require you to gather that data that you can't get otherwise (sticking the probe from the outside into the chimney is not an option). 

Another question I see coming up is - since there is fan pushing those combustion gases out, wouldn't the pressure in the flue pipe be greater than the CAZ pressure? 

Would appreciate your experience on the matter.

Views: 3201

Reply to This

Replies to This Discussion

Eric, I am BA, Envelope and Heating BPI Certified. I have quite a bit of experience in HVAC. Some of the adjustments I could make, or I would either refer the homeowner to a HVAC tech or provide a service tech for them if it was a unit that I did not feel competent to repair. In NY where we have a very active Home Performance programs running, this has not been an issue or should it be. There is a great difference between placing a probe in a flue gas stream to measure vs. making repairs and/or adjustments.

To get back to the topic, BPI appears to be against the idea of drilling power vented (CAT IV, PVC vent). The reasons to not drill are the same as why the radon fan is outside the house and the pressurized part of the system is not allowed to go through living space.

I agree with you about the confidence and training.  I'm unclear on what level of combustion testing you would advocate for the BPI BA or Shell/Envelope person and if the current standards are allowing too much.  The scenario you gave (assuming compliance with the current BPI standards) about the testing results is addressed in the BPI standards  Adjustments, if required to be part of the work-scope, are required to be performed by a Heating, AC/Heat Pump, or other applicable BPI-certified person or, if performed by a non-BPI-certified applicable specialist, it must be approved by the appropriate BPI-certified specialist.  In other words, the BA and Shell guys are required to enlist the services of a more qualified professional.

 

I think the theme here is what should and what shouldn't the bazillion auditors out there be testing.  Everybody is trying to get on the same page about even the requirements of the existing standards.  As new standards come out and existing ones (hopefully) evolve, we need as much consensus on the do's and don'ts.  Surely we can come up with acceptable boundaries that will be safe and beneficial for all concerned.

 

As a BA and Shell/Envelope certified person, I don't drill PVC, B-vent, stainless steel or any positive pressure venting system.  I am still concerned about potential results of missed testing opportunities and wish there was an approved procedure that would allow the testing.  The limitations of many scenarios prohibit some folks from accessing the exterior vent openings; ladder or roof work may be necessary and not possible due to weather or other liability concerns.

 

I find it hard to believe that resealable test ports are not a requirement for all installations.  Wouldn't this be better for everyone?

As far as I can tell, the intent of the BPI standard is to determine whether or not there is negative CAZ pressure, and whether or not atmospheric draft appliances are burning cleanly. Checking out typical 80% equipment is quite easy and I don't think it creates any issues. If TWO things go wrong--a vent that's being backdrafted, AND a burner that's emitting a high level of CO, you have a possible disaster. With newer sealed combustion equipment the likelihood is very low, but there can still be issues. 

RSS

Featured Forum Discussions

Too many BTU's. Too much horsepower?

Started by Steve in General Forum. Last reply by Eric Kjelshus on Saturday. 4 Replies

Stack/wind pressure and flow networks.

Started by Daniel James Grundy in Training. Last reply by Daniel James Grundy on Thursday. 5 Replies

BDT with vermiculite in hollow CMU walls?

Started by Brad Cook in General Forum. Last reply by John Nicholas on Thursday. 2 Replies

Strange IR Image

Started by Larry Nissman in General Forum. Last reply by Brad Cook Mar 9. 7 Replies

Videos

  • Add Videos
  • View All

Latest Activity

Mike Rogers replied to Quinn Korzeniecki's discussion Don MacOdrum Receives BPI's 2017 Tony Woods Award and Four Others Inducted in to Hall of Fame in the group Building Performance Institute (BPI)
"Congratulations to Don! A deep thanks for the honor--and even more thanks to the many who've…"
19 minutes ago
Mike Rogers joined Building Performance Institute's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
19 minutes ago
Horace Douglas Hunt, Jr. replied to eric anderson's discussion Energy auditing equipment for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Have you sold this or still interested in sales of this equipment?"
3 hours ago
Charles Maier is now a member of Home Energy Pros
11 hours ago
Derrick Brodanex joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
yesterday
Eric Kjelshus replied to Steve's discussion Too many BTU's. Too much horsepower?
"Its more about run time with high RH removing, than to large over sized AC unit, in houses.  …"
Saturday
Sarah OConnell posted a blog post

Crowdsourcing for Innovation

Share Your Ideas!Novel Building Envelope Design for Increased Thermal PerformanceIn 2014, more than…See More
Friday
Colin de Paor is now a member of Home Energy Pros
Friday

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service