Drilling through a flue pipe of a power-vented combustion appliance

Here is a dilemma for a BPI-certified building auditor - should I or shouldn't I drill through a flue pipe of a power-vented combustion appliance? At first it seems obvious - don't. The BPI standards state that clearly. However, in the industry I see a number of people do that anyway. And even one of the best demo videos of combustion safety test performed by a BPI certified guy you can find online shows him drill through it in TWO places, without even a sign of doubt or concern on his face. Also, some government financing programs require you to gather that data that you can't get otherwise (sticking the probe from the outside into the chimney is not an option). 

Another question I see coming up is - since there is fan pushing those combustion gases out, wouldn't the pressure in the flue pipe be greater than the CAZ pressure? 

Would appreciate your experience on the matter.

Views: 3200

Reply to This

Replies to This Discussion

Jack wrote:   "one of the best demo videos of combustion safety test performed by a BPI certified guy you can find online"

The best you can find online?  How good does that have to be?  I'll grant that the production values are very good.

As for your concluding question, even an induced draft must be proven superior to the worst case conditions.

I'll come back after reviewing the video I paid for.

More precisely, in order to conform to the appliance in the video you referenced, fan-assisted draft, power burner type (fan located at inlet).  According to Krigger & Dorsi,

"Most fan-assisted heaters are vented into vertical chimneys and their draft fans have little or no effect on the atmospheric chimney draft. When a fan-assisted 80+ AFUE furnace or boiler is vented horizontally, the draft in the stainless-steel vent is positive.  The positive-draft vent must be substantially airtight."

I still haven't gotten to my video, but I've noticed that BPI allows drilling holes in such (Category I) vent designs.  Category IV, direct vent and power vented designs must be hole(s) free.

http://www.youtube.com/watch?v=7A7sExbFO8w

 

In this one he drills and tests a PVC flue. 

 

I've read a number of debates about this topic and rarely come across anything I'd hang my hat on. The vent pipe manufacturers will apparently all tell you not to drill their product. I've heard a few descriptions from seasoned techs about how to plug drilled holes in various types of pipe. Some states have licensing for HVAC contractors that doesn't allow a non-licensed person to touch a furnace or water heater. It's a can of worms...

The appliance in the video is not " power vented " , but is " induced draft " ,or " fan assisted " meaning Category I according to NFPA 54

(Cat I = negative pressure in the vent pipe , non-condensing ) This should not be a problem when drilling a test port properly.

Cat III or IV vented appliances are under positive pressure and the integrity of the vent pipe should not be breached unless you are prepared to replace the section or fittings that were opened and then re-test the ambient ..

Great question.

 

BF

Blaine, you beat me to it. There is a huge difference between a positive pressure Cat IV and a negative pressure Cat I vent system. With the Cat IV (positive pressure, PVC vent) there is condensation and some of the condensation is corrosive due to the other gases condensing as well as water vapor. If a test hole is drilled, and the seal is compromised in any way the flue gas will leak into the CAZ which is usually in the basement and the stack pressure will carry the flue gas through the house.

The best way to resolve this would be working with the manufacturers to install a test port in the furnace cabinet that we can utilize for testing.

Thank you very much, guys, your answers are very helpful.

It looks like we've figured out the CAT I versus III&IV concern --good feedback. 

 

I had to go watch the youtube link (pt 1&2) in Jack's question and, while it was clear and informative, it was incorrect on more than a few things.  For example, at 3:04 he incorrectly states that an induced draft furnace does not need to be checked for spillage. Per BPI Building Analyst standards p. 10, "Induced draft heating systems shall be checked for spillage at the base of the chimney liner or flue.  If a chimney is shared between and induced draft heating system and a natural draft water heater, spillage shall be checked at the water heater draft diverter." (emphasis added)

At 4:40 he just "calls it" for the CO levels versus checking to see if CO levels have leveled off or are still rising.  He must check to see if CO levels will continue to rise; if they exceed 100 ppm, then he must amend his workscope per BA standards p.14

 

I think both draft and CO of the furnace could have been checked from one port (his draft port); it would still be undiluted flue gas.  I could go on but it sort of feels like work.  If they post my comments to youtube maybe I'll continue.

I have to disagree with you on using those plugs. Cat IV PVC flues are pressurized and need to be sealed. How do those plugs seal into the hole? Are they glued in? is there a problem with the fact that they are a lighter, thinner material than the PVC? What kind of life span do they have in a moist, acidic, pressurized pipe?

 

This isn't hard, when there is PVC exhaust vent, you simply go outside to the vent termination and test the appliance. Simple, straight forward and reliable and you avoid any issue with drilling PVC vents.

I hadn't seen those before, but they look like they're intended for plugging holes in metal ductwork after taking pressures.

I guess I can't see why one cannot go outside and test at the vent terminal. Then there is no question about drilling PVC vents. I'll sleep better that night knowing that I didn't drill a hole and leave a compromised vent which could have the potential to fail and cause an indoor air quality issue at some point in the future.

Blaine & Chris have noted what should have been obvious to anyone considering testing mechanical equipment.  Although many states may not require licensing for this procedure one should not attempt without the highest confidence and training.  If you are not sure how to go about testing, what are you going to do with the results when they show that adjustments to the burner, gas valve or venting need to be done? I suggest hiring a competent service tech, leave it to the appliance professional.

 

RSS

Featured Forum Discussions

Too many BTU's. Too much horsepower?

Started by Steve in General Forum. Last reply by Walter Ahlgrim 1 hour ago. 3 Replies

Stack/wind pressure and flow networks.

Started by Daniel James Grundy in Training. Last reply by Daniel James Grundy 5 hours ago. 5 Replies

BDT with vermiculite in hollow CMU walls?

Started by Brad Cook in General Forum. Last reply by John Nicholas 11 hours ago. 2 Replies

Strange IR Image

Started by Larry Nissman in General Forum. Last reply by Brad Cook Mar 9. 7 Replies

Videos

  • Add Videos
  • View All

Latest Activity

Walter Ahlgrim replied to Steve's discussion Too many BTU's. Too much horsepower?
"The 5 ton system you have is not 500 hp racecar engines they are 500 hp truck engines. The duct…"
1 hour ago
Daniel James Grundy replied to Daniel James Grundy's discussion Stack/wind pressure and flow networks.
"So I wanted to start with a basic who can help then go into more detail later. But yes find…"
5 hours ago
Daniel James Grundy replied to Daniel James Grundy's discussion Stack/wind pressure and flow networks.
"My tutor got back to me and while areas don't quite feel right a little to much assumptions…"
6 hours ago
Brennan Less replied to Daniel James Grundy's discussion Stack/wind pressure and flow networks.
"Daniel, I'm assuming you're trying to predict the airflows through the different openings…"
7 hours ago
Martin Newmark joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
9 hours ago
John Nicholas replied to Brad Cook's discussion BDT with vermiculite in hollow CMU walls?
"If the drywall is in good shape, you should have little worries about the 50pa depressurization…"
11 hours ago
tedkidd replied to Steve's discussion Too many BTU's. Too much horsepower?
"Does the house ever feel clammy? Do you have to keep the thermostat below 74 to be comfortable? Is…"
14 hours ago
Danielle Sass Byrnett liked Diane Chojnowski's blog post Don MacOdrum receives BPI's 2017 Tony Woods Award!
14 hours ago

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service