Hi everyone,

I haven't been in the game too long (two years), but I have been in a few hundred houses. I have never seen a DHW exhaust like this in any house. There is no draft diverter at the top of the water heater, and the exhaust is continuous until it enters the chimney. It is commonly vented with the 80% efficient furnace.

I asked the owner about it, and she said she would have it checked into. Once she got back to me, she said the HVAC company she has on contract (this is a rental unit) said that the metal box in the middle of the picture is the draft diverter.

So, first, is that really a draft diverter? Second, if so, how does it work? I can only figure it's a valve of some sort. When or where can I expect to see this technology in the future?

Thanks in advance for all your feedback and advice.

Views: 1683

Reply to This

Replies to This Discussion

I was back in the residence today and took a look at the underside of the box in question. It is most certainly a draft diverter, but it looks as if it is decidedly unsafe. Based on the stack effect, the warm, moist air would circulate at the top of the box and cause the box to rust. I took a picture, and lo and behold that's exactly what's happening. I assume the box will eventually rust out, and the diverter will fail or the box will be compromised.

The primary purpose of a draft hood is to maintain a constant, and not excessive, draft from the appliance, much like the barometric damper on a furnace flue.

In many jurisdictions, you can't vent a gas appliance into the same flue used by any non-gas combustion appliance and the smaller BTU/hr burner must enter below the larger burner if two gas units share a common chimney.

Also, a large chimney flue may not generate enough draft speed to properly evacuate the water heater gasses, which may be why there is moisture accumulation in that intermediate draft hood, which is also far enough from the water heater to allow flue gasses to cool. The long horizontal run and the number of elbows will also significantly slow the flue gas speed.

I would recommend a complete rebuild of that flue system, using B-vent directly to the outside, with a proper draft hood at the water heater.

I am by no means an expert in this area & you should call one in to look at it but the applicable code is:

IRC 2009 - G2407.3 (304.3) Draft hood/regulator location. Where used, a draft hood or a barometric draft regulator shall be installed in the same room or enclosure as the appliance served so as to prevent any difference in pressure between the hood or regulator and the combustion air supply.

As for seeing this "technology" in the future - lets hope not as atmosperic devices should be going bye bye & replaced with direct vent

You also have to recall that a draft hoods main purpose is not to ensure a draft but to act as a safety feature in case the vent is blocked by allowing the gasses to escape into the room - Safety Sunday: Water Heaters, the Combustion Process & the Draf...

So, if I'm reading that correctly, as long as there is no pressure differential between the combustion air supply and draft hood, it is technically in compliance. The combustion air intake and draft hood are in the same room.

As far as "future," I meant in other houses, not as new units are installed, of course. I would be stunned to see something this silly in new installation.

Have you done any CAZ testing under worst case situations to test for combustion gas spillage? I agree that this horizontal venting holds a lot of potential for dangerous CO spillage. What are the rise, run and sizes of the flue pipes, including where and size of the flue the DWH is tied into?

Looks almost perfectly horizontal.  Think they took a level to it (lol)?

Strangely, it does slope within normal limits. I hadn't thought about flue gas condensation being a problem, though. On the plus side, there are a handful of CO detectors around the house.

The next step will be a full CAZ. Having not identified the box as the draft diverter, I didn't have a chance to do so.

Rob-

It might be a direct vent mobile home water heater installed in a house. This is only a guess but check underneath the water heater and look for a opening.

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Amber Vignieri posted a blog post
3 hours ago
ofer ben -nathan added a discussion to the group HVAC
11 hours ago
ofer ben -nathan joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
11 hours ago
Mary Knox replied to Kim Tanner's discussion Game of Homes
"Sounds interesting. I will definitely try it."
12 hours ago
Judy Roberson joined Norm Bourassa's group
Thumbnail

Multifamily Buildings

For too long there has been relatively little EE focus on multifamily, but some new programs have…See More
17 hours ago
Peter Cantone liked Tom White's blog post Energy Raters and Builders Raise the Bar for Home Performance at RESNET’s Building Performance Conference
yesterday
Diane Chojnowski's 6 events were featured
yesterday
Diane Chojnowski posted events
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service