Hi everyone,

I haven't been in the game too long (two years), but I have been in a few hundred houses. I have never seen a DHW exhaust like this in any house. There is no draft diverter at the top of the water heater, and the exhaust is continuous until it enters the chimney. It is commonly vented with the 80% efficient furnace.

I asked the owner about it, and she said she would have it checked into. Once she got back to me, she said the HVAC company she has on contract (this is a rental unit) said that the metal box in the middle of the picture is the draft diverter.

So, first, is that really a draft diverter? Second, if so, how does it work? I can only figure it's a valve of some sort. When or where can I expect to see this technology in the future?

Thanks in advance for all your feedback and advice.

Views: 368

Reply to This

Replies to This Discussion

I was back in the residence today and took a look at the underside of the box in question. It is most certainly a draft diverter, but it looks as if it is decidedly unsafe. Based on the stack effect, the warm, moist air would circulate at the top of the box and cause the box to rust. I took a picture, and lo and behold that's exactly what's happening. I assume the box will eventually rust out, and the diverter will fail or the box will be compromised.

The primary purpose of a draft hood is to maintain a constant, and not excessive, draft from the appliance, much like the barometric damper on a furnace flue.

In many jurisdictions, you can't vent a gas appliance into the same flue used by any non-gas combustion appliance and the smaller BTU/hr burner must enter below the larger burner if two gas units share a common chimney.

Also, a large chimney flue may not generate enough draft speed to properly evacuate the water heater gasses, which may be why there is moisture accumulation in that intermediate draft hood, which is also far enough from the water heater to allow flue gasses to cool. The long horizontal run and the number of elbows will also significantly slow the flue gas speed.

I would recommend a complete rebuild of that flue system, using B-vent directly to the outside, with a proper draft hood at the water heater.

I am by no means an expert in this area & you should call one in to look at it but the applicable code is:

IRC 2009 - G2407.3 (304.3) Draft hood/regulator location. Where used, a draft hood or a barometric draft regulator shall be installed in the same room or enclosure as the appliance served so as to prevent any difference in pressure between the hood or regulator and the combustion air supply.

As for seeing this "technology" in the future - lets hope not as atmosperic devices should be going bye bye & replaced with direct vent

You also have to recall that a draft hoods main purpose is not to ensure a draft but to act as a safety feature in case the vent is blocked by allowing the gasses to escape into the room - Safety Sunday: Water Heaters, the Combustion Process & the Draf...

So, if I'm reading that correctly, as long as there is no pressure differential between the combustion air supply and draft hood, it is technically in compliance. The combustion air intake and draft hood are in the same room.

As far as "future," I meant in other houses, not as new units are installed, of course. I would be stunned to see something this silly in new installation.

Have you done any CAZ testing under worst case situations to test for combustion gas spillage? I agree that this horizontal venting holds a lot of potential for dangerous CO spillage. What are the rise, run and sizes of the flue pipes, including where and size of the flue the DWH is tied into?

Looks almost perfectly horizontal.  Think they took a level to it (lol)?

Strangely, it does slope within normal limits. I hadn't thought about flue gas condensation being a problem, though. On the plus side, there are a handful of CO detectors around the house.

The next step will be a full CAZ. Having not identified the box as the draft diverter, I didn't have a chance to do so.

Rob-

It might be a direct vent mobile home water heater installed in a house. This is only a guess but check underneath the water heater and look for a opening.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Home Energy Magazine posted a blog post
55 minutes ago
Egr renovation posted a status
"of course he is in paris but works around europe http://ning.it/16KrbS7"
1 hour ago
Egr renovation posted a status
"i just find a good photogrpahe for your master piece http://www.armanimage.com"
1 hour ago

Tom Mallard just added their location.
(via Member Map)

17 hours ago
Profile IconDon Hughes, Julian Sark, James Hatheway and 4 more joined Home Energy Pros
19 hours ago
Meagan Foster posted events
20 hours ago
Meagan Foster updated an event

EnergyLogic's RaterFest! at Black Hawk, CO

September 13, 2013 at 10am to September 15, 2013 at 12pm
Join us for one of the best home energy conferences available!  This retreat will provide…See More
20 hours ago
Meagan Foster updated an event

Homes 401: Green Rater Training at Berthoud, CO

June 25, 2013 to June 26, 2013
This highly interactive workshop builds upon the material presented in the online course, further…See More
20 hours ago
Meagan Foster updated an event

HERS Rater Training - Online at Online

July 1, 2013 to July 26, 2013
NEW - our great RESNET HERS Rater online training is now completely self-paced, so you can start at…See More
20 hours ago
Meagan Foster updated an event

BPI Building Analyst Training - Online at Online

June 3, 2013 to June 28, 2013
Join the EnergyLogic Academy for our BPI BA online training - we just went to a completely open…See More
20 hours ago
Anna Svensson posted a discussion

Looking for residential building and remodeling experts

Making sure you residential building and remodeling professionals out there are aware of the call…See More
21 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service