Hi everyone,

I haven't been in the game too long (two years), but I have been in a few hundred houses. I have never seen a DHW exhaust like this in any house. There is no draft diverter at the top of the water heater, and the exhaust is continuous until it enters the chimney. It is commonly vented with the 80% efficient furnace.

I asked the owner about it, and she said she would have it checked into. Once she got back to me, she said the HVAC company she has on contract (this is a rental unit) said that the metal box in the middle of the picture is the draft diverter.

So, first, is that really a draft diverter? Second, if so, how does it work? I can only figure it's a valve of some sort. When or where can I expect to see this technology in the future?

Thanks in advance for all your feedback and advice.

Views: 346

Reply to This

Replies to This Discussion

I was back in the residence today and took a look at the underside of the box in question. It is most certainly a draft diverter, but it looks as if it is decidedly unsafe. Based on the stack effect, the warm, moist air would circulate at the top of the box and cause the box to rust. I took a picture, and lo and behold that's exactly what's happening. I assume the box will eventually rust out, and the diverter will fail or the box will be compromised.

The primary purpose of a draft hood is to maintain a constant, and not excessive, draft from the appliance, much like the barometric damper on a furnace flue.

In many jurisdictions, you can't vent a gas appliance into the same flue used by any non-gas combustion appliance and the smaller BTU/hr burner must enter below the larger burner if two gas units share a common chimney.

Also, a large chimney flue may not generate enough draft speed to properly evacuate the water heater gasses, which may be why there is moisture accumulation in that intermediate draft hood, which is also far enough from the water heater to allow flue gasses to cool. The long horizontal run and the number of elbows will also significantly slow the flue gas speed.

I would recommend a complete rebuild of that flue system, using B-vent directly to the outside, with a proper draft hood at the water heater.

I am by no means an expert in this area & you should call one in to look at it but the applicable code is:

IRC 2009 - G2407.3 (304.3) Draft hood/regulator location. Where used, a draft hood or a barometric draft regulator shall be installed in the same room or enclosure as the appliance served so as to prevent any difference in pressure between the hood or regulator and the combustion air supply.

As for seeing this "technology" in the future - lets hope not as atmosperic devices should be going bye bye & replaced with direct vent

You also have to recall that a draft hoods main purpose is not to ensure a draft but to act as a safety feature in case the vent is blocked by allowing the gasses to escape into the room - Safety Sunday: Water Heaters, the Combustion Process & the Draf...

So, if I'm reading that correctly, as long as there is no pressure differential between the combustion air supply and draft hood, it is technically in compliance. The combustion air intake and draft hood are in the same room.

As far as "future," I meant in other houses, not as new units are installed, of course. I would be stunned to see something this silly in new installation.

Have you done any CAZ testing under worst case situations to test for combustion gas spillage? I agree that this horizontal venting holds a lot of potential for dangerous CO spillage. What are the rise, run and sizes of the flue pipes, including where and size of the flue the DWH is tied into?

Looks almost perfectly horizontal.  Think they took a level to it (lol)?

Strangely, it does slope within normal limits. I hadn't thought about flue gas condensation being a problem, though. On the plus side, there are a handful of CO detectors around the house.

The next step will be a full CAZ. Having not identified the box as the draft diverter, I didn't have a chance to do so.

Rob-

It might be a direct vent mobile home water heater installed in a house. This is only a guess but check underneath the water heater and look for a opening.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

George Kopf posted a discussion

Misting Aeroseal in Pressurized Home = Amazing Air Sealing Innovation

As a training program manager for a non-profit, I am often too busy managing my program to catch…See More
5 minutes ago
Dennis Heidner replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"Ben,  the German highway system concept actually started BEFORE Nazi Germany during  the…"
11 hours ago
Stan Kuhn replied to Patrick Michaelyan's discussion Hot Upper Stories
"You note overheating on the south side (naturally.)  Assuming the typical roof overhang of…"
16 hours ago
Patrick Michaelyan replied to Patrick Michaelyan's discussion Hot Upper Stories
"Thanks a lot Ed. And thanks to all who have added their two cents. I think I know where to take…"
17 hours ago
Ed Minch replied to Patrick Michaelyan's discussion Hot Upper Stories
"We have successfully treated this same problem in perhaps 1000 of this same house in the…"
18 hours ago
Craig Savage commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Hello Tom We are working with A.O. Smith, GE and Stiebel Eltron on a Building America task to…"
19 hours ago
Tom Delconte commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Craig: I was serious, since my propane price jumped from .98 to 1.85! according to everyone the GE…"
20 hours ago
Ben Jacobs replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"I think that government support for good ideas results in major benefits over the long haul. Please…"
21 hours ago
Craig Savage commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Hello Tom Not sure if you are being sarcastic, but a serious answer would be that GE is selling…"
23 hours ago
Tom Delconte commented on Craig Savage's video
Thumbnail

What is a Heat Pump Water Heater

"Craig: do you have a diagram of one that will run longer than one year? They don't really seem…"
yesterday
Cory Chovanec replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"All good points brought up. My advice is not to leave the lights. When you said halogen I think…"
yesterday
Jon Haehnel replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"The first 2 answers by Tom and Sean jive with my thinking and experience. Thank you Don for…"
yesterday

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service