Hi everyone,

I haven't been in the game too long (two years), but I have been in a few hundred houses. I have never seen a DHW exhaust like this in any house. There is no draft diverter at the top of the water heater, and the exhaust is continuous until it enters the chimney. It is commonly vented with the 80% efficient furnace.

I asked the owner about it, and she said she would have it checked into. Once she got back to me, she said the HVAC company she has on contract (this is a rental unit) said that the metal box in the middle of the picture is the draft diverter.

So, first, is that really a draft diverter? Second, if so, how does it work? I can only figure it's a valve of some sort. When or where can I expect to see this technology in the future?

Thanks in advance for all your feedback and advice.

Views: 1939

Reply to This

Replies to This Discussion

I was back in the residence today and took a look at the underside of the box in question. It is most certainly a draft diverter, but it looks as if it is decidedly unsafe. Based on the stack effect, the warm, moist air would circulate at the top of the box and cause the box to rust. I took a picture, and lo and behold that's exactly what's happening. I assume the box will eventually rust out, and the diverter will fail or the box will be compromised.

The primary purpose of a draft hood is to maintain a constant, and not excessive, draft from the appliance, much like the barometric damper on a furnace flue.

In many jurisdictions, you can't vent a gas appliance into the same flue used by any non-gas combustion appliance and the smaller BTU/hr burner must enter below the larger burner if two gas units share a common chimney.

Also, a large chimney flue may not generate enough draft speed to properly evacuate the water heater gasses, which may be why there is moisture accumulation in that intermediate draft hood, which is also far enough from the water heater to allow flue gasses to cool. The long horizontal run and the number of elbows will also significantly slow the flue gas speed.

I would recommend a complete rebuild of that flue system, using B-vent directly to the outside, with a proper draft hood at the water heater.

I am by no means an expert in this area & you should call one in to look at it but the applicable code is:

IRC 2009 - G2407.3 (304.3) Draft hood/regulator location. Where used, a draft hood or a barometric draft regulator shall be installed in the same room or enclosure as the appliance served so as to prevent any difference in pressure between the hood or regulator and the combustion air supply.

As for seeing this "technology" in the future - lets hope not as atmosperic devices should be going bye bye & replaced with direct vent

You also have to recall that a draft hoods main purpose is not to ensure a draft but to act as a safety feature in case the vent is blocked by allowing the gasses to escape into the room - Safety Sunday: Water Heaters, the Combustion Process & the Draf...

So, if I'm reading that correctly, as long as there is no pressure differential between the combustion air supply and draft hood, it is technically in compliance. The combustion air intake and draft hood are in the same room.

As far as "future," I meant in other houses, not as new units are installed, of course. I would be stunned to see something this silly in new installation.

Have you done any CAZ testing under worst case situations to test for combustion gas spillage? I agree that this horizontal venting holds a lot of potential for dangerous CO spillage. What are the rise, run and sizes of the flue pipes, including where and size of the flue the DWH is tied into?

Looks almost perfectly horizontal.  Think they took a level to it (lol)?

Strangely, it does slope within normal limits. I hadn't thought about flue gas condensation being a problem, though. On the plus side, there are a handful of CO detectors around the house.

The next step will be a full CAZ. Having not identified the box as the draft diverter, I didn't have a chance to do so.


It might be a direct vent mobile home water heater installed in a house. This is only a guess but check underneath the water heater and look for a opening.



  • Add Videos
  • View All


Latest Activity

Tom White's video was featured

Retrofitting Vintage Home for Energy Efficiency

A presentation by Greg Labbé in April 2014 on retrofitting vintage home for energy efficiency. He talked about basic building science, brick houses, movement of heat energy and moisture in and out of the house, air barrier and water barrier, house…
22 minutes ago
Sam Goode is now a member of Home Energy Pros
18 hours ago
Tina Gleisner commented on Tom White's video

How to Insulate a Tiny House (or a Big Fat House)

"Really like how Corbett tells his story in a simple manner that homeowners should be able to…"
21 hours ago
Tom Mallard commented on Tom White's video

How to Insulate a Tiny House (or a Big Fat House)

"So consider the conduction paths of studs-rafters show quite clearly, to counter this requires…"
22 hours ago
Davide Lanzoni commented on Tom White's video

How to Insulate a Tiny House (or a Big Fat House)

"Very cool the thermal tuning with body in white and glasses in black !"
23 hours ago
Quinn Korzeniecki posted a discussion

Applications for Jon Siemen Scholarship Due by 11/31

Thinking of obtaining a BPI Quality Control Inspector (QCI), Energy Auditor (EA), Crew Leader, or…See More
23 hours ago
Benny hani replied to Benny hani's discussion Manual J online
"Thanks Bob"
Benny hani replied to Benny hani's discussion Manual J online
"Thank you Isaac"

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service