I did an audit yesterday and found out that a single doggy door was responsible for 1,300 CFM50 of air leakage (in an already-leaky house...total leakage of 5,300 CFM50 and only 2,200 square feet of conditioned floor area).

So, what to do about this doggy door? I could spent some time thinking of a clever way to address this, or do some research online, but I thought of y'all first, as the preeminent professionals.

Any advice?

Thanks,

Patrick

Views: 696

Reply to This

Replies to This Discussion

Replace it with one that has two doors (one on each side) & magnets - they work great

I can't recall the brand but the last few I got were at Home Depot & I think I even saw them at Lowe's

Most pet flaps have some sort of positive closure, magnet or similar, and for the most part they work OK, although some air works its way around the flap's perimeter.


What I think happened here is that the blower door test pressure, which far exceeds natural pressure, overwhelmed the flap's magnet and it swung open, allowing an extra 1300 CFM. That should not occur under normal, non-blower-door test conditions.

Let me call Bull - if the blower door could pull it open, that means the wind will easily blow it open as it wasn't able to resist one pound of pressure (PSF) --- for more see Pascals & Pressure 

Either the magnet is shot, it is filthy, or the unit is worthless, which is one reason why I like the double flap system

 

I appreciate the frankness Sean (I really do).

Let me look into this flap again, and maybe these folks are looking at the POS series pet flap.

The blower door test pressure of 50 Pa is roughly equivalent to a 20 mph wind, which is quite uncommon in most areas

Unless you live in Oklahoma.

Thanks Curt.

I have to look at this flap again. It appeared to fit by friction.

Locating pet doors on a relatively sheltered wall of the house could help. I've been designing a two door doggie airlock in my head. It would be disguised as a bench (or banco in my neck of the woods), be heavily insulated, and vented to the exterior to disperse pulses of wind back to the outside of the house. If the vent could exhaust around a corner from the exterior flap that would be best, and it should have some kind of a flapper to reduce air coming in it. Or build the whole thing on the outside as a tunnel with exterior door at the end and vents both sides.

Locating Doggie Doors on South or East walls helps a lot.

worry more about the other 4000 cfm

the air coming from the dog door is fresh air

Where is the other 4000 cfm coming from?

S

I recently had a similar situation, only the doggy door was big enough for an adolescent to crawl through. When I told my client she should consider replacing the door, she waxed nostalgic about the happy times when her dog and children would chase each other through the door. She made it clear she'd never replace the thing. I still haven't done any work for her.

Another trick I've seen is to dedicate the bottom half of a cabinet as a vestibule/mud-room with a second air-lock flapper like Peter suggests.  Obviously you'ed need to design some people access to clean it out occasionally, but I agree with Glen re. the other 4000 cfm. 

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Helen Best posted a blog post

Low-Flow Shower Heads Save Water

Just about everyone enjoys a nice long hot shower. It does come with some cost for the water and…See More
1 hour ago
Helen Best liked Helen Best's blog post This Might Be the Most Water-Efficient Shower Head Ever Invented
2 hours ago
Therma-HEXX posted blog posts
6 hours ago
Michael Dunseith posted photos
8 hours ago
Jeffrey Anthony posted a discussion

9 Blower Door Frames, 9 Shrouds, and 11 Fans, and 8 Fan Controllers For Sale

We are clearing out some of our redundant inventory. All items are from The Energy Conservatory.9…See More
10 hours ago
Quinn Korzeniecki posted a discussion

Five Retrotec Products Added to BPI Product List

The Building Performance Institute, Inc. (BPI) has recognized five new products in its Product…See More
11 hours ago
Tom White's video was featured

New York energy policy & North American Passive House Network Conference

New York is increasing its energy standards and is investigating the possibility of implementing the Passive House Standard for new construction and retrofit projects. Interviewee: Ken Levenson, with NY Passive House Assoc and 475.
11 hours ago
Profile IconRichard Hale, Joseph Schulman, Carol W and 1 more joined Home Energy Pros
12 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service