I did an audit yesterday and found out that a single doggy door was responsible for 1,300 CFM50 of air leakage (in an already-leaky house...total leakage of 5,300 CFM50 and only 2,200 square feet of conditioned floor area).

So, what to do about this doggy door? I could spent some time thinking of a clever way to address this, or do some research online, but I thought of y'all first, as the preeminent professionals.

Any advice?

Thanks,

Patrick

Views: 760

Reply to This

Replies to This Discussion

Replace it with one that has two doors (one on each side) & magnets - they work great

I can't recall the brand but the last few I got were at Home Depot & I think I even saw them at Lowe's

Most pet flaps have some sort of positive closure, magnet or similar, and for the most part they work OK, although some air works its way around the flap's perimeter.


What I think happened here is that the blower door test pressure, which far exceeds natural pressure, overwhelmed the flap's magnet and it swung open, allowing an extra 1300 CFM. That should not occur under normal, non-blower-door test conditions.

Let me call Bull - if the blower door could pull it open, that means the wind will easily blow it open as it wasn't able to resist one pound of pressure (PSF) --- for more see Pascals & Pressure 

Either the magnet is shot, it is filthy, or the unit is worthless, which is one reason why I like the double flap system

 

I appreciate the frankness Sean (I really do).

Let me look into this flap again, and maybe these folks are looking at the POS series pet flap.

The blower door test pressure of 50 Pa is roughly equivalent to a 20 mph wind, which is quite uncommon in most areas

Unless you live in Oklahoma.

Thanks Curt.

I have to look at this flap again. It appeared to fit by friction.

Locating pet doors on a relatively sheltered wall of the house could help. I've been designing a two door doggie airlock in my head. It would be disguised as a bench (or banco in my neck of the woods), be heavily insulated, and vented to the exterior to disperse pulses of wind back to the outside of the house. If the vent could exhaust around a corner from the exterior flap that would be best, and it should have some kind of a flapper to reduce air coming in it. Or build the whole thing on the outside as a tunnel with exterior door at the end and vents both sides.

Locating Doggie Doors on South or East walls helps a lot.

worry more about the other 4000 cfm

the air coming from the dog door is fresh air

Where is the other 4000 cfm coming from?

S

I recently had a similar situation, only the doggy door was big enough for an adolescent to crawl through. When I told my client she should consider replacing the door, she waxed nostalgic about the happy times when her dog and children would chase each other through the door. She made it clear she'd never replace the thing. I still haven't done any work for her.

Another trick I've seen is to dedicate the bottom half of a cabinet as a vestibule/mud-room with a second air-lock flapper like Peter suggests.  Obviously you'ed need to design some people access to clean it out occasionally, but I agree with Glen re. the other 4000 cfm. 

RSS

Featured Forum Discussions

BPI Anaylist

Started by Larry R Waters in BPI 46 minutes ago. 0 Replies

What causes a temperature plane in a home

Started by Energy Wise Solutions in HVAC. Last reply by Brad Cook 9 hours ago. 6 Replies

Velocity Pressure Testing

Started by Horace Douglas Hunt, Jr. in General Forum. Last reply by Horace Douglas Hunt, Jr. Apr 15. 2 Replies

Videos

  • Add Videos
  • View All

Latest Activity

Larry R Waters posted a discussion

BPI Anaylist

Industry leader in the north bay area California. Looking for experienced professionals and…See More
46 minutes ago
Larry R Waters joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
51 minutes ago
John Nicholas replied to Jim Fowler's discussion TREAT modeling of mid-rise apartments low heating load
"So why is tenant behavior significantly different in this building?"
1 hour ago
Jim Fowler replied to Jim Fowler's discussion TREAT modeling of mid-rise apartments low heating load
"Hi John - I'm strictly modeling the entire building, not individual units. I'm looking…"
2 hours ago
John Nicholas replied to Jim Fowler's discussion TREAT modeling of mid-rise apartments low heating load
"Where is this going?  Are you (the housing authority) trying to set the Utility Allowance?…"
6 hours ago
Brad Cook replied to Energy Wise Solutions's discussion What causes a temperature plane in a home
"It is interesting that people respond to questions like this with answers that make some…"
9 hours ago
Ed Minch replied to Energy Wise Solutions's discussion What causes a temperature plane in a home
"We see this in the mid-Atlantic with ceiling feeds on a hot air system, and usually with a…"
10 hours ago
North East Hydronic Radiant Inc posted photos
13 hours ago

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service