I did an audit yesterday and found out that a single doggy door was responsible for 1,300 CFM50 of air leakage (in an already-leaky house...total leakage of 5,300 CFM50 and only 2,200 square feet of conditioned floor area).

So, what to do about this doggy door? I could spent some time thinking of a clever way to address this, or do some research online, but I thought of y'all first, as the preeminent professionals.

Any advice?

Thanks,

Patrick

Views: 362

Reply to This

Replies to This Discussion

Replace it with one that has two doors (one on each side) & magnets - they work great

I can't recall the brand but the last few I got were at Home Depot & I think I even saw them at Lowe's

Most pet flaps have some sort of positive closure, magnet or similar, and for the most part they work OK, although some air works its way around the flap's perimeter.


What I think happened here is that the blower door test pressure, which far exceeds natural pressure, overwhelmed the flap's magnet and it swung open, allowing an extra 1300 CFM. That should not occur under normal, non-blower-door test conditions.

Let me call Bull - if the blower door could pull it open, that means the wind will easily blow it open as it wasn't able to resist one pound of pressure (PSF) --- for more see Pascals & Pressure 

Either the magnet is shot, it is filthy, or the unit is worthless, which is one reason why I like the double flap system

 

I appreciate the frankness Sean (I really do).

Let me look into this flap again, and maybe these folks are looking at the POS series pet flap.

The blower door test pressure of 50 Pa is roughly equivalent to a 20 mph wind, which is quite uncommon in most areas

Unless you live in Oklahoma.

Thanks Curt.

I have to look at this flap again. It appeared to fit by friction.

Locating pet doors on a relatively sheltered wall of the house could help. I've been designing a two door doggie airlock in my head. It would be disguised as a bench (or banco in my neck of the woods), be heavily insulated, and vented to the exterior to disperse pulses of wind back to the outside of the house. If the vent could exhaust around a corner from the exterior flap that would be best, and it should have some kind of a flapper to reduce air coming in it. Or build the whole thing on the outside as a tunnel with exterior door at the end and vents both sides.

Locating Doggie Doors on South or East walls helps a lot.

worry more about the other 4000 cfm

the air coming from the dog door is fresh air

Where is the other 4000 cfm coming from?

S

I recently had a similar situation, only the doggy door was big enough for an adolescent to crawl through. When I told my client she should consider replacing the door, she waxed nostalgic about the happy times when her dog and children would chase each other through the door. She made it clear she'd never replace the thing. I still haven't done any work for her.

Another trick I've seen is to dedicate the bottom half of a cabinet as a vestibule/mud-room with a second air-lock flapper like Peter suggests.  Obviously you'ed need to design some people access to clean it out occasionally, but I agree with Glen re. the other 4000 cfm. 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Mark Richardson added a discussion to the group Renewable Energy
Thumbnail

Disasters & sustainable energy

Read my response to J.C. Martel's discussion:…See More
7 hours ago
Mark Richardson replied to J.C. Martel's discussion Disasters & sustainable energy
"Hi All, Interesting topic - myriad issues in play here, but I’ll try to touch on the ones I…"
7 hours ago
Eric Kjelshus replied to Johnny Ritzo's discussion Selecting a Water Heater
"I have been using  Rheem or State or Brad/white PVC flued tank type hot water heater…"
19 hours ago
Bachi Brunato replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"As it turns out, we have 10 Halo 99RT housings with Halo 998P Eyeball trim in the kitchen. The trim…"
22 hours ago
Bachi Brunato's discussion was featured

Boxing and Insulating Around Non-ICAT Cans

I have a client with 16) 4" halogen recessed light fixtures in the attic.I'd like to cover the cans…See More
yesterday
Johnny Ritzo's discussion was featured

Selecting a Water Heater

I am looking at updating the heating and water heating systems in a rental home I recently…See More
yesterday
George Kopf's discussion was featured

Misting Aeroseal in Pressurized Home = Amazing Air Sealing Innovation

As a training program manager for a non-profit, I am often too busy managing my program to catch…See More
yesterday
Tom Delconte's blog post was featured
yesterday
Christopher Morin's blog post was featured

Selling with Rebates: The Simple Payback

  The easiest way to show a homeowner how their investment in high-efficient equipment will help…See More
yesterday
Edward Foskey's blog post was featured
yesterday
Mike Rogers's blog post was featured

HOMES Act introduced with Bi-Partisan Sponsorship

We don't see a lot of bi-partisan bills in Congress these days. Here's one focusing on home…See More
yesterday
Mike Rogers posted a blog post

HOMES Act introduced with Bi-Partisan Sponsorship

We don't see a lot of bi-partisan bills in Congress these days. Here's one focusing on home…See More
yesterday

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service