I did an audit yesterday and found out that a single doggy door was responsible for 1,300 CFM50 of air leakage (in an already-leaky house...total leakage of 5,300 CFM50 and only 2,200 square feet of conditioned floor area).

So, what to do about this doggy door? I could spent some time thinking of a clever way to address this, or do some research online, but I thought of y'all first, as the preeminent professionals.

Any advice?

Thanks,

Patrick

Views: 551

Reply to This

Replies to This Discussion

Replace it with one that has two doors (one on each side) & magnets - they work great

I can't recall the brand but the last few I got were at Home Depot & I think I even saw them at Lowe's

Most pet flaps have some sort of positive closure, magnet or similar, and for the most part they work OK, although some air works its way around the flap's perimeter.


What I think happened here is that the blower door test pressure, which far exceeds natural pressure, overwhelmed the flap's magnet and it swung open, allowing an extra 1300 CFM. That should not occur under normal, non-blower-door test conditions.

Let me call Bull - if the blower door could pull it open, that means the wind will easily blow it open as it wasn't able to resist one pound of pressure (PSF) --- for more see Pascals & Pressure 

Either the magnet is shot, it is filthy, or the unit is worthless, which is one reason why I like the double flap system

 

I appreciate the frankness Sean (I really do).

Let me look into this flap again, and maybe these folks are looking at the POS series pet flap.

The blower door test pressure of 50 Pa is roughly equivalent to a 20 mph wind, which is quite uncommon in most areas

Unless you live in Oklahoma.

Thanks Curt.

I have to look at this flap again. It appeared to fit by friction.

Locating pet doors on a relatively sheltered wall of the house could help. I've been designing a two door doggie airlock in my head. It would be disguised as a bench (or banco in my neck of the woods), be heavily insulated, and vented to the exterior to disperse pulses of wind back to the outside of the house. If the vent could exhaust around a corner from the exterior flap that would be best, and it should have some kind of a flapper to reduce air coming in it. Or build the whole thing on the outside as a tunnel with exterior door at the end and vents both sides.

Locating Doggie Doors on South or East walls helps a lot.

worry more about the other 4000 cfm

the air coming from the dog door is fresh air

Where is the other 4000 cfm coming from?

S

I recently had a similar situation, only the doggy door was big enough for an adolescent to crawl through. When I told my client she should consider replacing the door, she waxed nostalgic about the happy times when her dog and children would chase each other through the door. She made it clear she'd never replace the thing. I still haven't done any work for her.

Another trick I've seen is to dedicate the bottom half of a cabinet as a vestibule/mud-room with a second air-lock flapper like Peter suggests.  Obviously you'ed need to design some people access to clean it out occasionally, but I agree with Glen re. the other 4000 cfm. 

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner replied to Hal Skinner's discussion How our ceramic based RCC works in the group Radiant Control Coatings
"Hey Tom, I will find the ORNL repoprt and post it.  It was a test on a ballasted roof sample.…"
5 hours ago
Tom Mallard replied to Hal Skinner's discussion How our ceramic based RCC works in the group Radiant Control Coatings
"So it seems that what you're saying is for heat-transfer the stuff has little resistance or…"
6 hours ago
Hal Skinner added a discussion to the group Radiant Control Coatings
Thumbnail

How our ceramic based RCC works

How our RCC worksEveryone knows, understands and accepts that RCCs reflect heat away from roofs,…See More
7 hours ago
Mike Kandel posted a discussion

Earn BPI CEUs at 3rd Annual Building Performance Forum

If you're searching for BPI CEUs, you'll find plenty at the 3rd Annual Building Performance Forum…See More
12 hours ago
Mike Kandel added a discussion to the group Building Performance Institute (BPI)
Thumbnail

Earn BPI CEUs at 3rd Annual Building Performance Forum

If you're searching for BPI CEUs, you'll find plenty at the 3rd Annual Building Performance Forum…See More
12 hours ago
Sean Lintow Sr commented on Christopher Morin's blog post UPDATED: Big Changes for Duct Testing in MA
"4% TOTAL Ted - Leakage to outside was stripped from the codes & for good reason"
15 hours ago
tedkidd commented on Christopher Morin's blog post UPDATED: Big Changes for Duct Testing in MA
"Wait!  4% total leakage or 4% leakage to outdoors? "
16 hours ago
Tom White's video was featured

Alliant Energy's PowerHouse TV: Sealing Leaky Ductwork

The PowerHouse television shows are written and produced by Alliant Energy, an energy services company based in Madison, Wis. The first PowerHouse episode was aired in September 1996 on KCRG-TV9 in Cedar Rapids, Iowa, and appears in six broadcast…
18 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service