Dirty Sock Syndrome in high efficiency HVAC units

I was recently told my new HE HVAC unit has the dreaded dirty sock syndrome.  Never had this problem with the old unit.  My research shows me it is usually tied to heat pumps.  I have a gas furnace.  Research shows mixed opinions on solutions: UV lights, treated coils, etc.  I do not want to fork out any more money if it's not going to fix the problem.  I was also advised to run the A/C with the windows open to clear out the smell.  I did this and it did not work (and now I feel guilty for wasting energy all day).  I was told there is no health threat associated with DSS.  How is this not possible?  I have a 9-month baby in the house and am concerned.  What are my options?  And am I responsible financially for the fix (if there is a fix)?  

Views: 6845

Reply to This

Replies to This Discussion

Dirty Sock Syndrome is actually caused by a combination of bacterial "slime" (biofilm) and mold, such as yeasts, that typically grow on the coils of the unit.  The biofilm has been described as being like the slippery, slimy surface that develops inside a pet's water bowl. I think you would agree that is not significantly hazardous either.

I have tested for it (mainly mold) in several instances and have read similar accounts.  Essentially the mold spores do not easily become airborne, perhaps because they grow in the slime, nor are yeasts generally considered particularly hazardous.  Therefore it is rare to even detect the mold in air samples.  The bacteria is also not of a concern other than the odor it creates.  Unfortunately I have not read of any surefire long-term remediation method either.

Thanks Bob.  Glad to read your thoughts on the low health risks associated with DSS.  

I had a customer who came to me about DSS.  She had been looking for an answer for several years, after trying ultraviolet lights, filters, bleach, etc.  The smell only occurred in the fall, after the cooling season.  I found some flex duct returns that had a low spot where moisture accumulated and didn't drain. In any case, she had the ducting removed entirely, replaced with steel ducts, and the DSS disappeared.

Thanks Andrew, but I'm not sure I'm ready to go this route.  It seems like I would have experienced DSS with my previous unit if the problem is in the ducts.  

Your mention of the low spot in the flex ducting collecting water (thereby soaking the insulation at some point, most likely) makes me wonder if internal duct lining may contribute to DSS. The OP is puzzled by his DSS in that he's running a gas furnace instead of a heat pump, where DSS problems are commonly reported.

That your customer had her ducting replaced with steel ducts, and with the assumption said ducts were externally insulated vs. internally insulated, makes me think internal lining of ducts remains not to be a good idea.

Was the AC coil and drip pan checked for mold?  That would be the easiest fix.

No, actually the service tech gave me his diagnosis just by asking me questions.  We have since called the dealer back and they are sending someone else out to further assess the situation.  I will definitely make sure they check the coil and drip pan for mold.  The gentleman on the phone said they may need to order us a new coil.  

I'm still perplexed as to why this is happening since we have a gas furnace and all my research ties DSS to heat pumps.  Research has also shown that DSS is common with high efficiency units.  Any thoughts as to why?   

 I would keep good tabs on effects on your baby as a first priority.  Coils can be cleaned, they don't have to be thrown away when dirty.  Has your heat run since the furnace was installed?  You stated that you ran the AC but didn't mention the heat.  My GUESS as to the reason for the problem with heat pumps is that they generate a low temperature heat vs. a gas furnace, and the higher temperatures of the gas furnace may kill mold spores on the coil.  If the heat hasn't run, try it.

Thanks Stan. I am still very concerned about the effects on my baby... almost to the point where I don't want to run the A/C until this problem gets resolved.  Seeing how we live in Texas, this could be challenging.  

And to answer your question... we have been using the gas furnace all winter, which is why I don't understand why we're experiencing DSS.  We've had a few warm spells this January and have turned on the A/C, which is when we notice the smell.  Is it possible that it's the high efficiency of the gas furnace that's preventing the temperatures from getting hot enough to kill the mold spores?  

There is a cure for Dirty Sock Syndrome.  You may not find long lasting results with chemicals, and UV light may not be effective.  A deposit of an antibacterial must be left on the coil, or it will eventually come back each time the coil gets wet.

 

The cure is not expensive or difficult to apply.  What you need is a very dilute solution of pine oil.  See link or search, "Dirty Sock Syndrome" in YouTube:

http://www.youtube.com/watch?v=VclGuogRPCY

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Meagan Foster posted events
10 minutes ago
Meagan Foster updated an event

EnergyLogic's RaterFest! at Black Hawk, CO

September 13, 2013 at 10am to September 15, 2013 at 12pm
Join us for one of the best home energy conferences available!  This retreat will provide…See More
13 minutes ago
Meagan Foster updated an event

Homes 401: Green Rater Training at Berthoud, CO

June 25, 2013 to June 26, 2013
This highly interactive workshop builds upon the material presented in the online course, further…See More
17 minutes ago
Meagan Foster updated an event

HERS Rater Training - Online at Online

July 1, 2013 to July 26, 2013
NEW - our great RESNET HERS Rater online training is now completely self-paced, so you can start at…See More
18 minutes ago
Meagan Foster updated an event

BPI Building Analyst Training - Online at Online

June 3, 2013 to June 28, 2013
Join the EnergyLogic Academy for our BPI BA online training - we just went to a completely open…See More
21 minutes ago
Anna Svensson posted a discussion

Looking for residential building and remodeling experts

Making sure you residential building and remodeling professionals out there are aware of the call…See More
1 hour ago
Bryce Cramer joined Leslie McDowell, BPI's group
Thumbnail

Building Performance Institute (BPI)

BPI is the nation's premier standards development, quality assurance and credentialing organization…See More
4 hours ago
Bryce Cramer replied to Mike Kandel's discussion June's Stump the Chump: What's Wrong with this Picture? in the group Building Performance Institute (BPI)
"Key is this was done in warm weather. The back wall of the room was also uninsulated, but the lower…"
4 hours ago
James Hatheway added a discussion to the group Job Board
Thumbnail

Quality Assurance Verification Specialist - Little Rock, Arkansas

CLEAResult (clearesult.com) is looking for a QA Verification professional who wants to leverage…See More
6 hours ago
Profile IconJames Hatheway and Mike Wallis joined Diane Chojnowski's group
Thumbnail

Job Board

This group is for posting jobs related to all aspects of the home performance industry including…See More
6 hours ago
Profile IconJames Hatheway, Malcolm Gray, Perry Ning and 2 more joined Home Energy Pros
6 hours ago
tedkidd commented on Mike Rogers's blog post HOMES Act introduced with Bi-Partisan Sponsorship
"% savings programs suck.  Ask the folks in CA.  When your incentive structure pits…"
8 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service