Just looking for thoughts about sealing an attic that has HVAC equipment in it by using a netting product and dense packing cellulose in the rafters. I have seen this before, although I usually see it combined with foam on the roof deck. Home is in southeastern Virginia, climate zone 4 and we traditionally do not insulate between the rafters, just the ceiling. The home in question has 85 can lights and we are looking at a cost effective way to eliminate the air flow through these bad boys.
Thanks
Tags:
Permalink Reply by Timothy DeLuca on November 4, 2011 at 9:29pm Hey Brad,
My two cents,
1. Build some "hats" around the cans. look up can light tophats on the net. You can manufacture these 'hats' with drywall or sheet metal. I think the clearance from the cans is 3". Get a good system and fabricate. That is a lot of lights.
2. Seal the hell out of every duct joint that you you can get your hands on with mastic, including plenums.
3. wrap all duct work including returns, supply and plenums with FSK fiberglass...R-19..tape well.
4. plug all penetrations, bypasses in lid from attic.
5. blow loose fill cellulose or fiberglass to a minimum R-38.
If you blow rafters with netting your thermal boundary not be aligned (insulation + air barrier). You could pack into a plastic "netting" and possibly incur moisture liability.
there are my two cents....in this economy they are probably only worth one anyway.
please let me know what you come up with, as I am learning and would love to know what your solution is.
tim
Permalink Reply by David Meiland on November 5, 2011 at 9:45am
Permalink Reply by Brad Brinke on November 5, 2011 at 1:23pm
Permalink Reply by David Meiland on November 7, 2011 at 7:52am
Permalink Reply by Rod Fox on November 10, 2011 at 9:37am At $4300, you could replace all of those lights with these:
http://www.lowes.com/pd_78215-3-70644_4294857050_4294937087_?produc...
They tend to leak very little and throw out a decent amount of light for LEDs.
And, over time, they would pay for themselves (not sure what that would be though, you do the math :-)
85 recessed lights seems a bit excessive... They might consider mudding over half of them and using task lights instead... sheesh.
Permalink Reply by Brad Brinke on November 10, 2011 at 1:49pm It was a ton of lights. Turns out the dense pack did not work. Test in 2755cfm50, test out 4500cfm50
Permalink Reply by Rod Fox on November 12, 2011 at 8:29am Me also thinks something is wrong there with your in and out tests. Baseline fluctuating from wind? That's a huge difference in readings. And with the dense pack, I would expect the test out to actually be lower rather than higher.
Permalink Reply by Bud Poll on November 12, 2011 at 8:45am Brad, did you/they change anything with those lights, are they 85 leakier holes now? And what did you do with the ventilation?
Bud
Permalink Reply by Brad Brinke on November 12, 2011 at 9:36am I am not involved in the project at this point. I did the initial audit only and not the test out. The WX contractor dense packed the rafters and did no other air sealing. The homeowner wanted to expand the home into the attic and that is one reason that they dense packed. So, the test out number is a bit misleading because they added about 1400 sq feet of "conditioned" space. I have not been back to the house since they did this and my original concern was that it was not the best option for the homeowner.
Permalink Reply by Craig Bird on December 8, 2011 at 12:56pm Sounds like this is done, but for anyone interested, there is a much more cost effective solution to air seal all of these cans. Everyone talks about building a "box" over each can light...very labor intensive and on sloped roofs, very difficult access in many situations. There is a retrofit air tight trim that may be installed from the bottom. It is cone shape and has the gasket on the top where it clips into the socket, and the rim just gets caulked to the drywall. Simple. They are only $5 a piece and take 5 minutes to install. They are for 6" cans only and will not fit in a low profile can. Here is a link www.affordablequalitylighting.com/docs/indoor/recessed/6in120vstand... . That is the only place I have ever found these and I have done probably 300 lights and never built a drywall box in the attic. Combine them with a good quality R30 fluorescent and you can have a big savings package.
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
yangxiaohua posted a blog post
Jeena Smith commented on Molly Banton's blog post Install a Pellet-Burning Fireplace Insert and Save Money
Johnny Ritzo posted a discussion
Eric Kjelshus replied to Patrick Michaelyan's discussion Hot Upper Stories
Bud Poll replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Sean Lintow Sr replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Bachi Brunato posted a discussion
Dennis Heidner replied to Patrick Michaelyan's discussion Hot Upper Stories
Bob Blanchette replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
Bob Blanchette replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??© 2013 Created by Lawrence Berkeley National Laboratory.