Just looking for thoughts about sealing an attic that has HVAC equipment in it by using a netting product and dense packing cellulose in the rafters. I have seen this before, although I usually see it combined with foam on the roof deck.  Home is in southeastern Virginia, climate zone 4 and we traditionally do not insulate between the rafters, just the ceiling. The home in question has 85 can lights and we are looking at a cost effective way to eliminate the air flow through these bad boys.

 

Thanks

Views: 2140

Reply to This

Replies to This Discussion

Hey Brad,

My two cents,

1. Build some "hats" around the cans. look up can light tophats on the net. You can manufacture these 'hats' with drywall or sheet metal. I think the clearance from the cans is 3". Get a good system and fabricate. That is a lot of lights.

 

2. Seal the hell out of every duct joint that you you can get your hands on with mastic, including plenums.

 

3. wrap all duct work including returns, supply and plenums with FSK fiberglass...R-19..tape well.

 

4. plug all penetrations, bypasses in lid from attic.

 

5. blow loose fill cellulose or fiberglass to a minimum R-38.

 

If you blow rafters with netting your thermal boundary not be aligned (insulation + air barrier). You could pack into a plastic "netting" and possibly incur moisture liability.

 

there are my two cents....in this economy they are probably only worth one anyway.

 

please let me know what you come up with, as I am learning and would love to know what your solution is.

 

tim

 

 

 

 

 

The can lights are in the attic floor, you are asking about insulating the rafters, correct?
Yes, another weatherization company in my area has done this for a client I did an audit for.  I do not see the advantage in dense packing the rafters.
What size are the rafters? With cellulose insulation you are going to need to install baffles for ventilation of the roof deck, so take that into account as you figure the max R value you can achieve that way, and compare it with what you could do with loose fill on the attic floor. But, the wild card is the mechanical equipment and all those can lights, and it may be that overall higher efficiency can be had by turning this into a conditioned attic by insulating the roof. I believe it is more common to condition an attic by spray-foaming the roof, but it probably varies regionally.

At $4300, you could replace all of those lights with these:

http://www.lowes.com/pd_78215-3-70644_4294857050_4294937087_?produc...

They tend to leak very little and throw out a decent amount of light for LEDs.

And, over time, they would pay for themselves (not sure what that would be though, you do the math :-)

85 recessed lights seems a bit excessive... They might consider mudding over half of them and using task lights instead... sheesh.

It was a ton of lights.  Turns out the dense pack did not work.  Test in 2755cfm50, test out 4500cfm50

Me thinks something is wrong there

Me also thinks something is wrong there with your in and out tests. Baseline fluctuating from wind? That's a huge difference in readings. And with the dense pack, I would expect the test out to actually be lower rather than higher.

Brad, did you/they change anything with those lights, are they 85 leakier holes now?  And what did you do with the ventilation?

 

Bud

I am not involved in the project at this point.  I did the initial audit only and not the test out.  The WX contractor dense packed the rafters and did no other air sealing.  The homeowner wanted to expand the home into the attic and that is one reason that they dense packed.  So, the test out number is a bit misleading because they added about 1400 sq feet of "conditioned" space.  I have not been back to the house since they did this and my original concern was that it was not the best option for the homeowner.

 

Sounds like this is done, but for anyone interested, there is a much more cost effective solution to air seal all of these cans. Everyone talks about building a "box" over each can light...very labor intensive and on sloped roofs, very difficult access in many situations. There is a retrofit air tight trim that may be installed from the bottom. It is cone shape and has the gasket on the top where it clips into the socket, and the rim just gets caulked to the drywall. Simple. They are only $5 a piece and take 5  minutes to install. They are for 6" cans only and will not fit in a low profile can. Here is a link www.affordablequalitylighting.com/docs/indoor/recessed/6in120vstand... . That is the only place I have ever found these and I have done probably 300 lights and never built a drywall box in the attic. Combine them with a good quality R30 fluorescent and you can have a big savings package.

Craig, thanks much for that link to the retrofit trims! I've been looking for something like that for quite a while.

RSS

Featured Forum Discussions

Too many BTU's. Too much horsepower?

Started by Steve in General Forum. Last reply by Eric Kjelshus on Saturday. 4 Replies

Stack/wind pressure and flow networks.

Started by Daniel James Grundy in Training. Last reply by Daniel James Grundy Mar 23. 5 Replies

BDT with vermiculite in hollow CMU walls?

Started by Brad Cook in General Forum. Last reply by John Nicholas Mar 23. 2 Replies

Videos

  • Add Videos
  • View All

Latest Activity

Chris Dorsi commented on Home Energy Magazine's blog post The Elephant in the Room
"This was a great session, witness the fact that we had to schedule a second showing to accommodate…"
2 hours ago
Chris Dorsi liked Home Energy Magazine's blog post The Elephant in the Room
2 hours ago
eric anderson added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Equipement still for sail (what is left from what I was selling before)

For some reason I can't reply to my previous thread.  I sold the blower door and duct blaster/flow…See More
9 hours ago
Mark Sackerson replied to angela stanzione's discussion Used Weatherization and auditing equipment for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Angela, Do you have any blower door sets left? mark"
10 hours ago
Mark Sackerson replied to Jeffrey Anthony's discussion Blower Door Kits in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Jeffrey, do you have any blower door kits left? mark msackerson@franzoso.com"
10 hours ago
Mark Sackerson joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
10 hours ago
Profile IconMark Sackerson and Matt Ward joined Home Energy Pros
10 hours ago
Quinn Korzeniecki's discussion was featured

Join BPI's New Professional Website Focus Group

Want to be part of the elite group of individuals that views the new BPI professional website…See More
10 hours ago

Home Energy Pros

Welcome to Home Energy Pros – the unique digital community by and for those who work in the home energy performance arena.

Home Energy Pros was founded by the developers of Home Energy Saver Pro (supported by the U.S. Department of Energy) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network. Please honor our Guidelines

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service