Hey all,

We recently hired a new tech that has previously done a bunch of Home Performance work on the East coast and he has turned me on to a new idea on how to insulate a basement rim joist that is enclosed with a ceiling. I wanted to see what everyone thinks about dense pack cellulose in an enclosed rim joist.

It makes sense that when you have a joist running parallel to the foundation wall that you can drill a hole in the ceiling and fill the joist cavity that is up against the rim. But for the side of the basement that has a wall perpendicular to the joists, can this work?

I have not heard about any contractors here in Portland OR using this technique, but in my mind it seems possible. I just wanted to make sure before we do the install, that it will pass program QC. Before I present it to the program, I wanted to hear some opinions from people that have experience  using this method.

So here's how I see it. If you drill the hole about 2 -3 feet away from the rim joist (towards the inside of the basement) in the basement ceiling, and blow material into the cavity, you should be able to make sure that the rim is fully insulated. I can imagine that the material would taper towards the hole, but as long as you pack it in, it would be fine.

Thanks!

Views: 821

Reply to This

Replies to This Discussion

Other approved materials are allowed only in section 4 of R302.11 (above), for around mechanical penetrations, not for draftstopping or firestopping in concealed frame cavities.

I was referring to the concealed cavities where codes have required nominal 2" lumber, and where dense-pack cellulose can meet or exceed the same standard.

 

R302.11.1 Fireblocking materials.

Except as provided in Section R302.11, Item 4, fireblocking shall consist of the following materials.

    1. Two-inch (51 mm) nominal lumber.

    2. Two thicknesses of 1-inch (25.4 mm) nominal lumber with broken lap joints.

    3. One thickness of 23/32-inch (18.3 mm) wood structural panels with joints backed by 23/32-inch (18.3 mm) wood structural panels.

    4. One thickness of 3/4-inch (19.1 mm) particleboard with joints backed by 3/4-inch (19.1 mm) particleboard.

    5. One-half-inch (12.7 mm) gypsum board.

    6. One-quarter-inch (6.4 mm) cement-based millboard.

    7. Batts or blankets of mineral wool or glass fiber or other approved materials installed in such a manner as to be securely retained in place.

    8. Cellulose insulation installed as tested for the specific application.

It would be great if someone did a video and u-tubed it.

 

Practically speaking, we seal all holes less than about 2' with foam.  1/2" OSB does the rest.  We foam gypsum common wall gaps at framing, gaps between double walls, and most items.  Average house will have 3-4 places where a piece of wood is used.  

Then you're not complying with code.

In what way are we not complying with the code?
In what way are we not complying with the code?
In what way are we not complying with the code?

See R302.11.1 above.

can you be specific - I am not seeing it

"we seal all holes less than about 2' with foam.  1/2" OSB does the rest"

How is that consistent with the very specific list of allowed fireblocking materials?

And, did you mean holes less than 2 feet? Even if you meant 2 inches, that still exceeds what you reported as the maximum span for foam: not span more than 1-5/16"

Something is screwy with the site tonight

We use OSB to cover the edges of things like soffits then seal with foam, and use extruded styrofoam to seal the tops for energy,  We use the foam to cover the backs of kneewalls, and use it to fabricate top and bottom plates as necessary,  No one says anything at 2" even though the es says 1-5/16 - as they realize what the material is.  We will do this as we seal over 2500 new houses in 2012 in, as I said, 500 jurisdictions (New Jersey has a jurisdiction every couple of miles)

We have excellent working relationships with most of the inspectors that we deal with.  Based on this experience, I have no qualms about using this same system in existing houses, even though the code does not apply for the level of work we are usually doing in retrofits.

Wow thanks for all the advice! I think this is enough info to prove that this is a valid strategy.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.

Latest Activity

Eric Kjelshus replied to Johnny Ritzo's discussion Selecting a Water Heater
"I have been using  Rheem or State or Brad/white PVC flued tank type hot water heater…"
7 hours ago
Bachi Brunato replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
"As it turns out, we have 10 Halo 99RT housings with Halo 998P Eyeball trim in the kitchen. The trim…"
10 hours ago
Bachi Brunato's discussion was featured

Boxing and Insulating Around Non-ICAT Cans

I have a client with 16) 4" halogen recessed light fixtures in the attic.I'd like to cover the cans…See More
11 hours ago
Johnny Ritzo's discussion was featured

Selecting a Water Heater

I am looking at updating the heating and water heating systems in a rental home I recently…See More
11 hours ago
George Kopf's discussion was featured

Misting Aeroseal in Pressurized Home = Amazing Air Sealing Innovation

As a training program manager for a non-profit, I am often too busy managing my program to catch…See More
11 hours ago
Tom Delconte's blog post was featured
11 hours ago
Christopher Morin's blog post was featured

Selling with Rebates: The Simple Payback

  The easiest way to show a homeowner how their investment in high-efficient equipment will help…See More
11 hours ago
Edward Foskey's blog post was featured
11 hours ago
Mike Rogers's blog post was featured

HOMES Act introduced with Bi-Partisan Sponsorship

We don't see a lot of bi-partisan bills in Congress these days. Here's one focusing on home…See More
12 hours ago
Mike Rogers posted a blog post

HOMES Act introduced with Bi-Partisan Sponsorship

We don't see a lot of bi-partisan bills in Congress these days. Here's one focusing on home…See More
15 hours ago
David Eggleton replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
"That varies, as policies are different from state to state."
15 hours ago
Orvil D Boyer replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"I have a Fluke TIR 32.  Used aproximately 10 times 1.5 yrs old.  This is the first…"
15 hours ago

© 2013   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service