Hi There Folks,


I came across this crawlspace vapor barrier installed by a BPI contractor. 

Location:  Bay Area of California- near the ocean.  

Environmental Factors:  The area receives a lot of rain, and is notorious for rising groundwater.  

Health Factors:  The customers have respiratory issues, and these were communicated to the contractor.

Material:  6mm visqueen, red tape, nails

Concerns:  The material stops several inches short of the foundation walls. Some seams are taped with red tape.  Held to ground with 8 inch nails. 

I have a lot of respect for this particular contractor, but I have grave questions about how he approaches barrier installation in crawl spaces.

He has responded that this approach is adequate for unconditioned crawlspaces.  


I would appreciate insights, and direction to standards. 

Tags: barrier, crawl, space, vapor

Views: 11409

Attachments:

Replies to This Discussion

I am not sure what the codes say in Cali but (unless I am overlooking it) there is no requirement in the 2009 IRC or IECC for "vented" crawls

For sealed crawls it is;

R408.3.1 Exposed earth is covered with a continuous Class I vapor retarder. Joints of the vapor retarder shall overlap by 6 inches (152 mm) and shall be sealed or taped. The edges of the vapor retarder shall extend at least 6 inches (152 mm) up the stem wall and shall be attached and sealed to the stem wall;

As for the groundwater issue:

R408.6 Finished grade. The finished grade of under-floor surface may be located at the bottom of the footings; however, where there is evidence that the groundwater table can rise to within 6 inches (152 mm) of the finished floor at the building perimeter or where there is evidence that the surface water does not readily drain from the building site, the grade in the under-floor space shall be as high as the outside finished grade, unless an approved drainage system is provided.

As for best practices, especially when a respiratory issue is involved - it is basically what everyone else mentioned - run up the foundation wall a minimum of 6", joints lapped lapped, and every hole, seam, etc... should be taped & sealed per manufacturers directions

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Ed Minch commented on Tom White's video
Thumbnail

Measured Home Performance: Assessment with a Infrared Camera

"I find it best to scan one time before the Blower Door is used to check for insulation and…"
15 hours ago
Profile IconLarry Kinney and teplie_poly joined Home Energy Pros
18 hours ago
Dan Antonioli replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"Okay, a couple of things. The 1.0 kW per square meter reference is only under the most ideal lab…"
yesterday
Hans Joachim Preiss replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"Dan, Let me attempt to compare apples with apples: My solar thermal system is located in…"
yesterday
Dan Antonioli replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"Hi Hans, I don't know where you're located but where I am a 2.5 kw pv system costs closer…"
yesterday
Hans Joachim Preiss replied to Dan Antonioli's discussion Net Zero Energy Hot Water
"I use the combination of solar PV and heatpump water heaters in the vast majority of net-zero…"
yesterday
Amber Vignieri posted a blog post
yesterday
William Zwack added a discussion to the group Job Board
Thumbnail

Residental Energy Specialist: Washington, DC (or possibly telework)

Position Summary: CSRA Incorporated is searching for a Sr. Residential Building Energy Efficiency…See More
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service