Convert BTU/hr in a Manual J to actual fuel usages

I cannot find any conversion table that translates the BTU/hr heat loss in a Manual J report to the amount of fuel required to heat the building to the design temperature.  In this case I'm using propane and I have calculated the 92,000 BTU/gal using the actual BTU/Hr X Degree Days and end up requiring over 30K gallons of propane for a heating system.  This cannot be correct.  Any guidance would be greatly appreciated.

Views: 1389

Reply to This

Replies to This Discussion

Morgan,
From the perspective of the energy auditor, I don’t agree with that statement.
“Actual fuel and electrical usage" is anecdotal at best”
Unless you change something, the best predictor of future energy usage is past energy usage. Now if you are going to use fuel and electrical usage, you have to have a minimum of one years data, you need to know the heating degree days and cooling degree days over that exact period, (Or binned temp data) And you need to measure the combustion efficiency of the heat source.
I will try to dig up a paper I have on the subject- the punch line was that identically built and situated houses had a 2 fold difference in energy usage based on occupant behavior. Both have identical manual J heat loss, but use very different amounts of energy. If you are trying to make rational choices based on payback, you have to know the actual usage- which is related to occupant behavior.
An example- If you are going to recommend a solar pool heater to save money- you better make sure they are actually using their existing electric resistance pool heater. Likewise recommending a high efficiency AC replacement makes no sense if the homeowner hates AC. A customer who keeps his house at 80°F all winter, uses a lot more energy than someone who keeps the thermostat at 55. Some efficiency measures that have a reasonable payback in one situation will not in the other.
The customer generally does not care about manual J- design temps, etc. They want to know what it is going to cost to heat and cool their house, and what is the best way to do it. Manual J is one tool in the box to help do this.
Cheers,
Eric

RSS

Videos

  • Add Videos
  • View All

Twitter

Latest Activity

Allan G Hurst joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
50 minutes ago
Michael Dunseith commented on Michael Dunseith's photo
Thumbnail

Proof is possible Tour - Corbett Lungsford

"Oldest House in America to have a Blower Door Test  - Cira 1652"
1 hour ago
Michael Dunseith posted a photo

Proof is Possible tour, with BPI

Corbett and Grace , Proof is Possible Tour hosted by ZERO DRAFT, Ithica, NY. BPI Crew
2 hours ago
Sandra K. Adomatis, SRA posted photos
2 hours ago
Sean Lintow Sr replied to Larry Nissman's discussion Foam insulation on attic floor
"The insulation job is quite simply a freaking eyesore & mess - with that it shouldn't be…"
9 hours ago
Sean Lintow Sr replied to Melissa Baldridge's discussion IECC 2012 & 2015 Compliance & HRVs
"commercial is 67% efficiency & 2.8 cfm per watt for residential as I recall on 2015 which…"
10 hours ago
Simon added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Advice needed please

I'm looking to build my own blower unit for use with the minneapolis system.Please could anyone…See More
13 hours ago
Simon joined Kim Tanner's group
Thumbnail

TEC

Discussion group for The Energy ConservatoryHave a question about residential or big building air…See More
13 hours ago

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service