Convert BTU/hr in a Manual J to actual fuel usages

I cannot find any conversion table that translates the BTU/hr heat loss in a Manual J report to the amount of fuel required to heat the building to the design temperature.  In this case I'm using propane and I have calculated the 92,000 BTU/gal using the actual BTU/Hr X Degree Days and end up requiring over 30K gallons of propane for a heating system.  This cannot be correct.  Any guidance would be greatly appreciated.

Views: 1044

Reply to This

Replies to This Discussion

Morgan,
From the perspective of the energy auditor, I don’t agree with that statement.
“Actual fuel and electrical usage" is anecdotal at best”
Unless you change something, the best predictor of future energy usage is past energy usage. Now if you are going to use fuel and electrical usage, you have to have a minimum of one years data, you need to know the heating degree days and cooling degree days over that exact period, (Or binned temp data) And you need to measure the combustion efficiency of the heat source.
I will try to dig up a paper I have on the subject- the punch line was that identically built and situated houses had a 2 fold difference in energy usage based on occupant behavior. Both have identical manual J heat loss, but use very different amounts of energy. If you are trying to make rational choices based on payback, you have to know the actual usage- which is related to occupant behavior.
An example- If you are going to recommend a solar pool heater to save money- you better make sure they are actually using their existing electric resistance pool heater. Likewise recommending a high efficiency AC replacement makes no sense if the homeowner hates AC. A customer who keeps his house at 80°F all winter, uses a lot more energy than someone who keeps the thermostat at 55. Some efficiency measures that have a reasonable payback in one situation will not in the other.
The customer generally does not care about manual J- design temps, etc. They want to know what it is going to cost to heat and cool their house, and what is the best way to do it. Manual J is one tool in the box to help do this.
Cheers,
Eric

RSS

Photos

Loading…
  • Add Photos
  • View All

Latest Activity

JC NATALE posted photos
14 hours ago
Mike Burton replied to Amos Dunham's discussion ISO blower door or other equipment
"Are you still looking?  I have rarely used Minneapolis Blower Door and Duct Blaster Systems I…"
21 hours ago
Jonny Fisher posted a discussion

Used energy equipment for sale (blower door, duct blaster

I've got some used equipment that I need to sell. Let me know if you are interested in any of the…See More
yesterday
Joe Quiroz Jr. liked Don Hynek's discussion Superinsulation retrofit is Complete!
yesterday
Mick Lane replied to Rob Buchanan's discussion High-use headscratcher
"The geothermal heat pump is the most likely culprit.  The heat pump doesn't make heat it…"
yesterday
Mick Lane is now a member of Home Energy Pros
yesterday
Empower Efficiency added 2 discussions to the group Job Board
yesterday
Tom White's video was featured

A net-zero builders formula for insulating a super energy efficient home

Here is Peter Amerongen's formula for insulating a super energy efficient home.
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service