Convert BTU/hr in a Manual J to actual fuel usages

I cannot find any conversion table that translates the BTU/hr heat loss in a Manual J report to the amount of fuel required to heat the building to the design temperature.  In this case I'm using propane and I have calculated the 92,000 BTU/gal using the actual BTU/Hr X Degree Days and end up requiring over 30K gallons of propane for a heating system.  This cannot be correct.  Any guidance would be greatly appreciated.

Views: 940

Reply to This

Replies to This Discussion

From the perspective of the energy auditor, I don’t agree with that statement.
“Actual fuel and electrical usage" is anecdotal at best”
Unless you change something, the best predictor of future energy usage is past energy usage. Now if you are going to use fuel and electrical usage, you have to have a minimum of one years data, you need to know the heating degree days and cooling degree days over that exact period, (Or binned temp data) And you need to measure the combustion efficiency of the heat source.
I will try to dig up a paper I have on the subject- the punch line was that identically built and situated houses had a 2 fold difference in energy usage based on occupant behavior. Both have identical manual J heat loss, but use very different amounts of energy. If you are trying to make rational choices based on payback, you have to know the actual usage- which is related to occupant behavior.
An example- If you are going to recommend a solar pool heater to save money- you better make sure they are actually using their existing electric resistance pool heater. Likewise recommending a high efficiency AC replacement makes no sense if the homeowner hates AC. A customer who keeps his house at 80°F all winter, uses a lot more energy than someone who keeps the thermostat at 55. Some efficiency measures that have a reasonable payback in one situation will not in the other.
The customer generally does not care about manual J- design temps, etc. They want to know what it is going to cost to heat and cool their house, and what is the best way to do it. Manual J is one tool in the box to help do this.


Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Eric Kjelshus commented on Chris Laumer-Giddens's blog post Sparky Doubled the Air Leakage in this Home!
"What if after the building is sealed and tested.   The trades man would have to reseal all…"
2 hours ago
Colin Genge posted events
4 hours ago
David Downard replied to David Downard's discussion Blower Door for Sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Price is $1700. "
5 hours ago
David Downard added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase

Blower Door for Sale

MINNEAPOLIS BLOWER DOOR Complete system with DG700 Like new, its been used about 6…See More
5 hours ago
David Downard joined allen p tanner's group

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
6 hours ago
Profile IconEdward Burns, Nina Baird, Cindy Hasenjager and 2 more joined Home Energy Pros
7 hours ago
John Proctor commented on Chris Laumer-Giddens's blog post Sparky Doubled the Air Leakage in this Home!
"Nice job on the house -- bad job on Sparky's high tech hole."
12 hours ago
Jeffrey Gephart shared Chris Laumer-Giddens's blog post on Facebook
12 hours ago

© 2015   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service