I'm opening a separate discussion under a new thread as this one: http://homeenergypros.lbl.gov/forum/topics/locating-the-neutral-pre...  was getting overly congested and this topic deserves its own space.

Homes need to be tight to be energy efficient, but then comes the question of how to provide the necessary fresh air that we and our houses need.  Robert Riversong (above thread and several others) has posted some great information on passive vents and the economics of simple exhaust venting that I think offers a good alternative to expensive H/ERV installations.  However, I feel there needs to be a better understanding of just how static venting works.

Most of us in the energy business have read about, used, or advised on using some form of passive venting for replacement air that involves a form of air trap.  Robert posted his version and mentioned the "Saskatoon Loop" as methods of restricting the unwanted air flow while still providing a path for the desired air flow.  I have looked at the "duct ending in a bucket" and the "loop up at the bottom" cold air traps in the past and concluded they are not exactly what they appear to be.  Essentially they modify the height and resistance of the flow path, but otherwise do not act as an air block.

 

Since the explanation of the above can be long, I have put together a simple statement that I feel conveys the guidance we need when designing and installing passive vents, at least some of the guidance.

"For any fresh air vent duct passing from inside a home to the outside (under natural pressures), the effective pressure from end to end of that duct is the stack effect pressure (wrto) at the height of:

1.  the outside opening when the duct is filled with inside temperature air.

2.  the inside opening when the duct is filled with outside temperature air.

3.  the penetration through the envelope when outside is filled with outside air and the inside is filled with inside air."

I haven't reviewed this for summer conditions, but I believe the statement will hold.

When any kind of winding path is filled with the same air as is around it, it might as well be a straight shot, if the structure allows.  Alternatively, if a straight shot is not possible, a winding path will not alter the effective air flow, other than adding a bit more resistance.

The bottom line is, passive venting should follow and use the internal pressures within a home, positive, negative, and that somewhat elusive NPP.

John is very good at challenging or explaining many of my statement and he creates great artwork, so I'll post this and see what we get for input from all.

Bud

Views: 4976

Reply to This

Replies to This Discussion

Here's a cathedral ceiling over one of the ceiling light fixtures. This was a "vented" roof with fiberglass batts and no vent channel.

Attachments:

Julius Sumner Miller was a student of Einstein and a "fellow" student and a close friend.

 

.......

Robert said: "At elevation of 1000 ft above sea level, the change in atmospheric pressure is 3.67 Pa/Ft or 0.306 Pa/inch. At sea level, it's 3.81 Pa/Ft or 0.318 Pa/inch."

I think Straube's formula is based at sea level

Robert, what is the temperature for your examples?

For the sea level example...

the reciprocal of 0.318 Pa /inch will return a Vertical Isobar spacing of 3.14 inches

and 0.306 Pa/inch (elevation 1,000 ft)  translates to a "Spacing" of 3.27 inches

Robert said: "the most foolish way to duct an exhaust fan is straight up through the roof"

It seems to me that in a heating climate (or during the heating season) ...

It would be desireable to have the "passive NPP"  high

This would make the house more "negative" and would reduce (or eliminate) positive pressure near the top of the enclosure.

Therefore terminating exhaust stacks "HIGH" might not be so "foolish".

It is not-so-foolish to terminate fireplace or woodstove chimneys (stacks) high rather than low.

It is not-so-foolish to terminate a sanitary sewer vent HIGH...

even if it does require going thru the roof.

Of course it would be better to have fewer penetrations thru the ceiling and  roof...and condensation should be considered and drained properly.

If it makes sense to run a sewer vent thru the roof...why not an exhaust stack?

You nailed the reason - condensation

The next reason is dampers & wind

In some cases going through the roof is the only option, but for most of us we will look first for the nearest gable end

How about soffits - nope as you will be pulling it back into the house

By the way, the more negative a house, the more cold dry or warm moist air you are pulling in - while that maybe good during some parts of the year in certain parts of the country it's not the best thing to do

I did say "During the Heating Season"

We run a chimney through the roof (and minimum 3' above, and 2' above anything within 10' horizontally) both to maximize the updraft, to get smoke away from the house (including from staining the roof) and to prevent downdrafts from wind passing over obstacles such as roof peaks).

We run a plumbing vent through the roof to also maximize stack effect draft and to get the stink away from all fenestration. Similarly with a a radon vent.

Maximizing static draft pressure and velocity in an exhaust fan that's not supposed to be moving air when it's turned off is generally not a wise option. If the exterior backdraft damper were to get stuck open, the house would have a passive chimney moving large quantities of air.

If it's connected to a bath fan that's used on low speed 24/7 as a whole-house ventilator, then it's probably fine.

On a side note...we have run out of chances to  "Reply to This" again

So I will just "reply" wherever I can

I didn't see any formula for absolute air pressure in Straube's article.

The formula I'm using is local barometric pressure is sea level pressure (assuming 14.696 psi) / 2^(h/18,400), with h being the local elevation above sea level. The formula is independent of temperature.

Isn't the "14.696" assumption based on a certain temperature ?

At least the sidebar in John Straube's latest article is a little more "Bud Friendly"

http://www.buildingscience.com/documents/published-articles/pa-air-...

Yah, but buildings don't grow - they get built.

I'm not confident that airs tendency to mix doesn't overcome this "house natural stratification" theory.

In fact, I'm thinking that you have to have a fair delta to overcome mixing. Anybody experiencing wood stove heat in a cabin knows that big delta will stratify, but low gentile heat tends to be uniform.

I've been in homes where unintentionally conditioned attics end up sauna temps, hottest area in the home, from downstairs wood stoves. When the same home is heated with the oil furnace the attic temps stay below 60, coldest room in the home.

The implication of stratification w/o rt heating source temperature seems to miss a really big slice of the stack concept, and lead to some poor assumptions for many situations. In fact, I'd propose lumping stack and stratification together is confusing apples and oranges.

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Tom White posted videos
5 hours ago
Maria Lacey replied to Linda Wigington's discussion Low-cost electricity monitoring: Accuracy & Applications in the group 1000 Home Challenge
"I attempted to use an AZTech device. I have used the Watt Stopper, Watts Up Pro, Kill-A-Watt…"
9 hours ago
Maria Lacey joined David Eggleton's group
Thumbnail

1000 Home Challenge

Linda Wigington distinguished between deep retrofits & deep energy reductions, thus expanding…See More
9 hours ago
Profile IconCynthia Sandherr, James Skeldon, Mathew Castel and 3 more joined Home Energy Pros
11 hours ago
Andy Li replied to David Parker's discussion Energy auditor equipment for sale- blower door, duct tester,combustion analyzer in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Is Minneapolis Duct Blaster still available? send some photos and how much do you ask for? my…"
14 hours ago
Andy Li joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
14 hours ago
Hal Skinner replied to Richard Beyer's discussion What's your opinion on the best insulation option for your GREEN attic space?
"Mornin Richard, Maybe 'Options' might be more appropriate here?  We take the path…"
16 hours ago
Richard Beyer posted a discussion
17 hours ago

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service