I'm opening a separate discussion under a new thread as this one: http://homeenergypros.lbl.gov/forum/topics/locating-the-neutral-pre... was getting overly congested and this topic deserves its own space.
Homes need to be tight to be energy efficient, but then comes the question of how to provide the necessary fresh air that we and our houses need. Robert Riversong (above thread and several others) has posted some great information on passive vents and the economics of simple exhaust venting that I think offers a good alternative to expensive H/ERV installations. However, I feel there needs to be a better understanding of just how static venting works.
Most of us in the energy business have read about, used, or advised on using some form of passive venting for replacement air that involves a form of air trap. Robert posted his version and mentioned the "Saskatoon Loop" as methods of restricting the unwanted air flow while still providing a path for the desired air flow. I have looked at the "duct ending in a bucket" and the "loop up at the bottom" cold air traps in the past and concluded they are not exactly what they appear to be. Essentially they modify the height and resistance of the flow path, but otherwise do not act as an air block.
Since the explanation of the above can be long, I have put together a simple statement that I feel conveys the guidance we need when designing and installing passive vents, at least some of the guidance.
"For any fresh air vent duct passing from inside a home to the outside (under natural pressures), the effective pressure from end to end of that duct is the stack effect pressure (wrto) at the height of:
1. the outside opening when the duct is filled with inside temperature air.
2. the inside opening when the duct is filled with outside temperature air.
3. the penetration through the envelope when outside is filled with outside air and the inside is filled with inside air."
I haven't reviewed this for summer conditions, but I believe the statement will hold.
When any kind of winding path is filled with the same air as is around it, it might as well be a straight shot, if the structure allows. Alternatively, if a straight shot is not possible, a winding path will not alter the effective air flow, other than adding a bit more resistance.
The bottom line is, passive venting should follow and use the internal pressures within a home, positive, negative, and that somewhat elusive NPP.
John is very good at challenging or explaining many of my statement and he creates great artwork, so I'll post this and see what we get for input from all.
Bud
Tags:
Permalink Reply by Robert Riversong on September 22, 2012 at 1:35pm Here's a cathedral ceiling over one of the ceiling light fixtures. This was a "vented" roof with fiberglass batts and no vent channel.
Permalink Reply by John Brooks on September 22, 2012 at 2:11pm Julius Sumner Miller was a student of Einstein and a "fellow" student and a close friend.
.......
Robert said: "At elevation of 1000 ft above sea level, the change in atmospheric pressure is 3.67 Pa/Ft or 0.306 Pa/inch. At sea level, it's 3.81 Pa/Ft or 0.318 Pa/inch."
I think Straube's formula is based at sea level
Robert, what is the temperature for your examples?
For the sea level example...
the reciprocal of 0.318 Pa /inch will return a Vertical Isobar spacing of 3.14 inches
and 0.306 Pa/inch (elevation 1,000 ft) translates to a "Spacing" of 3.27 inches
Permalink Reply by John Brooks on September 27, 2012 at 5:35am Robert said: "the most foolish way to duct an exhaust fan is straight up through the roof"
It seems to me that in a heating climate (or during the heating season) ...
It would be desireable to have the "passive NPP" high
This would make the house more "negative" and would reduce (or eliminate) positive pressure near the top of the enclosure.
Therefore terminating exhaust stacks "HIGH" might not be so "foolish".
It is not-so-foolish to terminate fireplace or woodstove chimneys (stacks) high rather than low.
It is not-so-foolish to terminate a sanitary sewer vent HIGH...
even if it does require going thru the roof.
Of course it would be better to have fewer penetrations thru the ceiling and roof...and condensation should be considered and drained properly.
If it makes sense to run a sewer vent thru the roof...why not an exhaust stack?
Permalink Reply by Sean Lintow Sr on September 27, 2012 at 6:41am You nailed the reason - condensation
The next reason is dampers & wind
In some cases going through the roof is the only option, but for most of us we will look first for the nearest gable end
How about soffits - nope as you will be pulling it back into the house
By the way, the more negative a house, the more cold dry or warm moist air you are pulling in - while that maybe good during some parts of the year in certain parts of the country it's not the best thing to do
Permalink Reply by John Brooks on September 27, 2012 at 7:51am I did say "During the Heating Season"
Permalink Reply by Robert Riversong on September 27, 2012 at 9:22am We run a chimney through the roof (and minimum 3' above, and 2' above anything within 10' horizontally) both to maximize the updraft, to get smoke away from the house (including from staining the roof) and to prevent downdrafts from wind passing over obstacles such as roof peaks).
We run a plumbing vent through the roof to also maximize stack effect draft and to get the stink away from all fenestration. Similarly with a a radon vent.
Maximizing static draft pressure and velocity in an exhaust fan that's not supposed to be moving air when it's turned off is generally not a wise option. If the exterior backdraft damper were to get stuck open, the house would have a passive chimney moving large quantities of air.
If it's connected to a bath fan that's used on low speed 24/7 as a whole-house ventilator, then it's probably fine.
Permalink Reply by John Brooks on September 22, 2012 at 2:19pm On a side note...we have run out of chances to "Reply to This" again
So I will just "reply" wherever I can
Permalink Reply by Robert Riversong on September 22, 2012 at 2:40pm I didn't see any formula for absolute air pressure in Straube's article.
The formula I'm using is local barometric pressure is sea level pressure (assuming 14.696 psi) / 2^(h/18,400), with h being the local elevation above sea level. The formula is independent of temperature.
Permalink Reply by John Brooks on September 22, 2012 at 2:48pm Isn't the "14.696" assumption based on a certain temperature ?
Permalink Reply by John Brooks on September 22, 2012 at 2:52pm At least the sidebar in John Straube's latest article is a little more "Bud Friendly"
http://www.buildingscience.com/documents/published-articles/pa-air-...
Permalink Reply by Robert Riversong on September 22, 2012 at 3:25pm Yah, but buildings don't grow - they get built.
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Ed Minch replied to Patrick Michaelyan's discussion Hot Upper Stories
Craig Savage commented on Craig Savage's video
Tom Delconte commented on Craig Savage's video
Ben Jacobs replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??
Craig Savage commented on Craig Savage's video
Tom Delconte commented on Craig Savage's video
Cory Chovanec replied to Bachi Brunato's discussion Boxing and Insulating Around Non-ICAT Cans
Jon Haehnel replied to Jose Macho's discussion Why Are Energy-Saving Home Inprovements Down??