I have a confused 8,000 square foot commercial office space. It has a dropped ceiling suspended from wooden truss system. It has a vented attic with pitched shingle roof. We are in climate Zone 5 at 7,000ft elevation with around 7,000 HDD.Around $9,000 in gas per year.
There is no sheathing top or bottom of trusses. The insulation has been stapled in floating style and we all know how that goes. Pretty much no air barrier and insulation dropping all over the place. There are multiple furnaces(I think 4 or 5) all installed on top of trusses with grilles incorporated into the dropped ceiling. Ideally we would like to go with an unvented roof assembly with foam on the underside of the deck. My concern is all the non-sealed combustion appliances and corresponding combustion air requirements. We feel that not only is there no space to move the furnaces, it most likely would not be cost effective. We considered various insulation strategies on the existing attic floor, but seems to patchwork to me. Two options left were foam the underside of roof and either A) buy all condensing furnaces, or B) create a box around each furnace with combustion air running to the outside.
I would like comments on Option B, as I do not think new condensing units are going to fit in the budget.
Craig
Flagstaff, AZ
Tags:
Permalink Reply by Sean Lintow Sr on May 31, 2011 at 3:45am You mean the furnaces are installed under the trusses,not above them right? My first thought is those are commercial vent-less units & thank goodness you are in Flagstaff.
I am not sure I would be worried about combustion air running to the units, but rather changing air out for the occupants with an HRV which would provide needed combustion air. Now if they are vented units, you have other issues
Permalink Reply by Craig Bird on May 31, 2011 at 9:39am The furnaces are installed above the bottom chord of the trusses - so in the attic space. These are normal 80% non-condensing, forced air, vented furnaces.
I didn't think about using conditioned volume for combustion air requirements. We will have to run the calcs and see if there is enough volume. If needed we can have pass thru vents from the living space to conditioned attic and introducing fresh air with an HRV.
We're you thinking of code issues for vented furnaces? That is what I was concerned about with having non-sealed combustion ap.0pliances all in conditioned space once the thermal barrier is moved to the roof deck and venting removed.
It seems to me, barring any specific code issues, you can pull combustion air from conditioned space if the volume is sufficient. It just makes me nervous, but barring replacing all the hvac, it may be the only solution.
Any other ideas or comments?
Permalink Reply by Isaac Savage on June 2, 2011 at 8:43am I think option B makes great sense. The air injector fans shouldn't run more than a few hundred dollars each. Much cheaper upfront cost than replacing furnaces.
However, you should definitely map out a payback on the furnace upgrade option. With $9k in heating costs (will be less, of course, after the insulation retrofit), the payback may seem appealing to the building owner. It may also be possible to completely drop one of the systems, and replace it with a zone, avoiding one of the system upgrades all together. In general, I think option B is certainly a reasonable approach.
Permalink Reply by Craig Bird on June 2, 2011 at 9:07am
Permalink Reply by Isaac Savage on June 2, 2011 at 11:05am Field Controls has a "fan in a can" product that can be wired to the furnace. A pressure switch must be proved before the furnace will fire. Could be used in lieu of hi/low if only one envelope penetration was desired. This also works well for furnaces in crawlspaces that require "sealing" but don't have the budget for a furnace upgrade.
There's a statement in the code that allows combustion air grilles from the conditioned space of a building (larger sqin/btu ratio than to outside, if I recall correctly). It may be worth investigating whether or not you could deliver this combustion air from the conditioned space. Obviously not ideal to exhaust conditioned air. But, would be more affordable upfront, as you wouldn't need to box-in around each unit. This may be an issue related to thermal barrier coatings on foam. But, you'll be facing that anyhow if there is only a dropped-tile ceiling separating the attic from the office space.
Permalink Reply by Craig Bird on June 2, 2011 at 11:23am
Permalink Reply by Isaac Savage on June 2, 2011 at 2:58pm
Permalink Reply by Isaac Savage on June 2, 2011 at 3:05pm What's the budget?
If you drop the bill to $2000, will they let you have the $7000?
I'd guess that'll cover cost of spray foam the space and allow for 2 hybrid heat systems. Can't image you couldn't manage that space with two 100mbtu/5 ton hybrids. I did this with a similar space. Building owner is now unhappy because he spends more on energy for his 2200 sf house.
I wouldn't start doing analysis without some participation from the client. They need to give you some $ for design and analysis work.
Also, you have the PAIN - $9000 a year. You need MONEY, what they are willing to allocate to this project. Then you need DECISION, commitment to move forward with the work if it solves pain for less than or equal to money.
Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy, under the American Recovery and Reinvestment Act) and brought to you in partnership with Home Energy magazine.
Tom Delconte commented on Tom Delconte's blog post Lykans $29, Vampires $0 !
Judi Lyall joined allen p tanner's group
Judi Lyall replied to David Starrett's discussion I am looking for a good IR camera in the group Energy Auditing Equipment for Sale, Trade or to Purchase
Tom Maides commented on Jim Gunshinan's blog post The Universe Is Made of Stories
Laurie DiDonato posted an event
Tom Delconte posted a blog post
Jim Gunshinan commented on Jim Gunshinan's blog post The Universe Is Made of Stories
Edward Foskey commented on Jim Gunshinan's blog post The Universe Is Made of Stories© 2013 Created by Lawrence Berkeley National Laboratory.