Does anyone have an inexpensive method to "clock" a combustion furnace to estimate BTU output similar to Natural gas, but for propane, kerosene, or oil? I work in the Weatherization Assistance Program and often the nameplates are missing from existing furnaces. Without BTU output it is tough to do an accurate computer model of the home. Thanks!

Views: 305

Reply to This

Replies to This Discussion

For natural gas, run only the furnace for a given time, mark the dial difference on the meter and multiply the gas used by the heat multiplier for your gas supplier. This will give you a ball park estimate.

For propane, you can look at the burner orfice size.  there are charts that give the btu rating for the orfice size. then multiply by the numbers of burners.  will give approx output.  LP orfices are usually slightly smaller btu than Nat. ones.

Follow the link

http://www.joppaglass.com/burner/lowp_chrt.html

Thanks for all the comments plus the link. I think based on them I have enough information forfollks in the field to get close enough to the correct size furnaces for modeling the houses thanks all.

Ernst,

You mentioned oil, but the replies seem to all be for gas, unless I didn't read correctly.  For oil you can look for the nozzle size.  Sometimes it is notes on the service tag or in the manual, if still around.  In some cases you might be able to call the service company as they may have that noted for their HDD fuel calculations or service work. 

Bud

Thanks, I did find that out. In weatherization we deal with some really old furnaces, so sometimes getting a ballpark furnace size is the best we can do but the nozzle sizes for oil seem to be pretty specific.

For the oil burning furnaces, you should check the pump pressure. Older furnaces run at 100psi, and newer ones run at 140psi. When the pressure is higher, you need to cross reference the nozzle size to get proper Btu ratings. Plenty of reference materials are located on the Beckett website.

For propane figure about 20-25k per burner rated input. Varies some form unit to unit but 22k is typical.

Thanks Bob, we'll go woithout. It should be close enough without having to factor in pressures and temps, etc and  complicate the process too much.

I'll apologies in advance for drifting here a bit, but your "close enough" comment threw me back to my beginning in this business (05) when I questioned every number we use.  The idea of pinning down the performance of a home to the last tiny detail is laughable when we consider just how many of our inputs are "close enough" numbers.  From insulation values, HDD, window performance, and air leakage (to name a few), we guess and we guess and then carry our calculations out to two decimal places (or the computer does).  I think my tape measure is the only real source of accurate information :).

I enjoyed the comment

Bud

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Kim Tanner updated an event

Beyond Residential Testing at The Energy Conservatory

May 14, 2014 to May 16, 2014
The Energy Conservatory (TEC) is hosting a Beyond Residential Testing event. In addition we are…See More
10 minutes ago
Casey Gesell posted a video

Super Attic - Attic Insulation System

http://www.drenergysaver.com | 1-888-225-6260 The new Super Attic: Advanced Conversion System -- converts your attic from a vented attic into an unvented at...
33 minutes ago

Casey Gesell just added their location.
(via Member Map)

2 hours ago
H.O. Electric posted a video

H.O. Services, Generator, Electrical, Plumbing, Heating, Cooling, Belmont, Lexington, Arlington, MA

H.O. Services is your residential Electric-Plumbing-Heating-Cooling Specialist. We are an electrical contracting company providing homeowners the best Electr...
2 hours ago
Jim Gunshinan's blog post was featured
2 hours ago
Profile IconMichael and michael coleman joined Home Energy Pros
2 hours ago
Luis Hernandez posted a discussion

Air Source Heat pump or mini-split efficiency

Greetings everyone!    I have a technical questions I hope I could get some feedback! I understood…See More
4 hours ago
Jim Gunshinan posted blog posts
22 hours ago
H.O. Electric posted a photo

about us-team

H.O. Services is your residential Electric-Plumbing-Heating-Cooling Specialist. We are an…
22 hours ago
H.O. Electric added a discussion to the group News & Announcements
Thumbnail

Stay Cool With Easy To Install Ductless AC System!

Stay Cool With Easy To Install Ductless AC System!   Save $300.00 Off A New AC System For A Limited…See More
22 hours ago
Richard Wells commented on Diane Chojnowski's group Facebook Pages
"Three thousand home energy efficiency audits, and nearly a thousand retrofits in four short…"
yesterday
Richard Wells joined Diane Chojnowski's group
Thumbnail

Facebook Pages

Does your company or organization have a Facebook Page?This group is for pros who have facebook…See More
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service