Does anyone have an inexpensive method to "clock" a combustion furnace to estimate BTU output similar to Natural gas, but for propane, kerosene, or oil? I work in the Weatherization Assistance Program and often the nameplates are missing from existing furnaces. Without BTU output it is tough to do an accurate computer model of the home. Thanks!

Views: 306

Reply to This

Replies to This Discussion

For natural gas, run only the furnace for a given time, mark the dial difference on the meter and multiply the gas used by the heat multiplier for your gas supplier. This will give you a ball park estimate.

For propane, you can look at the burner orfice size.  there are charts that give the btu rating for the orfice size. then multiply by the numbers of burners.  will give approx output.  LP orfices are usually slightly smaller btu than Nat. ones.

Follow the link

http://www.joppaglass.com/burner/lowp_chrt.html

Thanks for all the comments plus the link. I think based on them I have enough information forfollks in the field to get close enough to the correct size furnaces for modeling the houses thanks all.

Ernst,

You mentioned oil, but the replies seem to all be for gas, unless I didn't read correctly.  For oil you can look for the nozzle size.  Sometimes it is notes on the service tag or in the manual, if still around.  In some cases you might be able to call the service company as they may have that noted for their HDD fuel calculations or service work. 

Bud

Thanks, I did find that out. In weatherization we deal with some really old furnaces, so sometimes getting a ballpark furnace size is the best we can do but the nozzle sizes for oil seem to be pretty specific.

For the oil burning furnaces, you should check the pump pressure. Older furnaces run at 100psi, and newer ones run at 140psi. When the pressure is higher, you need to cross reference the nozzle size to get proper Btu ratings. Plenty of reference materials are located on the Beckett website.

For propane figure about 20-25k per burner rated input. Varies some form unit to unit but 22k is typical.

Thanks Bob, we'll go woithout. It should be close enough without having to factor in pressures and temps, etc and  complicate the process too much.

I'll apologies in advance for drifting here a bit, but your "close enough" comment threw me back to my beginning in this business (05) when I questioned every number we use.  The idea of pinning down the performance of a home to the last tiny detail is laughable when we consider just how many of our inputs are "close enough" numbers.  From insulation values, HDD, window performance, and air leakage (to name a few), we guess and we guess and then carry our calculations out to two decimal places (or the computer does).  I think my tape measure is the only real source of accurate information :).

I enjoyed the comment

Bud

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Everblue posted events
28 seconds ago
Mst. Fatema Aktar is now a member of Home Energy Pros
8 hours ago
Robert Leone added a discussion to the group Energy Auditing Equipment for Sale, Trade or to Purchase
Thumbnail

Blower Door Package for Sale

Hi,I am selling my blower door with extras as a package or individually. These items are used but…See More
15 hours ago
Profile IconRobert Leone and Richard Vito joined allen p tanner's group
Thumbnail

Energy Auditing Equipment for Sale, Trade or to Purchase

Discuss the pros and cons of the equipment you are interested in prior to purchase. Post equipment…See More
15 hours ago
Richard Vito joined Sean Lintow Sr's group
Thumbnail

Best Practices (Residential)

Best Building, Retrofitting, or even Auditing Practices - what are they, what should change, what…See More
23 hours ago
Richard Vito joined James Sayers's group
Thumbnail

Marketing Energy Efficiency

Sharing ideas, tools and examples of promoting energy efficiency to consumersSee More
23 hours ago
Richard Vito joined Allison A. Bailes III's group
Thumbnail

HVAC

HVAC design, Manuals J, S, T, & D, Duct leakage, Air flow, ENERGY STAR new home requirements,…See More
23 hours ago
Richard Vito joined Kyle Brown's group
Thumbnail

Wrightsoft - Manual J / Manual D

If you use Wrightsoft to calculate loads or design ducts, you likely have questions.  Get answers…See More
23 hours ago
Jim Gunshinan commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"I had a revelation while attending Bruce Manclark's session of duct leak testing at the Energy…"
yesterday
George J. Nesbitt commented on Jim Gunshinan's blog post Energy Upgrade California—Up Close and Personal
"Blower Door; the 2007 test was a depressurization test, and the 2014 a pressurization test, which…"
yesterday
George J. Nesbitt replied to Kaushal Bharath Raju's discussion Affordability & Deep Energy Upgrade/Passive House Retrofit in Berkeley, California.
"Plan, plan, plan, plan. The 1st step to is to understand the house, how it's built, the…"
yesterday
George J. Nesbitt posted an event

High Performance Windows - A Panel of Experts at Pyramid Alehouse`

April 26, 2014 from 3pm to 5pm
Join a lively panel discussion on high performance windows. We'll cover some basics, as well as…See More
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service