Does anyone have an inexpensive method to "clock" a combustion furnace to estimate BTU output similar to Natural gas, but for propane, kerosene, or oil? I work in the Weatherization Assistance Program and often the nameplates are missing from existing furnaces. Without BTU output it is tough to do an accurate computer model of the home. Thanks!

Views: 322

Reply to This

Replies to This Discussion

For natural gas, run only the furnace for a given time, mark the dial difference on the meter and multiply the gas used by the heat multiplier for your gas supplier. This will give you a ball park estimate.

For propane, you can look at the burner orfice size.  there are charts that give the btu rating for the orfice size. then multiply by the numbers of burners.  will give approx output.  LP orfices are usually slightly smaller btu than Nat. ones.

Follow the link

http://www.joppaglass.com/burner/lowp_chrt.html

Thanks for all the comments plus the link. I think based on them I have enough information forfollks in the field to get close enough to the correct size furnaces for modeling the houses thanks all.

Ernst,

You mentioned oil, but the replies seem to all be for gas, unless I didn't read correctly.  For oil you can look for the nozzle size.  Sometimes it is notes on the service tag or in the manual, if still around.  In some cases you might be able to call the service company as they may have that noted for their HDD fuel calculations or service work. 

Bud

Thanks, I did find that out. In weatherization we deal with some really old furnaces, so sometimes getting a ballpark furnace size is the best we can do but the nozzle sizes for oil seem to be pretty specific.

For the oil burning furnaces, you should check the pump pressure. Older furnaces run at 100psi, and newer ones run at 140psi. When the pressure is higher, you need to cross reference the nozzle size to get proper Btu ratings. Plenty of reference materials are located on the Beckett website.

For propane figure about 20-25k per burner rated input. Varies some form unit to unit but 22k is typical.

Thanks Bob, we'll go woithout. It should be close enough without having to factor in pressures and temps, etc and  complicate the process too much.

I'll apologies in advance for drifting here a bit, but your "close enough" comment threw me back to my beginning in this business (05) when I questioned every number we use.  The idea of pinning down the performance of a home to the last tiny detail is laughable when we consider just how many of our inputs are "close enough" numbers.  From insulation values, HDD, window performance, and air leakage (to name a few), we guess and we guess and then carry our calculations out to two decimal places (or the computer does).  I think my tape measure is the only real source of accurate information :).

I enjoyed the comment

Bud

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Ramon Aguirre replied to Tom Conlon's discussion Whole House Fans - Love 'Em or Not?
"Whole house fan basically serves the purpose of exhaust fans. They are more cheaper than air…"
5 hours ago
Brandon Walton commented on Brandon Walton's photo
Thumbnail

2014-07-25 15.17.30

"While performing a QC it is always good to look inside the return.........."
13 hours ago
Brandon Walton posted a photo

2014-07-25 15.17.30

Supposed Sealed Return Chase
13 hours ago
Brandon Walton commented on Diane Chojnowski's group Facebook Pages
13 hours ago
Brandon Walton joined Diane Chojnowski's group
Thumbnail

Facebook Pages

Does your company or organization have a Facebook Page?This group is for pros who have facebook…See More
13 hours ago
Brandon Walton posted a discussion

12 Things Every Home Performance Contractor Should Have on Their Work Truck

Every home is unique and differs from the last. It would be a perfect world (from a project…See More
15 hours ago
Brandon Walton posted a blog post

12 Things Every Home Performance Contractor Should Have on Their Work Truck

Every home is unique and differs from the last. It would be a perfect world (from a project…See More
15 hours ago
Todd Collins replied to Mike Kandel's discussion Our Homes Suck – And That's Why Our Kids Have Sinus Problems
"Richard,   The study you cited states:    "Patrick N. Breysse, a public health…"
yesterday
Don Fitchett shared their blog post on Digg
yesterday
Don Fitchett shared their blog post on StumbleUpon
yesterday
Don Fitchett shared their blog post on Twitter
yesterday
Kurt Albershardt replied to John Shillito's discussion Fixing a water heater?
"2000 ppm CO is not a problem?  Really?  In what universe?"
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service