I have a customer that we dense packed the attic floor of their house and airsealed around the masonry chimney.  The problem is the red brick chimney condenses in the attic. This has caused the floor around the chimney to heave and the ceiling below to stain.  The attic is 1260 square feet and is pretty leaky to the outside.  The customer states the problem has only occurred since we did the work.  Can any one give me some ideas what would cause this issue?

Views: 2195

Attachments:

Reply to This

Replies to This Discussion

It seems to me the chimney is probably cold, being connected to the outdoors.  So the moisture is coming from the surrounding air.  If keeping moisture out of the surrounding air is not practical, I'd suggest insulating the chimney with fiberglass batts with a vapor barrier on the outside.  Does that sound reasonable?
Is the chimney lined? It could be from flue gases from an unlined chimney. Any problem with condensation on the roof sheathing?

The condensation is from the flue gasses condensing inside the chimney.  This will be increase  as the attic temp drops. ths cools down the brick which allows the flue gasses to condense out at a greater rate.  If there is no clay liner or a flexible chimney liner in the chinmey one will neeed to be installed.  

This has been happeneing before but because the attic was kept warmer do to the heat loss through the ceiling it would only have shown up when it got colder outside.  Now that the attis is seperated from the house there is not enought heat to keep the bricks warm so more condensate from flue gasses is present.  

The condensate is mildly accitic (like lemon juice)  It will turn any paper products a dark chocloate brown after a while.  This is one way to tell the difference between a roof leak and condensate.     

 

All gas furnaces produce water vapor as a by product of combustion adn need to be addressed when furnace, water heaters and such are changed out-   You will need to recommend a chimney liner.

http://oee.nrcan.gc.ca/residential/personal/chimneys.cfm?attr=4  the link will give you a explanation, even though it is canadian, they expriance the problems much more than warmer climates

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Steven Lewis replied to William Fisher's discussion Can tankless water heaters provide hot water even when the groundwater is fairly cold?
"Look at reducing the ambient humidity in the home.  The dew point is the key to the…"
17 hours ago
Olivia Taylor posted blog posts
yesterday
norman farwell replied to Bryan Pringle's discussion Dense packed cellulose in basement?
"Ha, we're on the same wavelength.  That's the big question--I'm still thinking…"
yesterday
Bryan Pringle replied to Bryan Pringle's discussion Dense packed cellulose in basement?
"Thanks Norm, we'll have a couple of case studies when all is said and done. Just curious, do…"
yesterday
norman farwell replied to Bryan Pringle's discussion Dense packed cellulose in basement?
"Bryan,  I am trying the same thing for most of the same reasons and also against advice to the…"
yesterday
Morgan M Audetat commented on Sean McLoughlin's blog post Programming in-floor electric radiant heat, is it worth it?
"You would need a large bathroom to see the difference. We install them both ways depending on the…"
yesterday
Dennis Heidner commented on Sean McLoughlin's blog post Programming in-floor electric radiant heat, is it worth it?
"The key is that this is the bathroom.  Occupancy is not constant.  It is more likely used…"
yesterday
Charles Cormany commented on Sean McLoughlin's blog post Programming in-floor electric radiant heat, is it worth it?
"I have seen resistance floor heaters add nearly $100 per month to an electric bill. Since most…"
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service