I have a customer that we dense packed the attic floor of their house and airsealed around the masonry chimney.  The problem is the red brick chimney condenses in the attic. This has caused the floor around the chimney to heave and the ceiling below to stain.  The attic is 1260 square feet and is pretty leaky to the outside.  The customer states the problem has only occurred since we did the work.  Can any one give me some ideas what would cause this issue?

Views: 2838

Attachments:

Reply to This

Replies to This Discussion

It seems to me the chimney is probably cold, being connected to the outdoors.  So the moisture is coming from the surrounding air.  If keeping moisture out of the surrounding air is not practical, I'd suggest insulating the chimney with fiberglass batts with a vapor barrier on the outside.  Does that sound reasonable?
Is the chimney lined? It could be from flue gases from an unlined chimney. Any problem with condensation on the roof sheathing?

The condensation is from the flue gasses condensing inside the chimney.  This will be increase  as the attic temp drops. ths cools down the brick which allows the flue gasses to condense out at a greater rate.  If there is no clay liner or a flexible chimney liner in the chinmey one will neeed to be installed.  

This has been happeneing before but because the attic was kept warmer do to the heat loss through the ceiling it would only have shown up when it got colder outside.  Now that the attis is seperated from the house there is not enought heat to keep the bricks warm so more condensate from flue gasses is present.  

The condensate is mildly accitic (like lemon juice)  It will turn any paper products a dark chocloate brown after a while.  This is one way to tell the difference between a roof leak and condensate.     

 

All gas furnaces produce water vapor as a by product of combustion adn need to be addressed when furnace, water heaters and such are changed out-   You will need to recommend a chimney liner.

http://oee.nrcan.gc.ca/residential/personal/chimneys.cfm?attr=4  the link will give you a explanation, even though it is canadian, they expriance the problems much more than warmer climates

RSS

Photos

Loading…
  • Add Photos
  • View All

Latest Activity

Daniel Cullen replied to Rodney Fox's discussion Radon: Truth vs. Myth
"As you point out Caoimhin, radon is not the health issue...it's the progeny, yes? Mr.…"
1 hour ago
Daniel Cullen replied to Rodney Fox's discussion Radon: Truth vs. Myth
"Is all Alpha radiation equal insofar as it's capacity to damage human tissue?  Does the…"
1 hour ago
Earth Advantage posted an event
Thumbnail

CakeSystems™ Software Course at Webinar

March 4, 2016 from 9am to 11am
CakeSystems Software training is offered as a self-paced online course of 3-4 hours followed by a…See More
9 hours ago
Anthony Adams posted a blog post

Bonus room attic walls heat load

Hi Everyone...First of all I am 59yr old retired Federal employee. I took HVAC in a trade school 30…See More
12 hours ago
Tom White's video was featured

Multifamily Building Energy Innovation- TrueFlow Capture Box

Video explaining the new tool to help reduce the energy costs of effective ventilation in multifamily buildings.
16 hours ago
Alfie Davis posted a blog post

Utility of a Hardwood Staircase

Everything needs a makeover after a certain time. Your home is one of them.  Sometimes, you…See More
19 hours ago
miguel pace shared a profile on Facebook
yesterday
miguel pace liked miguel pace's blog post It is very important to select a fin fan
yesterday

© 2016   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service