I have a customer that we dense packed the attic floor of their house and airsealed around the masonry chimney.  The problem is the red brick chimney condenses in the attic. This has caused the floor around the chimney to heave and the ceiling below to stain.  The attic is 1260 square feet and is pretty leaky to the outside.  The customer states the problem has only occurred since we did the work.  Can any one give me some ideas what would cause this issue?

Views: 1701

Attachments:

Reply to This

Replies to This Discussion

It seems to me the chimney is probably cold, being connected to the outdoors.  So the moisture is coming from the surrounding air.  If keeping moisture out of the surrounding air is not practical, I'd suggest insulating the chimney with fiberglass batts with a vapor barrier on the outside.  Does that sound reasonable?
Is the chimney lined? It could be from flue gases from an unlined chimney. Any problem with condensation on the roof sheathing?

The condensation is from the flue gasses condensing inside the chimney.  This will be increase  as the attic temp drops. ths cools down the brick which allows the flue gasses to condense out at a greater rate.  If there is no clay liner or a flexible chimney liner in the chinmey one will neeed to be installed.  

This has been happeneing before but because the attic was kept warmer do to the heat loss through the ceiling it would only have shown up when it got colder outside.  Now that the attis is seperated from the house there is not enought heat to keep the bricks warm so more condensate from flue gasses is present.  

The condensate is mildly accitic (like lemon juice)  It will turn any paper products a dark chocloate brown after a while.  This is one way to tell the difference between a roof leak and condensate.     

 

All gas furnaces produce water vapor as a by product of combustion adn need to be addressed when furnace, water heaters and such are changed out-   You will need to recommend a chimney liner.

http://oee.nrcan.gc.ca/residential/personal/chimneys.cfm?attr=4  the link will give you a explanation, even though it is canadian, they expriance the problems much more than warmer climates

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.

Latest Activity

Hal Skinner replied to Hal Skinner's discussion An example of what an RCC can do with no R- insulation in the walls.
"Mornin Brett. 90 to 85, yes a slight variance there.  Same ASTM test, different scientists,…"
14 hours ago
Bret Curry replied to Hal Skinner's discussion An example of what an RCC can do with no R- insulation in the walls.
"Great information Hal. It appears the thermal emissivity in your test was .85 rather than .90. Are…"
15 hours ago
Juan Roca commented on Dale Stephens's blog post LED Lighting - Garage Door opener interference
"Hi,There is a real problem with remote controls and LED lights. However, there is a solution in the…"
22 hours ago
Profile IconJuan Roca and Elizabeth Coe joined Home Energy Pros
yesterday
Casey Gesell posted videos
yesterday
Gerald Shechter posted videos
yesterday
Hal Skinner replied to Hal Skinner's discussion An example of what an RCC can do with no R- insulation in the walls.
"Bret,  here are the 2 reports I referred…"
yesterday
Craig Foley shared George Kopf's discussion on Twitter
yesterday

© 2014   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service