I have a customer that we dense packed the attic floor of their house and airsealed around the masonry chimney.  The problem is the red brick chimney condenses in the attic. This has caused the floor around the chimney to heave and the ceiling below to stain.  The attic is 1260 square feet and is pretty leaky to the outside.  The customer states the problem has only occurred since we did the work.  Can any one give me some ideas what would cause this issue?

Views: 3935

Attachments:

Reply to This

Replies to This Discussion

It seems to me the chimney is probably cold, being connected to the outdoors.  So the moisture is coming from the surrounding air.  If keeping moisture out of the surrounding air is not practical, I'd suggest insulating the chimney with fiberglass batts with a vapor barrier on the outside.  Does that sound reasonable?
Is the chimney lined? It could be from flue gases from an unlined chimney. Any problem with condensation on the roof sheathing?

The condensation is from the flue gasses condensing inside the chimney.  This will be increase  as the attic temp drops. ths cools down the brick which allows the flue gasses to condense out at a greater rate.  If there is no clay liner or a flexible chimney liner in the chinmey one will neeed to be installed.  

This has been happeneing before but because the attic was kept warmer do to the heat loss through the ceiling it would only have shown up when it got colder outside.  Now that the attis is seperated from the house there is not enought heat to keep the bricks warm so more condensate from flue gasses is present.  

The condensate is mildly accitic (like lemon juice)  It will turn any paper products a dark chocloate brown after a while.  This is one way to tell the difference between a roof leak and condensate.     

 

All gas furnaces produce water vapor as a by product of combustion adn need to be addressed when furnace, water heaters and such are changed out-   You will need to recommend a chimney liner.

http://oee.nrcan.gc.ca/residential/personal/chimneys.cfm?attr=4  the link will give you a explanation, even though it is canadian, they expriance the problems much more than warmer climates

RSS

Forum Discussions

Origin of guarded blower door testing

Started by Kim Tanner in General Forum. Last reply by Eric Kjelshus Aug 17. 9 Replies

Electro Magnetic Fields (EMF)

Started by Barry L NewDelman in General Forum. Last reply by Daniel Cullen Aug 10. 5 Replies

When is it too windy to use blower door?

Started by Brandon Walton in General Forum. Last reply by Iain Walker Aug 10. 17 Replies

Latest Activity

Tina Baldt added 2 discussions to the group Job Board
12 hours ago
Laurie DiDonato updated an event
Thumbnail

Hybrid HERS Rater Training September 2017 (NH) at Online/ Classroom in Manchester, NH

September 11, 2017 at 9am to October 6, 2017 at 5pm
EXTENDED DEADLINE: Register by August 29th!This training has been approved by the MA Workforce…See More
13 hours ago
Profile IconCharles Bracco, Ryan Gath, Steve Klunder and 11 more joined Home Energy Pros
17 hours ago
Mark Bloomfield added a discussion to the group Job Board
Thumbnail

HVAC Designer with Manual J and D Experience

Job Description:Sustainably Built (SB) of Boulder, Colorado is dedicated to helping architects,…See More
yesterday

Photos

Loading…
  • Add Photos
  • View All

© 2017   Created by Lawrence Berkeley National Laboratory.   Powered by

Badges  |  Report an Issue  |  Terms of Service