CAZ pressure too low

On an energy retrofit project during the test out I learned that under worst case conditions, without the air handler on, the unfinished basement CAZ was at the threshold of the BPI guidelines of -5 pa. There is an atmospherically vented furnace and HWH down there. When the air handler was turned on AND the basement door closed, the pressure went to -7 pa. I read this as leaky air returns in the basement, many of which are panned joist bays. The homeowner is going to seal these, but will not be able to seal them perfectly. I suspect, the worst case CAZ pressure will not pass the BPI standards, even after the sealing of the exposed returns. This client will be switching to geothermal in a few years and getting a sealed combustion or electric HWH.

 

In the past, a passive fresh air intake would be installed. There must be something more controlled out there.

I have made temporary provisions to accommodate the combustion appliances, but what would be the best way to remedy this?

He has a hopper window near the equipment that needs to be replaced: Is there a glass block tile vent that would accomplish this: something that would open only when the pressure went below a set point?

Thanks in advance!

Rob Post

 

Views: 76

Reply to This

Replies to This Discussion

Clients tend to plug holes to the outside when cold air spills in through them.  Relying on a mechanical device to operate and ensure makeup air when demanded is generally not a good solution as it may fail at some point. Plans for switching heating system may be delayed, so install a permanent fix. I think you're on the right track with sealing the return up well. Upstairs ventilation equipment may be pulling air through the duct-work from the basement as well. You don't mention what the whole house pressure is with respect to outside when the CAZ is negative; you may have a supply duct leaking to the outside through a crawlspace or attic which would depressurize the whole house and yield the same negative pressures in the CAZ. I recommend air-sealing the basement ceiling if you haven't already. This helps isolate the CAZ from upstairs ventilation equipment when combined with duct sealing.  If all else fails, I recommend power assist venting.

 

Dale Sherman

Thanks, Dale.

 

There is no duct work in unconditioned spaces. The leaking returns in the basement are the culprits. The entire basement  was air-sealed with ccsf with the exception of the duct work.

I got some solid advice on another forum and will be installing a combustion and make up air system. I've ordered an Equaliz-Air and a Skuttle Model 216. I will test both and decide which is best for my situation. These are passive systems

Sounds like you're on top of it, both make-up air vents are good units.  I prefer piping them to the appliances.  And as Ed suggests, you want to be sure the return is well sealed.  If the homeowner does it, just follow up with a QC inspection.  Thanks for sharing.

 

Dale

Rob:

 

I think your assessment of the situation is correct.  If you are sure that he will install a heat pump in the near future, I would have no qualms about installing a small supply into the area to pressurize it - something that would be easy to close back up.  Of course, do your best on the returns - don't trust a homeowner with this critical job as there are problems that are not obvious.

 

Ed Minch

RSS

Home Energy Pros

Home Energy Pros was founded by the developers of Home Energy Saver Pro (sponsored by the U.S. Department of Energy,) and brought to you in partnership with Home Energy magazine.  Home Energy Pros is sponsored by the Better Buildings Residential Network.

Latest Activity

Malcolm McKelvie replied to Alan Gindt's discussion Minneapolis Blower Door System for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"yes I would pay the delivery fee!"
17 hours ago
Alan Gindt replied to Alan Gindt's discussion Minneapolis Blower Door System for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"Malcolm, If you want to pay delivery from USA we can talk. Otherwise no thanks."
17 hours ago
Malcolm McKelvie replied to Alan Gindt's discussion Minneapolis Blower Door System for sale in the group Energy Auditing Equipment for Sale, Trade or to Purchase
"How old is it? I assume it is in good working order? I'm interested in it but the price needs…"
19 hours ago
William H Nickerson replied to Kim Tanner's discussion Fantastic innovation
"So that's where you use those True Flow plates....."
22 hours ago
Colin Genge updated an event
Thumbnail

Passive House Testing Webinar with Kevin Brennan of the Passive House Academy at Online

September 29, 2015 from 1pm to 2pm
Tests needed to qualify as a passive houseWhy we’re seeing an increase in PH buildingsBest…See More
yesterday
Colin Genge updated an event
Thumbnail

DM32 Smart Gauge 101 Webinar at Online

September 22, 2015 from 1pm to 2pm
Webinar Learning Objectives:Gauge settings and operationCalculate results in the gaugeUpdate the…See More
yesterday
Colin Genge updated an event
Thumbnail

Blower Door 101 Webinar at Online

September 15, 2015 from 1pm to 2pm
See how easy it is to do your first test. Learn tips to perform your first duct test in only twenty…See More
yesterday
Colin Genge updated an event
Thumbnail

Zone Pressure Diagnostics (ZPD) with Bill Eckman of NME$A Webinar at Online

September 10, 2015 from 1pm to 2pm
Benefits and limitations of Zonal Pressure Diagnostics (ZPD).Best practices for accurate…See More
yesterday

© 2015   Created by Lawrence Berkeley National Laboratory.

Badges  |  Report an Issue  |  Terms of Service